Title: Running 4x S9 on a 30A breaker + wiring + APC AP9571A 30a 208V PDU
Post by: btc-haze on December 21, 2017, 10:17:43 AM
Is this setup safe ? running borderline at about 80% capacity


Title: Re: Running 4x S9 on a 30A breaker + wiring + APC AP9571A 30a 208V PDU
Post by: BitcoinIntern on December 21, 2017, 05:10:46 PM
On the wall, the S9's can go upto 1500 watts. That will be above the 80% rule at 208 volt. Do you have any taps on the transformer to increase the voltage? Thanks.


Title: Re: Running 4x S9 on a 30A breaker + wiring + APC AP9571A 30a 208V PDU
Post by: fanatic26 on December 21, 2017, 10:01:41 PM
4 on a 30amp breaker is just fine. I even have a few dozen 30amp breakers running 5 altho in the summer the breakers trip from the heat and over use. I wouldnt recommend more than 4.


Title: Re: Running 4x S9 on a 30A breaker + wiring + APC AP9571A 30a 208V PDU
Post by: btc-haze on December 21, 2017, 10:39:50 PM
On the wall, the S9's can go upto 1500 watts. That will be above the 80% rule at 208 volt. Do you have any taps on the transformer to increase the voltage? Thanks.


no, i dont have taps, could you explain on how that would help ?  Thanks !!