I did not disgree with the general principle, you said his farm will be free of humidity, I corrected the "term".
humidity does not go away with higher temp
If the outside temp is 20c the maximum amount of water per cubic meter the air can hold is 17.3 g/m³ that gives it an RH of 100%, if your meter reads 50% RH it simply means there is 8.65 grams of water per cubic meter in the air.
Now go an heat that air to 100c, how much water/humidity will be in the air? the same 8.65 grams of water, however, since air at 100c can hold 598 grams of water per m3, then 8.65 grams / 598 grams gives you 1.45%, so RH drops from 50% to 1.45% but actual/absolute humidity doesn't change.
Now speaking of low RH, there is a HUGE risk of ESD when running electronics at low RH, when we ran our closed-AC-cooled farm we ran into low RH issues because ACs do lower absolute humidity which lowers RH, on most universal standards they say don't go below 20% RH, I contacted one of MicroBT's engineers and he said I could safely ignore that and go to as low as 5%, ours was at about 7% and we wanted to keep it above 10% to stay safe, we used a very unsophisticated mechanism to bring bring RH to 10%, we just dropped a few large buckets full of water

and filled them with water once in a while, ideally you want something with huge surface but we just used what we got and had RH almost always above 10% and never had a problem despite many professionals advising against it.