Author Topic: Putting out miners that set on fire  (Read 1483 times)
Anddos (OP)
Sr. Member
****
Offline Offline

Activity: 378
Merit: 250


View Profile
January 10, 2014, 05:58:20 PM
 #1

Seeing a few stories of bitcoin/litecoin miners setting on fire , placing a firealarm next to your miners wont prevent the fire if your not home, someone needs to create a device that would instantly put out the fire on your miner else you might not have a home,THOUGHTS??

phoenixsilverbird
Full Member
***
Offline Offline

Activity: 154
Merit: 100

BUYING ANTMINER S1!!!


View Profile
January 10, 2014, 06:15:59 PM
 #2

I was also looking about this.

For obvious reasons, water and powder cannot be used as they will harm the circuitry.

However, this automatic extinguisher releases a no-residue electronics friendly gas.
It was specifically designed for electronic equipment and server towers.
It activates at 79 Degrees Celsius so you should put it a bit of a distance away from the rig or it could go off when the miners get hot.

http://www.safelincs.co.uk/automatic-fire-extinguishers/

HellDiverUK
Hero Member
*****
Offline Offline

Activity: 1246
Merit: 501



View Profile
January 10, 2014, 06:47:58 PM
 #3

someone needs to create a device that would instantly put out the fire on your miner else you might not have a home,THOUGHTS??

It's called a CO2 fire extinguisher.   Huh  Point at base of fire and blast away.
phoenixsilverbird
Full Member
***
Offline Offline

Activity: 154
Merit: 100

BUYING ANTMINER S1!!!


View Profile
January 10, 2014, 09:47:33 PM
 #4

someone needs to create a device that would instantly put out the fire on your miner else you might not have a home,THOUGHTS??

It's called a CO2 fire extinguisher.   Huh  Point at base of fire and blast away.

He said when you AREN'T at home.

repairguy
Sr. Member
****
Offline Offline

Activity: 252
Merit: 250


View Profile
January 10, 2014, 09:58:59 PM
 #5

The product you are talking about already exists, They use it in data centers and on commercial cooking equipment.  Some use c02 and some use halon.  However, good electrical practices and regular inspection would probably be a better option.
yorich
Full Member
***
Offline Offline

Activity: 129
Merit: 100


View Profile
January 10, 2014, 11:29:08 PM
 #6

I keep my rig outside just in case something like this happens.  Sits on a concrete pad away from the house with a cover over it in case it rains.  Harder to set the house on fire, cooled naturally by the outside air....it's a win-win
frankenmint
Legendary
*
Offline Offline

Activity: 1456
Merit: 1018


HoneybadgerOfMoney.com Weed4bitcoin.com


View Profile WWW
January 11, 2014, 01:05:30 AM
 #7

I keep my rig outside just in case something like this happens.  Sits on a concrete pad away from the house with a cover over it in case it rains.  Harder to set the house on fire, cooled naturally by the outside air....it's a win-win

Put my expensive hardware outside for the elements?Huh RU serious???  Can't trust your HW?  If not...you're doing it wrong!  I believe in the auto fire extinguishers idea though thanks for the link!

empoweoqwj
Hero Member
*****
Offline Offline

Activity: 518
Merit: 500


View Profile
January 11, 2014, 02:21:16 AM
 #8

Don't create a rig that is likely to catch on fire. Prevention is better than cure.
southerngentuk
Sr. Member
****
Offline Offline

Activity: 1316
Merit: 253


Sugars.zone | DatingFi - Earn for Posting


View Profile
January 11, 2014, 08:46:26 AM
 #9

The product you are talking about already exists, They use it in data centers and on commercial cooking equipment.  Some use c02 and some use halon.  However, good electrical practices and regular inspection would probably be a better option.

From memory I think the systems were Halon or co2 (long time ago) however the systems I have seen usually where activated by the fire alarm system and incorporated disconnection of electricity supply - no point putting it out if it will reignite..

