November 27, 2017, 06:42:31 AM
 #1

This may be covered somewhere but I'm new here so hope you will bear with me.
I have 3 Asic miners and think it will be more efficient to run 220-240v so am trying to determine how to use the range plug which is on a separate circuit and split it into 3 or 4.  I thought I would just use a range cord 10-50P (3 prong non-grounded) and wire it into a splitter like this https://www.amazon.com/Conntek-1-5-Feet-Connector-Generator-Extension/dp/B005HSK29E but am not sure how the 3 prong non-grounded wire would be used in a conversion to a ground plug where the 3 prong has 2 120v and one neutral. Anyone?Thanks
1714042302
Hero Member
*
Offline Offline

Posts: 1714042302

View Profile Personal Message (Offline)

Ignore
1714042302
Reply with quote  #2

1714042302
Report to moderator
Even in the event that an attacker gains more than 50% of the network's computational power, only transactions sent by the attacker could be reversed or double-spent. The network would not be destroyed.
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
1714042302
Hero Member
*
Offline Offline

Posts: 1714042302

View Profile Personal Message (Offline)

Ignore
1714042302
Reply with quote  #2

1714042302
Report to moderator
1714042302
Hero Member
*
Offline Offline

Posts: 1714042302

View Profile Personal Message (Offline)

Ignore
1714042302
Reply with quote  #2

1714042302
Report to moderator
Steamtyme
Legendary
*
Offline Offline

Activity: 1540
Merit: 2036


Betnomi.com Sportsbook, Casino and Poker


View Profile WWW
November 27, 2017, 01:14:57 PM
 #2

Hey there,

If you can elaborate a little we could probably help you sort this out.
What type of miners are you using bitmain? Avalon? Ebit?
Also what is the room setup? If toy can change up the circuit I would go this route instead of using splitters.
Either way you should be okay on a 30 amp circuit. And if you can I would suggest setting it up this way. 30 amp 2 pole breaker to a l6-30 receptacle.
 Now if you grab a PDU, I bought mine used on eBay. You will want one rated for 220-240, and 30 amps ( I think most say 24) which is the max you want to put the 30 amp circuit under constant load anyways.
Then you just have to match the cord from the PDU to the PSU for each miner.


░░░░░▄▄██████▄▄
░░▄████▀▀▀▀▀▀████▄
███▀░░░░░░░░░░▀█▀█
███░░░▄██████▄▄░░░██
░░░░░█████████░░░░██▌
░░░░█████████████████
░░░░█████████████████
░░░░░████████████████
███▄░░▀██████▀░░░███
█▀█▄▄░░░░░░░░░░▄███
░░▀████▄▄▄▄▄▄████▀
░░░░░▀▀██████▀▀
Ripmixer
░░░░░▄▄██████▄▄
░░▄████▀▀▀▀▀▀████▄
███▀░░░░░░░░░░▀█▀█
███░░░▄██████▄▄░░░██
░░░░░█████████░░░░██▌
░░░░█████████████████
░░░░█████████████████
░░░░░████████████████
███▄░░▀██████▀░░░███
█▀█▄▄░░░░░░░░░░▄███
░░▀████▄▄▄▄▄▄████▀
░░░░░▀▀██████▀▀
fanatic26
Hero Member
*****
Offline Offline

Activity: 756
Merit: 560


View Profile
November 27, 2017, 04:33:53 PM
 #3

If you share the same circuit as your range you will pop that circuit every time you try and cook something with miners running. You need to put the mienrs on their own separate circuit.

Stop buying industrial miners, running them at home, and then complaining about the noise.