Author Topic: APW3 power cord 220 volt question  (Read 458 times)
rosesrfree4u (OP)
Newbie
*
Offline Offline

Activity: 4
Merit: 0


View Profile
November 12, 2017, 09:03:45 PM
 #1

Hi, I had posted in another section of the forum and told to move here, hopefully this is the correct section, such a newbie Grin

I have a 220V outlet wired on it's own 30 Amp circuit, wired by an electrician.  He installed a 4-Prong Dryer outlet, the NEMA 14-30P.  I am trying to connect and run one APW3-1600 watt power supply for an S7.  I have the power supply, miner and I see the plug on the power supply is the standard computer C13.  I have found it next to impossible to find an adapter from C-13 to any style of 220 plug.  I'm pretty creative and handy and not above putting something together with a standard dryer cord and a dissected c-13 cord but I really want to do this right and with 220 - it's serious business.  Can I get some advice on the safest/best way to connect my APW3 to my 220 outlet.
I'm really hoping there is some way of doing this that doesn't involve me paying for another semester of college for the electrician's kids!  He was expensive!  
I'll only be running this one power supply on the outlet/circuit and am looking for a less is more approach at this point.  I didn't think sourcing the power cord would be such a big deal.
1713561335
Hero Member
*
Offline Offline

Posts: 1713561335

View Profile Personal Message (Offline)

Ignore
1713561335
Reply with quote  #2

1713561335
Report to moderator
1713561335
Hero Member
*
Offline Offline

Posts: 1713561335

View Profile Personal Message (Offline)

Ignore
1713561335
Reply with quote  #2

1713561335
Report to moderator
1713561335
Hero Member
*
Offline Offline

Posts: 1713561335

View Profile Personal Message (Offline)

Ignore
1713561335
Reply with quote  #2

1713561335
Report to moderator
In order to get the maximum amount of activity points possible, you just need to post once per day on average. Skipping days is OK as long as you maintain the average.
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
philipma1957
Legendary
*
Offline Offline

Activity: 4102
Merit: 7723


'The right to privacy matters'


View Profile WWW
November 12, 2017, 09:13:31 PM
Last edit: December 12, 2018, 01:05:57 AM by frodocooper
 #2

https://www.amazon.com/Whirlpool-PT400L-4-Feet-30-Amp-Dryer/dp/B002R0DXNW/ref=sr_1_6?

is this a match?

btw you should have asked us what receptacle to put in.

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
rosesrfree4u (OP)
Newbie
*
Offline Offline

Activity: 4
Merit: 0


View Profile
November 13, 2017, 12:42:54 AM
 #3

Yes, I agree I should have asked!!  Wink
I thought I had more time - he came by to do the work when I was out of town.
Now I'm going to try and work with what I got. 

Yes, that it the exact outlet style I have.  My limited understanding is that the hot are the two vertical prongs, top is ground (round hole) and bottom is neutral (90 degree angle hole "L").
Steamtyme
Legendary
*
Offline Offline

Activity: 1540
Merit: 2036


Betnomi.com Sportsbook, Casino and Poker


View Profile WWW
November 13, 2017, 03:55:42 PM
Last edit: December 12, 2018, 01:06:28 AM by frodocooper
 #4

This is the one instance I would say it sucks your electrician followed codes, did you tell him it was for a dryer? If he had run a 3 wire circuit you could have switched out the receptacle in a couple of minutes. How long is the cable run? You could always disconnect the circuit and fish through a new wire, by pulling through from the receptacle. I doubt they opened up your walls and tacked cable in place.
It might be better in the long run. If they didn't charge to much it might be worth having them come back


░░░░░▄▄██████▄▄
░░▄████▀▀▀▀▀▀████▄
███▀░░░░░░░░░░▀█▀█
███░░░▄██████▄▄░░░██
░░░░░█████████░░░░██▌
░░░░█████████████████
░░░░█████████████████
░░░░░████████████████
███▄░░▀██████▀░░░███
█▀█▄▄░░░░░░░░░░▄███
░░▀████▄▄▄▄▄▄████▀
░░░░░▀▀██████▀▀
Ripmixer
░░░░░▄▄██████▄▄
░░▄████▀▀▀▀▀▀████▄
███▀░░░░░░░░░░▀█▀█
███░░░▄██████▄▄░░░██
░░░░░█████████░░░░██▌
░░░░█████████████████
░░░░█████████████████
░░░░░████████████████
███▄░░▀██████▀░░░███
█▀█▄▄░░░░░░░░░░▄███
░░▀████▄▄▄▄▄▄████▀
░░░░░▀▀██████▀▀
QuintLeo
Legendary
*
Offline Offline

Activity: 1498
Merit: 1030


View Profile
November 14, 2017, 11:01:18 PM
Last edit: December 12, 2018, 01:06:46 AM by frodocooper
 #5

There should be no issue with replacing a NEMA 14 socket with a NEMA 6 (or L6) type socket.
The wiring is all there after all - just don't USE the neutral wire.

There ARE adapters (often used for motor homes) to connect a NEMA L6-30 plug to a NEMA 14 socket.
Places like Home Depot, Menards, or Lowes should have those in stock.

