Title: Re: Electrical Safety concern For Minning Post by: davidjr on January 05, 2014, 11:22:32 AM One miner per circuit seems like a good rule of thumb for regular households.
Typical US circuit: 15A x 120V = 1800W Even though your CB won't "pop" as soon as it gets to 1800W, you shouldn't load circuits more than 70% for extended periods. 0.7 x 1800W = 1260W Assuming that there is nothing else on that circuit, you could safely run two Jupiters on it. But add in a TV or a few lights and you're starting to push your luck. European homeowners are a little better off: 0.7 x 10A x 230V = 1610W Regards, David Title: Re: Electrical Safety concern For Minning Post by: torusJKL on January 05, 2014, 11:34:08 AM Europeans with a 3 phase system are even better off:
0.7 * 1.73 * 16A * 230V = 4461W 1.73 is the square root of 3 (number of phases). Title: Re: Electrical Safety concern For Minning Post by: davidjr on January 05, 2014, 09:41:18 PM Europeans with a 3 phase system are even better off: 0.7 * 1.73 * 16A * 230V = 4461W 1.73 is the square root of 3 (number of phases). Thank you for your comment. Yes, 3-phase distribution is sweet. More commonly installed in newer houses. If you have a 16A 3-phase circuit installed you can feel free to load that puppy up like this: 0.7 x 3 x 16A x 230V = 7728W Just be careful to load it equally. That's roughly 2500W per phase, the neutral is shared between the three phases. The best way to do this is with a 3 phase splitter, see: http://www.kvmchoice.com/detail_switch.asp?id=11135 You can use the sqrt(3) in phase-to-phase voltage calculations (the Voltage between two phases, not N): 0.7*sqrt(3)*398V*16A= 7721W |