Author Topic: Problem with ventilation or cooling of room with 1 window  (Read 704 times)
pbuva (OP)
Full Member
***
Offline Offline

Activity: 194
Merit: 100


View Profile
April 25, 2017, 04:54:42 PM
Last edit: April 25, 2017, 05:37:39 PM by pbuva
 #1

Hi, I have a question about ventilating or cooling a room with multiple miners. This is a large cellar space with a single window of medium size over which the window from the neighboring flat is located. The window in the basement is up in the middle of one long wall. The window is on the other side at the level of the sidewalk, but it has a grid so there is about 5 cm between the glass and the grid. I may remove this window, but it will then be seen from the outside. On both sides of this wall I plan several miners. The problem is that there are only 1 miner with 3 GPUs (up to 5 GPUs) and even though the window is partially open, there is already a lot of heat. I plan to have 41-65 graphics, depending on the possibilities (new will be with 6 GPUs), the plan is SAPPHIRE PULSE Radeon RX 580 OC 8G.

I have three options:
- air conditioning (expensive acquisition and electricity cool so many graphics (5 or 7 Kwh units))
- place an industrial fan in the window and vacuum warm air out (noise under the neighbor's window, but maybe I just do not have the right idea of ​​the noise)
- Place the industrial fan on the floor and blow the warm air towards the window
Is there any other solution? Is there a divider as a window-fill, so that half the window blows the cold air in and the other blows the warm air?

What solution do you think best?





110 cm = 43.3 in
80 cm = 31.5 in

★ ★ ★ ★ ★   DeepOnion    Anonymous and Untraceable Cryptocurrency    TOR INTEGRATED & SECURED   ★ ★ ★ ★ ★
› › › › ›  JOIN THE NEW AIRDROP ✈️        VERIFIED WITH DEEPVAULT  ‹ ‹ ‹ ‹ ‹
▬▬▬▬▬▬▬▬▬▬▬▬▬▬▬   ANN  WHITEPAPER  FACEBOOK  TWITTER  YOUTUBE  FORUM   ▬▬▬▬▬▬▬▬▬▬▬▬▬▬▬
1714051755
Hero Member
*
Offline Offline

Posts: 1714051755

View Profile Personal Message (Offline)

Ignore
1714051755
Reply with quote  #2

1714051755
Report to moderator
1714051755
Hero Member
*
Offline Offline

Posts: 1714051755

View Profile Personal Message (Offline)

Ignore
1714051755
Reply with quote  #2

1714051755
Report to moderator
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
philipma1957
Legendary
*
Online Online

Activity: 4102
Merit: 7764


'The right to privacy matters'


View Profile WWW
April 25, 2017, 04:58:00 PM
Last edit: April 25, 2017, 05:11:34 PM by philipma1957
 #2

exact size of window is needed

14 inch duct

http://www.homedepot.com/p/14-in-x-25-ft-Insulated-Flexible-Duct-R6-in-Silver-Jacket-F6IFD14X300/100211848

10 inch duct
http://www.homedepot.com/p/10-in-x-25-ft-Insulated-Flexible-Duct-R6-Silver-Jacket-F6IFD10X300/100142376




 so if the window is 22 by 11    inches  you can use the 10 inch duct

if the window is 30 by  15 inches you can use the 14 inch duct


I have more wait for it

miners on a  wire shelf

http://www.homedepot.com/p/HDX-48-in-W-x-72-in-H-x-18-in-D-Decorative-Wire-Chrome-Finish-Commercial-Shelving-Unit-6T60184872C/100655787

use this to cover the shelf top and sides

https://www.amazon.com/gp/product/B016QUSH6G/ref=oh_aui_detailpage_o01_s00?ie=UTF8&psc=1

put a few fans behind the wire rack.  put fans in front of wire rack point the air into the flex duct and direct it out the window.

I am betting  that will send enough hot air out of the  basement.

as for cold air in  if the window is big enough a simple hole with a screen would allow air in.

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
pbuva (OP)
Full Member
***
Offline Offline

Activity: 194
Merit: 100


View Profile
April 25, 2017, 05:34:23 PM
 #3

So do you think, among other things, that it's foolish to use spec frames on a rig, but throw it directly into the wire shelves on a non-conductive mat and just hang up the cards?

