Bitcoin => Mining support => Topic started by: Aristoiz on April 09, 2021, 02:06:00 PM



Title: APW3 Question
Post by: Aristoiz on April 09, 2021, 02:06:00 PM
Hello I am new to this topic and I have a question, if I bring two 110V to form 220V in a receptacle is it safe to connect the source APW 3++? I mean without using neutral since it would be (Line-Line-Ground).


Title: Re: APW3 Question
Post by: NotFuzzyWarm on April 09, 2021, 02:11:53 PM
That is exactly how power in North America works. Here Neutral is only for making the 110v circuits.


Title: Re: APW3 Question
Post by: Aristoiz on April 09, 2021, 02:16:25 PM
That is exactly how power in North America works. Here Neutral is only for making the 110v circuits.
So if I put two 110 lines to make 220V to an APW 3 ++ nothing will happen to it?


Title: Re: APW3 Question
Post by: NotFuzzyWarm on April 09, 2021, 02:23:32 PM
"Happen to it"?
As I said, what you describe, L1-N-L2 is how power is fed to a house in NA and Ground is tied to the neutral at the incoming power junction. Appliances that use 220v just use L1 & L1 with ground so aside from it working, nothing will 'happen' to it.