Ok.... now I'm stumped. I've been trying to get my miners working at our warehouse which is 3-phase Wye. I have a couple of antminer s7 and a whatsminer m3. They have been running at home on 240v (single phase) fine. The Psu also turn on when plugged into 110v (no miner attached as it can't draw the needed amps, but the 12v fan spins up). However, at the warehouse when I connect it to 2 legs (leg-leg, no neutral) nothing happens (and I mean nothing; no noise, clicks, smoke anything). When I take them back home on the 240v again all runs well. Most interesting is we have some bfl miners still running at the warehouse off the same panel but on 110v (ie leg-neutral) circuits. I know when connected leg-leg there is power present but the power supplies just react like they arnt plugged into anything.
Any thoughts/help would be greatly appreciated as I'm thinking my only choice is to setup a 110v to 220v transformer which I'd like not to do for obvious reasons.
|