Title: Power setup for Antminer S9 Post by: KEBKR on July 07, 2018, 02:49:28 AM Hi. First of all sorry if this has been covered but I couldn’t find an answer specific to my setup. I have a fuse Panel, that’s old fashion glass fuses not breakers. I have a 12-2 wire to a 220v (red wire to one side and black to the other ) with 2x20 amp fuses. This is then connected to a dual 20 amp outlet. Does anyone know how many s9i units I can connect to this setup. Could I do 2 per plug so 4 on this one line? 2 on the top outlet and 2 on the bottom?
Title: Re: Power setup for Antminer S9 Post by: Raymond_B on July 07, 2018, 05:42:35 PM You want to run no more than 80% continuous capacity on each circuit. So if the circuits are 20A then no more than 16A continuous each. So 2 Antminers per. Are you saying each outlet has a separate wire run? Or are you saying 2 outlets using one run of 12-2 wire? If it's the latter then you're limited to 2 miners period. If it's one run of 12-2 wire to each outlet then 2 per or 4 total if you have 2 circuits.
Title: Re: Power setup for Antminer S9 Post by: ccgllc on July 07, 2018, 06:07:34 PM You want to run no more than 80% continuous capacity on each circuit. So if the circuits are 20A then no more than 16A continuous each. So 2 Antminers per. Are you saying each outlet has a separate wire run? Or are you saying 2 outlets using one run of 12-2 wire? If it's the latter then you're limited to 2 miners period. If it's one run of 12-2 wire to each outlet then 2 per or 4 total if you have 2 circuits. Agreed. My whole datacenter is wired based on (2) miners per 20amp 220V circuit. Title: Re: Power setup for Antminer S9 Post by: KEBKR on July 07, 2018, 11:30:29 PM You want to run no more than 80% continuous capacity on each circuit. So if the circuits are 20A then no more than 16A continuous each. So 2 Antminers per. Are you saying each outlet has a separate wire run? Or are you saying 2 outlets using one run of 12-2 wire? If it's the latter then you're limited to 2 miners period. If it's one run of 12-2 wire to each outlet then 2 per or 4 total if you have 2 circuits. Yes one 12-2 wire run from the panel to a dual outlet. So I’m limited to 2 miners per lead. Thanks for the response, much appreciated! Title: Re: Power setup for Antminer S9 Post by: Raymond_B on July 07, 2018, 11:33:00 PM Yes one 12-2 wire run from the panel to a dual outlet. So I’m limited to 2 miners per lead. Thanks for the response, much appreciated! Hold up, you're using 220v so both wires carry current. If you physically only have one piece of wire that is 2 conductor 12 gauge then you need to change the outlet to a single as you have a SINGLE 220v 20A circuit. Previously you had 2 110v 20A outlets Title: Re: Power setup for Antminer S9 Post by: KEBKR on July 08, 2018, 02:24:41 AM Hold up, you're using 220v so both wires carry current. If you physically only have one piece of wire that is 2 conductor 12 gauge then you need to change the outlet to a single as you have a SINGLE 220v 20A circuit. Previously you had 2 110v 20A outlets Yes I have one 12-2 wire with the black wire connected to one 110v leg and a 20 amp fuse and then the red wire connected to the other 110v leg and another 20 amp fuse. This is connected to a dual 20 amp outlet. Title: Re: Power setup for Antminer S9 Post by: tim-bc on July 08, 2018, 02:32:21 AM Agreed. My whole datacenter is wired based on (2) miners per 20amp 220V circuit. I second this, the miners that I work with are also wired with 2 S9s per 20A breaker. Title: Re: Power setup for Antminer S9 Post by: Raymond_B on July 08, 2018, 02:45:57 AM Yes I have one 12-2 wire with the black wire connected to one 110v leg and a 20 amp fuse and then the red wire connected to the other 110v leg and another 20 amp fuse. This is connected to a dual 20 amp outlet. I just want to make sure you understand that you will need to replace that outlet with a single outlet, you do not have 2x 220v outlets. You've got 1 220v or 2 110v Title: Re: Power setup for Antminer S9 Post by: KEBKR on July 08, 2018, 02:53:59 AM I just want to make sure you understand that you will need to replace that outlet with a single outlet, you do not have 2x 220v outlets. You've got 1 220v or 2 110v I’ve got this receptacle but what’s the difference in using this as opposed to a single outlet with a power bar with 2 miners attached? https://www.homedepot.ca/en/home/p.20-amp-duplex-receptacle-ivory.1000135014.html Title: Re: Power setup for Antminer S9 Post by: Raymond_B on July 08, 2018, 03:15:38 AM Nothing :) You're good, I thought you might have been thinking you actually had 4 circuits and were going to try to run 4 miners!
But you got it! Title: Re: Power setup for Antminer S9 Post by: KEBKR on July 08, 2018, 03:47:09 AM Nothing :) You're good, I thought you might have been thinking you actually had 4 circuits and were going to try to run 4 miners! But you got it! Ok thanks. Appreciate the help! |