I'm no longer legendary just in my own mind!
Like something I said? Donations gratefully accepted. LYLnTKvLefz9izJFUvEGQEZzSkz34b3N6U (Litecoin)
1GYbjMTPdCuV7dci3iCUiaRrcNuaiQrVYY (Bitcoin)
philipma1957
Legendary
*
Offline Offline

Activity: 4102
Merit: 7723


'The right to privacy matters'


View Profile WWW
November 15, 2017, 04:14:02 AM
Last edit: December 12, 2018, 01:07:13 AM by frodocooper
 #6

https://www.ebay.com/itm/WELDER-3PRONG-L6-30R-RECEPTACLE-to-4PIN-NEMA14-30P-DRYER-PLUG-POWER-CORD-ADAPTER/222634699162?
https://www.ebay.com/itm/New-NEMA-L6-30P-to-C19-Power-Cord-8ft-Heavy-Duty-DataCenter-Twist-Lock-Cable/112588250963?
https://www.ebay.com/itm/HP-5xC13-Intelligent-PDU-Extension-Bars-Kit-Power-Strip-NIB-Sealed-2-each-pair/222714312441?

these 3 pieces work  next time ask us first.

if the right receptacle was used  the first listed would not be needed

oh forgot

order  some of these  at least 3 or 4

https://www.monoprice.com/product?p_id=24192

your circuit can do 3 s-9's

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
vk279
Full Member
***
Offline Offline

Activity: 195
Merit: 100



View Profile
March 15, 2018, 12:27:15 AM
Last edit: December 12, 2018, 01:07:45 AM by frodocooper
 #7

Hello
I am going to have electrician come in this weekend to get new 220 v connection for my S9.
I am wondering if this particular outlet is good:

https://www.homedepot.com/p/Eaton-30-Amp-250-Volt-6-30R-Power-Receptacle-5700N/206469352?cm_mmc=Shopping%7cVF%7cG%7c0%7cG-VF-PLA%7c&gclid=Cj0KCQjwkKPVBRDtARIsAA2CG6Fh219jITXd27rwN7H9q8c0wQ9DGaP3qRvugO7xdPLbZJIRjBJuYVAaAiaOEALw_wcB&gclsrc=aw.ds&dclid=CIqm5YeH7dkCFYt9AQodpVoPrg

Any other recommendations are appreciated.

Also please let me know if its ok to use old circuit breaker which was used for Electric range.

Thanks

QuintLeo
Legendary
*
Offline Offline

Activity: 1498
Merit: 1030


View Profile
March 15, 2018, 03:06:47 AM
Last edit: December 12, 2018, 01:08:03 AM by frodocooper
 #8

Most Power Distribution Units are designed to work with a LOCKING version of the NEMA 6 socket, not the standard non-locking version.
https://www.homedepot.com/p/Leviton-30-Amp-250-Volt-3-Wire-Locking-Single-Outlet-Black-R50-02620-0CS/300861599 would be the outlet you are looking for.

Reuse of the range breaker should be fine *IF* it is a 30 amp breaker and is still functional.

I'm no longer legendary just in my own mind!
Like something I said? Donations gratefully accepted. LYLnTKvLefz9izJFUvEGQEZzSkz34b3N6U (Litecoin)
1GYbjMTPdCuV7dci3iCUiaRrcNuaiQrVYY (Bitcoin)
vk279
Full Member
***
Offline Offline

Activity: 195
Merit: 100



View Profile
March 15, 2018, 06:08:24 PM
Last edit: December 12, 2018, 01:08:18 AM by frodocooper
 #9

Thanks for the reply.

Do I need a Power Distribution Unit?  I only have a one Antminer S9?
I have this Bitmain Power Supply Unit
https://www.amazon.com/Antminer-Power-Supply-APW3-Connectors/dp/B0733JRFVL

and I ordered this Power cord
https://www.amazon.com/gp/product/B0049XGZ8U/ref=oh_aui_detailpage_o00_s00?ie=UTF8&psc=1.

Thanks again

QuintLeo
Legendary
*
Offline Offline

Activity: 1498
Merit: 1030


View Profile
March 15, 2018, 08:20:10 PM
Last edit: December 12, 2018, 01:08:36 AM by frodocooper
 #10

If you're having an electrician do the work anyway, easier to just have him put *2* (or even 3 to 4 given your intended usage) standard NEMA 6-15 single outlets on the circuit to match your power cord.
Then you have somewhere to plug in a second (third fourth) S9 if you go that route.
Then you don't need a PDU at all.

I'm no longer legendary just in my own mind!
Like something I said? Donations gratefully accepted. LYLnTKvLefz9izJFUvEGQEZzSkz34b3N6U (Litecoin)
1GYbjMTPdCuV7dci3iCUiaRrcNuaiQrVYY (Bitcoin)
vk279
Full Member
***
Offline Offline

Activity: 195
Merit: 100



View Profile
March 16, 2018, 12:30:46 PM
Last edit: December 12, 2018, 01:08:51 AM by frodocooper
 #11

Thanks a lot for clarifying.  For now I have just one s9 antminer. I will be coming back with more questions in future as I might have going thru the process of setting up.

NotFuzzyWarm
Legendary
*
Offline Offline

Activity: 3612
Merit: 2494


Evil beware: We have waffles!


View Profile
December 11, 2018, 04:09:32 PM
 #12

Personally I use Stayonline.com for all my AC power cables. Made in USA, fully UL/CSA registered and any plug/socket combination you could ever want.

- For bitcoin to succeed the community must police itself -    My info useful? Donations welcome! 1FuzzyWc2J8TMqeUQZ8yjE43Rwr7K3cxs9
 -Sole remaining active developer of cgminer, Kano's repo is here
-Support Sidehacks miner development. Donations to:   1BURGERAXHH6Yi6LRybRJK7ybEm5m5HwTr