★ ★ ★ ★ ★   DeepOnion    Anonymous and Untraceable Cryptocurrency    TOR INTEGRATED & SECURED   ★ ★ ★ ★ ★
› › › › ›  JOIN THE NEW AIRDROP ✈️        VERIFIED WITH DEEPVAULT  ‹ ‹ ‹ ‹ ‹
▬▬▬▬▬▬▬▬▬▬▬▬▬▬▬   ANN  WHITEPAPER  FACEBOOK  TWITTER  YOUTUBE  FORUM   ▬▬▬▬▬▬▬▬▬▬▬▬▬▬▬
mirny
Legendary
*
Offline Offline

Activity: 1108
Merit: 1005



View Profile
April 26, 2017, 12:44:58 AM
 #4

Best solution is, find a better room.
Can't imagine 60cards in there, even with opened window.
You will have lots of troubles.

This is my signature...
philipma1957
Legendary
*
Online Online

Activity: 4102
Merit: 7764


'The right to privacy matters'


View Profile WWW
April 26, 2017, 01:11:05 AM
Last edit: April 26, 2017, 01:29:04 AM by philipma1957
 #5

okay 110 cm = 43 inches

          80 cm = 31 inches



I think  you can use 2 of these


https://www.amazon.com/MaxxAir-HVHF-12COMBO-12-Inch-Cylinder/dp/B004GHNKU0/ref=sr_1_7?


to direct hot air out on the top ½  of the window

see shot below

this may be good  for 30 cards  not 60

  a lot depends on  outside temps.  ie  40c maybe only 20 cards

35 c maybe a few more cards  23
30 c maybe a few more cards  26
25 c  maybe a few more cards 29
20 c maybe a few more  cards  32

 I am guessing as to how many cards you can do

having the hot air on the top half of the window should help the cooler air come in of the bottom.

there are other factors involved if the room is very tightly sealed  you will naturally suck in air from the bottom slot.

you should take the temperature of the air coming in the bottom slot  and compare it to the temp of the air from the 2 blowers.




▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
h311m4n
Sr. Member
****
Offline Offline

Activity: 487
Merit: 266



View Profile
April 26, 2017, 01:38:15 PM
 #6

Hi, I have a question about ventilating or cooling a room with multiple miners. This is a large cellar space with a single window of medium size over which the window from the neighboring flat is located. The window in the basement is up in the middle of one long wall. The window is on the other side at the level of the sidewalk, but it has a grid so there is about 5 cm between the glass and the grid. I may remove this window, but it will then be seen from the outside. On both sides of this wall I plan several miners. The problem is that there are only 1 miner with 3 GPUs (up to 5 GPUs) and even though the window is partially open, there is already a lot of heat. I plan to have 41-65 graphics, depending on the possibilities (new will be with 6 GPUs), the plan is SAPPHIRE PULSE Radeon RX 580 OC 8G.

I have three options:
- air conditioning (expensive acquisition and electricity cool so many graphics (5 or 7 Kwh units))
- place an industrial fan in the window and vacuum warm air out (noise under the neighbor's window, but maybe I just do not have the right idea of ​​the noise)
- Place the industrial fan on the floor and blow the warm air towards the window
Is there any other solution? Is there a divider as a window-fill, so that half the window blows the cold air in and the other blows the warm air?

What solution do you think best?





110 cm = 43.3 in
80 cm = 31.5 in

I have a similar issue, but I don't even have a window, I just have an opening in the concrete that is like 40cm by 20cm wide. I have 3 rigs in there and things are getting pretty hot already.

I'm debating just putting 2 big 200mm case fans on there (with the highest airflow I can find) and just push the hot air out OR have one fan blow hot air out with a duct that goes a bit further up and have a second fan blow fresh air in.
philipma1957
Legendary
*
Online Online

Activity: 4102
Merit: 7764


'The right to privacy matters'


View Profile WWW
April 26, 2017, 04:00:12 PM
 #7

Hi, I have a question about ventilating or cooling a room with multiple miners. This is a large cellar space with a single window of medium size over which the window from the neighboring flat is located. The window in the basement is up in the middle of one long wall. The window is on the other side at the level of the sidewalk, but it has a grid so there is about 5 cm between the glass and the grid. I may remove this window, but it will then be seen from the outside. On both sides of this wall I plan several miners. The problem is that there are only 1 miner with 3 GPUs (up to 5 GPUs) and even though the window is partially open, there is already a lot of heat. I plan to have 41-65 graphics, depending on the possibilities (new will be with 6 GPUs), the plan is SAPPHIRE PULSE Radeon RX 580 OC 8G.

