well if your room temperature is fine, and your miner are working cool enough, you should be doing good already
you should aim at around 60° max, at least this with the antminer s5
There would be intake fans pulling in fresh air from outside, so that would be the room temp before going through the miners. I'm just in the hypothetical/planning phase to see if it would make sense with a bunch of miners in a warehouse and what it would take from an exhaust standpoint.
room size helps to know it, but
a 3000 cfm fan changes the air every 2 minutes in a 20 by 30 by 10 ft room (Under perfect conditions)
So look at 3000 cfm as the exit fan and 2000 cfm as the fresh air fans as a minimum if the room is 20 by 30 by 10.
Many do this:
^^^^^^^^^ hot air leaves the building
window window
^^ ^^^^^^^^^^^^^^
fan fan fan fan fanminers miners miners^^^^^^^^^^
fan fan fan fan window window window
cold air outside the building