Another point to note- the rooms had strobes to indicate activation ( in addition to audible ) primarily to prevent suffocation..  Shocked

SUGAR
██   ██

██   ██

██   ██

██   ██

██   ██

██   ██
▄▄████████████████████▄▄
▄████████████████████████▄
███████▀▀▀██████▀▀▀███████
█████▀██████▀▀██████▀█████
██████████████████████████
██████████████████████████
█████████████████████▄████
██████████████████████████
████████▄████████▄████████
██████████████████████████
▀████████████████████████▀
▀▀████████████████████▀▀

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██
███████████████████████████
███████████████████████████
██████               ██████
██████   ▄████▀      ██████
██████▄▄▄███▀   ▄█   ██████
██████████▀   ▄███   ██████
████████▀   ▄█████▄▄▄██████
██████▀   ▄███████▀▀▀██████
██████   ▀▀▀▀▀▀▀▀▀   ██████
██████               ██████
███████████████████████████
███████████████████████████
.
Backed By
ZetaChain

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██
▄▄████████████████████▄▄
██████████████████████████
████████████████████████████
█████████████████▀▀  ███████
█████████████▀▀      ███████
█████████▀▀   ▄▄     ███████
█████▀▀    ▄█▀▀     ████████
█████████ █▀        ████████
█████████ █ ▄███▄   ████████
██████████████████▄▄████████
██████████████████████████
▀▀████████████████████▀▀
▄▄████████████████████▄▄
██████████████████████████
██████ ▄▀██████████  ███████
███████▄▀▄▀██████  █████████
█████████▄▀▄▀██  ███████████
███████████▄▀▄ █████████████
███████████  ▄▀▄▀███████████
█████████  ████▄▀▄▀█████████
███████  ████████▄▀ ████████
████████████████████████████
██████████████████████████
▀▀████████████████████▀▀
southerngentuk
Sr. Member
****
Offline Offline

Activity: 1316
Merit: 253


Sugars.zone | DatingFi - Earn for Posting


View Profile
January 11, 2014, 08:55:41 AM
 #10

I believe a normal ATX power supply has built in protection, I have been considering an alternative DC supply, this would require some proper distribution, perhaps automotive fuses, to prevent such an occurrence.  Look for RV distribution boards on ebay perhaps.

Your main 12V DC could pass through a 12V relay/contactor and run its coil of the aux contacts of a smoke detector (most mains smoke detector manufacturers do an auxiliary unit for similar purposes)

Just make sure your contactor uses a hold on circuit with a manual "on" button, so it wont re energize in your absence.

SUGAR
██   ██

██   ██

██   ██

██   ██

██   ██

██   ██
▄▄████████████████████▄▄
▄████████████████████████▄
███████▀▀▀██████▀▀▀███████
█████▀██████▀▀██████▀█████
██████████████████████████
██████████████████████████
█████████████████████▄████
██████████████████████████
████████▄████████▄████████
██████████████████████████
▀████████████████████████▀
▀▀████████████████████▀▀

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██
███████████████████████████
███████████████████████████
██████               ██████
██████   ▄████▀      ██████
██████▄▄▄███▀   ▄█   ██████
██████████▀   ▄███   ██████
████████▀   ▄█████▄▄▄██████
██████▀   ▄███████▀▀▀██████
██████   ▀▀▀▀▀▀▀▀▀   ██████
██████               ██████
███████████████████████████
███████████████████████████
.
Backed By
ZetaChain

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██
▄▄████████████████████▄▄
██████████████████████████
████████████████████████████
█████████████████▀▀  ███████
█████████████▀▀      ███████
█████████▀▀   ▄▄     ███████
█████▀▀    ▄█▀▀     ████████
█████████ █▀        ████████
█████████ █ ▄███▄   ████████
██████████████████▄▄████████
██████████████████████████
▀▀████████████████████▀▀
▄▄████████████████████▄▄
██████████████████████████
██████ ▄▀██████████  ███████
███████▄▀▄▀██████  █████████
█████████▄▀▄▀██  ███████████
███████████▄▀▄ █████████████
███████████  ▄▀▄▀███████████
█████████  ████▄▀▄▀█████████
███████  ████████▄▀ ████████
████████████████████████████
██████████████████████████
▀▀████████████████████▀▀
brontosaurus
Sr. Member
****
Offline Offline

Activity: 441
Merit: 250



View Profile
January 11, 2014, 04:56:37 PM
 #11

Don't create a rig that is likely to catch on fire. Prevention is better than cure.

That makes a whole lot of sense.
repairguy
Sr. Member
****
Offline Offline

Activity: 252
Merit: 250


View Profile
January 11, 2014, 07:15:20 PM
 #12

The product you are talking about already exists, They use it in data centers and on commercial cooking equipment.  Some use c02 and some use halon.  However, good electrical practices and regular inspection would probably be a better option.