I have three options:
- air conditioning (expensive acquisition and electricity cool so many graphics (5 or 7 Kwh units))
- place an industrial fan in the window and vacuum warm air out (noise under the neighbor's window, but maybe I just do not have the right idea of ​​the noise)
- Place the industrial fan on the floor and blow the warm air towards the window
Is there any other solution? Is there a divider as a window-fill, so that half the window blows the cold air in and the other blows the warm air?

What solution do you think best?



110 cm = 43.3 in
80 cm = 31.5 in

I have a similar issue, but I don't even have a window, I just have an opening in the concrete that is like 40cm by 20cm wide. I have 3 rigs in there and things are getting pretty hot already.

I'm debating just putting 2 big 200mm case fans on there (with the highest airflow I can find) and just push the hot air out OR have one fan blow hot air out with a duct that goes a bit further up and have a second fan blow fresh air in.

try using these they will move a lot of air 8 inches = 200 mm/20cm


 http://www.ebay.com/itm/8inch-Electric-Radiator-Fans-Universal-Push-Pull-Engine-Bay-Slim-Cooling-Fan-Kit-/192060629141?

you can use an atx or server psu to power them.




▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
xxcsu
Hero Member
*****
Offline Offline

Activity: 1498
Merit: 597


View Profile WWW
April 26, 2017, 04:12:49 PM
Last edit: April 26, 2017, 04:42:11 PM by xxcsu
 #8

You need to provide some airflow for those 41-65 cards , with only one window that is not going to be a easy task
Do you have a right amount of electrical power need in that room ? with 65 cards it would be over 10KW , with 240 volts you need at least 50 amp to stay on the safe side , with 120 volt at least 90amp ...

"I have three options:
- air conditioning (expensive acquisition and electricity cool so many graphics (5 or 7 Kwh units))


forget , you need a very high btu cooling power to keep those cards in the right temp range in that closed airspace, AC unit/installation will be very expensive power bill going to be crazy high your ROI will be forever


- place an industrial fan in the window and vacuum warm air out (noise under the neighbor's window, but maybe I just do not have the right idea of ​​the noise)

you need a air intake also , you can not just suck out the air from that room


- Place the industrial fan on the floor and blow the warm air towards the window

the hot air never going to leave the room if there is no intake air

Solution :
split that window area ,use one half for intake air  , another side for air outlet , use any commercial air mover, with highest possible CFM rating Smiley, use 2 of this or something similar :
http://refinishingonline.com/store/exhaust-fans
make sure the inlet and outlet in the window is pushing/pulling air to a from a different angle . So the exhausted air not coming back via the intake duct.
Place the exhaust duct close to the ceiling ( hot air moving up always ) , you still going to need a high CFM fan to circulating air inside that room ( http://www.northwoodswarehouse.com/q-standard-30-direct-drive-industrial-drum-fan-10380 )

good luck with your project:)

Learn about Merit & new rank requirements , Learn how to use MERIT , make this community better
If you like the answer you got for your question from any member ,
If you find any post useful , informative use the +Merit button.
RentGPU
Sr. Member
****
Offline Offline

Activity: 661
Merit: 258


View Profile
April 26, 2017, 07:40:42 PM
 #9

I am sure you have a door Smiley , if you can push the hot air through that door with some fans , and let the window for the intake air fans , with that you can make a good airflow through the room , what is the normal air temp. you have there in this room ?.

2016 GPU Miner
pbuva (OP)
Full Member
***
Offline Offline

Activity: 194
Merit: 100


View Profile
April 26, 2017, 08:42:22 PM
Last edit: April 26, 2017, 08:56:09 PM by pbuva
 #10

I am sure you have a door Smiley , if you can push the hot air through that door with some fans , and let the window for the intake air fans , with that you can make a good airflow through the room , what is the normal air temp. you have there in this room ?.

I have a plastic door, the material that is used for plastic windows. It is a fact that it could be used at least on a small fan that would suck the air, it is about 1 meter below ground level, there are stairs down. The cellar itself is within 18 degrees, but in summer it can be up to 40 degrees celsius outside.

