Current setup:
Rig 1 has six 1080ti cards, two 1,000w power supplies that are connected to two different wall plates.
A second identical rig will be completed this week.

All of the outlets in my mining room are connected to a 20amp breaker.  Typically, how many watts can safely be pulled through one breaker.


Title: Re: 12 1080ti Cards, 4 1000w Power Supplies, what Power Strips?
Post by: Eyedol-X on December 31, 2017, 04:39:24 AM

Current setup:
Rig 1 has six 1080ti cards, two 1,000w power supplies that are connected to two different wall plates.
A second identical rig will be completed this week.

All of the outlets in my mining room are connected to a 20amp breaker.  Typically, how many watts can safely be pulled through one breaker.

are they on same breaker? If yes, you're pretty much at your limit.


Title: Re: 12 1080ti Cards, 4 1000w Power Supplies, what Power Strips?
Post by: VyprBTC on December 31, 2017, 04:41:50 AM

Current setup:
Rig 1 has six 1080ti cards, two 1,000w power supplies that are connected to two different wall plates.
A second identical rig will be completed this week.

All of the outlets in my mining room are connected to a 20amp breaker.  Typically, how many watts can safely be pulled through one breaker.

safely 16A or roughly 8-10 cards at 75% TDP if you're on 110v


Title: Re: 12 1080ti Cards, 4 1000w Power Supplies, what Power Strips?
Post by: Vann on December 31, 2017, 04:41:53 AM
It depends if you are running on 120V or 240V. A breaker is rated for a maximum 80% of the capacity for a continous load.

120 V x 20 A = 2400 W

2400 W x .8 = 1920 W maximum continous load.


Title: Re: 12 1080ti Cards, 4 1000w Power Supplies, what Power Strips?
Post by: starrbuck on December 31, 2017, 04:42:51 AM
20 amps x 120 volts = 2400 watts. You can only load up to 80% of the stated rating, so a 20 amp circuit at 120 volts (80%) will handle 1920 watts.


Title: Re: 12 1080ti Cards, 4 1000w Power Supplies, what Power Strips?
Post by: captaindiptoad on December 31, 2017, 04:44:49 AM
PHENOMENAL POWER STRIPS!!!

https://www.amazon.com/gp/product/B0000510Z9/ref=oh_aui_detailpage_o01_s00?ie=UTF8&psc=1

Got 2 of these guys, pulling 1kw through each no problem at all. no heat no loose parts. built tough.

Like the others said, that 2nd rig will put you at your limit for one breaker. just run those guys at a lower TDP and you'll be fine.

Grab this as well so you can ensure your safe.

https://www.amazon.com/P3-International-P4460-Electricity-Monitor/dp/B000RGF29Q/ref=sr_1_2?ie=UTF8&qid=1514695612&sr=8-2&keywords=killawatt+meter


Title: Re: 12 1080ti Cards, 4 1000w Power Supplies, what Power Strips?
Post by: splat1 on December 31, 2017, 01:59:35 PM
If you want more power I suggest looking into PDU's

I will be using this one soon.


https://www.amazon.com/Tripp-Lite-200-240V-Rack-Mount-PDUMH20HV/dp/B0052NM4JA

Keep in mind my hooking this up to a 20a 240v circuit.


Title: Re: 12 1080ti Cards, 4 1000w Power Supplies, what Power Strips?
Post by: WinningThePooh on February 03, 2018, 01:58:23 AM
Well, I managed to trip the breaker with only one rig running, and one laptop.

Plan on hiring an electrician to come in and add another breaker and outlets.  I don't plan on running more than 18 cards, so what should I shoot for in terms of breaker size?