From memory I think the systems were Halon or co2 (long time ago) however the systems I have seen usually where activated by the fire alarm system and incorporated disconnection of electricity supply - no point putting it out if it will reignite..

Another point to note- the rooms had strobes to indicate activation ( in addition to audible ) primarily to prevent suffocation..  Shocked

Yep,  They dissipate all of the oxygen so nothing can burn.  You don't want to be in a room when one goes off.  Some are activated electrically(24v) and some use a big ass spring and a lead link.
jzcjca00
Sr. Member
****
Offline Offline

Activity: 263
Merit: 250


View Profile
January 11, 2014, 07:18:23 PM
 #13

Don't create a rig that is likely to catch on fire. Prevention is better than cure.

BFL didn't mention it in their brochure!  How was I to know?

Tips much appreciated! 1PPJHDawPvjh6MEzsvXrMYLgpLmyAaNXUc
phoenixsilverbird
Full Member
***
Offline Offline

Activity: 154
Merit: 100

BUYING ANTMINER S1!!!


View Profile
January 11, 2014, 07:32:00 PM
 #14

I know right?
Absolutely shocking that we should have to take basic precautionary methods to stop fires.
Scandalous!

southerngentuk
Sr. Member
****
Offline Offline

Activity: 1316
Merit: 253


Sugars.zone | DatingFi - Earn for Posting


View Profile
January 12, 2014, 12:41:05 AM
 #15

The product you are talking about already exists, They use it in data centers and on commercial cooking equipment.  Some use c02 and some use halon.  However, good electrical practices and regular inspection would probably be a better option.

From memory I think the systems were Halon or co2 (long time ago) however the systems I have seen usually where activated by the fire alarm system and incorporated disconnection of electricity supply - no point putting it out if it will reignite..

Another point to note- the rooms had strobes to indicate activation ( in addition to audible ) primarily to prevent suffocation..  Shocked

Yep,  They dissipate all of the oxygen so nothing can burn.  You don't want to be in a room when one goes off.  Some are activated electrically(24v) and some use a big ass spring and a lead link.

I've seen the lead link system in boiler houses, they sit just above the burner in front of the boiler door. There also used for fire barriers in AC ducting.

For those interested it is basically to pieces of lead that overlap and is held together with solder that has a set melt temperature. Good for high heat fires not so good with smoke fires.

Anyone interested in rigging up a smoke detector to auto shut of the supply, I can provide some advice.

SUGAR
██   ██

██   ██

██   ██

██   ██

██   ██

██   ██
▄▄████████████████████▄▄
▄████████████████████████▄
███████▀▀▀██████▀▀▀███████
█████▀██████▀▀██████▀█████
██████████████████████████
██████████████████████████
█████████████████████▄████
██████████████████████████
████████▄████████▄████████
██████████████████████████
▀████████████████████████▀
▀▀████████████████████▀▀

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██
███████████████████████████
███████████████████████████
██████               ██████
██████   ▄████▀      ██████
██████▄▄▄███▀   ▄█   ██████
██████████▀   ▄███   ██████
████████▀   ▄█████▄▄▄██████
██████▀   ▄███████▀▀▀██████
██████   ▀▀▀▀▀▀▀▀▀   ██████
██████               ██████
███████████████████████████
███████████████████████████
.
Backed By
ZetaChain

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██

██   ██
▄▄████████████████████▄▄
██████████████████████████
████████████████████████████
█████████████████▀▀  ███████
█████████████▀▀      ███████
█████████▀▀   ▄▄     ███████
█████▀▀    ▄█▀▀     ████████
█████████ █▀        ████████
█████████ █ ▄███▄   ████████
██████████████████▄▄████████
██████████████████████████
▀▀████████████████████▀▀
▄▄████████████████████▄▄
██████████████████████████
██████ ▄▀██████████  ███████
███████▄▀▄▀██████  █████████
█████████▄▀▄▀██  ███████████
███████████▄▀▄ █████████████
███████████  ▄▀▄▀███████████
█████████  ████▄▀▄▀█████████
███████  ████████▄▀ ████████
████████████████████████████
██████████████████████████
▀▀████████████████████▀▀
empoweoqwj
Hero Member
*****
Offline Offline

Activity: 518
Merit: 500


View Profile
January 12, 2014, 02:34:45 AM
 #16

Don't create a rig that is likely to catch on fire. Prevention is better than cure.

BFL didn't mention it in their brochure!  How was I to know?

BFL don't care about customers. They have proved that over and over.