★ ★ ★ ★ ★   DeepOnion    Anonymous and Untraceable Cryptocurrency    TOR INTEGRATED & SECURED   ★ ★ ★ ★ ★
› › › › ›  JOIN THE NEW AIRDROP ✈️        VERIFIED WITH DEEPVAULT  ‹ ‹ ‹ ‹ ‹
▬▬▬▬▬▬▬▬▬▬▬▬▬▬▬   ANN  WHITEPAPER  FACEBOOK  TWITTER  YOUTUBE  FORUM   ▬▬▬▬▬▬▬▬▬▬▬▬▬▬▬
pbuva (OP)
Full Member
***
Offline Offline

Activity: 194
Merit: 100


View Profile
April 26, 2017, 08:52:06 PM
 #11

You need to provide some airflow for those 41-65 cards , with only one window that is not going to be a easy task
Do you have a right amount of electrical power need in that room ? with 65 cards it would be over 10KW , with 240 volts you need at least 50 amp to stay on the safe side , with 120 volt at least 90amp ...

I'm already dealing with an electrician, I have a drawer for bigger machines with 400 volts, it has 3 phases and it divides me into single phases for multiple drawers.

split that window area ,use one half for intake air  , another side for air outlet , use any commercial air mover, with highest possible CFM rating Smiley, use 2 of this or something similar :
http://refinishingonline.com/store/exhaust-fans
make sure the inlet and outlet in the window is pushing/pulling air to a from a different angle . So the exhausted air not coming back via the intake duct.
Place the exhaust duct close to the ceiling ( hot air moving up always ) , you still going to need a high CFM fan to circulating air inside that room ( http://www.northwoodswarehouse.com/q-standard-30-direct-drive-industrial-drum-fan-10380 )
I'll try this, and add another small air-suction fan to the door.

★ ★ ★ ★ ★   DeepOnion    Anonymous and Untraceable Cryptocurrency    TOR INTEGRATED & SECURED   ★ ★ ★ ★ ★
› › › › ›  JOIN THE NEW AIRDROP ✈️        VERIFIED WITH DEEPVAULT  ‹ ‹ ‹ ‹ ‹
▬▬▬▬▬▬▬▬▬▬▬▬▬▬▬   ANN  WHITEPAPER  FACEBOOK  TWITTER  YOUTUBE  FORUM   ▬▬▬▬▬▬▬▬▬▬▬▬▬▬▬
pbuva (OP)
Full Member
***
Offline Offline

Activity: 194
Merit: 100


View Profile
April 26, 2017, 08:55:25 PM
 #12

try using these they will move a lot of air 8 inches = 200 mm/20cm

 http://www.ebay.com/itm/8inch-Electric-Radiator-Fans-Universal-Push-Pull-Engine-Bay-Slim-Cooling-Fan-Kit-/192060629141?

you can use an atx or server psu to power them.


Thanks for the detailed answer, I appreciate it. I just want to ask, is not this small enough and probably weak?

★ ★ ★ ★ ★   DeepOnion    Anonymous and Untraceable Cryptocurrency    TOR INTEGRATED & SECURED   ★ ★ ★ ★ ★
› › › › ›  JOIN THE NEW AIRDROP ✈️        VERIFIED WITH DEEPVAULT  ‹ ‹ ‹ ‹ ‹
▬▬▬▬▬▬▬▬▬▬▬▬▬▬▬   ANN  WHITEPAPER  FACEBOOK  TWITTER  YOUTUBE  FORUM   ▬▬▬▬▬▬▬▬▬▬▬▬▬▬▬
RentGPU
Sr. Member
****
Offline Offline

Activity: 661
Merit: 258


View Profile
April 26, 2017, 10:35:23 PM
 #13

I am sure you have a door Smiley , if you can push the hot air through that door with some fans , and let the window for the intake air fans , with that you can make a good airflow through the room , what is the normal air temp. you have there in this room ?.

I have a plastic door, the material that is used for plastic windows. It is a fact that it could be used at least on a small fan that would suck the air, it is about 1 meter below ground level, there are stairs down. The cellar itself is within 18 degrees, but in summer it can be up to 40 degrees celsius outside.
You should use this door , i have a situations look like yours but i have a lot of windows but can't open any of them because there is insects and rats outside Smiley, so i used the door and put a wire window on it with two big fans pushing air outside the place , and one big fan to intake through a sheilded window with an air filter for dust...a rule of ventilation is to use a ratio of 1:2 intake outake fans or opposite.don't use the same number of intake and outake fans.....goodluck