Author Topic: Utility tariffs that name crypto mining: Idaho, North Dakota, Texas, BC  (Read 71 times)
strategiccryptoreserve (OP)
Newbie
*
Offline

Activity: 56
Merit: 0


View Profile WWW
September 26, 2026, 01:39:02 PM
 #1

Utility tariffs that now name crypto mining: what they mean for your power bill

More US utilities are writing large-load tariffs aimed at data centres, and a few of them name Bitcoin mining outright or set thresholds that catch mid-sized mining sites. If you run or plan hashrate, these change your real cost per kWh, your minimum-take commitments and how long you're locked in. Here are the ones most relevant to miners, each linked to a full breakdown:



Idaho: Idaho Power Schedule 20 ("Speculative High-Density Load")
  • Written for speculative high-density loads and explicitly includes cryptocurrency mining.
  • Effective January 1, 2024 (docket IPC-E-21-37).
  • Details: Idaho large-load tariff breakdown

North Dakota: MDU High Density Contracted Demand Response Tariff
  • Applies from 10 MW of high-density computer processing demand with an 85% minimum load factor, which is much lower than most states' thresholds and squarely in mining-site territory.
  • Requires a contract with MDU. Two Applied Digital sites (including a 530 MW site in Ellendale) already run under this framework.
  • Details: North Dakota large-load tariff breakdown

Texas: El Paso Electric Schedule 27 and SWEPCO's ES-LL contract
  • Facilities with 75 MW or more of annual peak demand fall under El Paso Electric's new Schedule 27 High Load Factor Large Power Service, which comes with an annual load-factor requirement.
  • Details: Texas large-load tariff breakdown

British Columbia: the opposite approach
  • BC has permanently banned new grid connections for crypto mining. Existing small miners are on residential tiered rates, and anything past the Tier 1 allowance is billed at 14.08 cents/kWh (Tier 2).
  • Real per-ASIC running costs at those rates, from our own small Comox Valley setup: BC Hydro rates for crypto mining 2026



Compare sites yourself (free)
We built a free calculator that applies each state's and province's power rates and large-load tariff rules to the same build, and returns CapEx, annual power cost and payback. It covers all 50 US states plus DC and nine Canadian provinces. No sign-up:
https://strategiccryptoreserve.ca/ai-build-configurator.html

Questions for miners here:
  • Is anyone running under Idaho's Schedule 20 or MDU's tariff? How do the minimum-take terms work in practice?
  • What all-in cost per kWh are you actually paying, and in which state or province?
  • Which states should we break down next?



Disclosure: the calculator and the tariff pages are ours (Strategic Crypto Reserve). We've also applied for a grant to add crypto payments to the calculator: Questbook proposal. Feedback or support there is welcome but not the point of this thread. Figures are planning estimates from public tariff filings; confirm terms with the utility before committing capital.
NotFuzzyWarm
Legendary
*
Offline

Activity: 4494
Merit: 3591


Evil beware: We have waffles!


View Profile
Today at 02:02:32 AM
Last edit: Today at 08:13:38 PM by NotFuzzyWarm
 #2

I see this more of blanket tariffs and rules mainly aimed at AI hyper data centers: most start at over 1GW. Compared to that, crypto farms while drawing 'only' up to several 100's of MW, still makes them a very significant load and the grid infra has to be able to support it. Crypto farms just happen to (rightly) fall into the same category as AI sites because of their very significant high-density loads.

Even the largest mining farms are just a fraction of what AI centers will pull from a states power grid. Case in point, Michigan has 5 AI centers under construction: The smallest has a final build out of 1.2GW and the largest will be 2.5GW.

The point of the new tarrifs is to set in stone who pays for the needed power and the infra to generate and carry it. In most states that is negotiated on a site by site basis. In Michigan after long negotiations with each company, the data centers are paying for all of the new transmission lines, substations, and any additional solar/wind/whatever power plants needed and rates are set so the Public does not pay for any of the power. Additionally, as is done in Texas, rules are setup regarding power cutbacks so power can be used elsewhere when needed to cover severe weather events.


- For bitcoin to succeed the community must police itself -    My info useful? Donations welcome!  3NtFuzyWREGoDHWeMczeJzxFZpiLAFJXYr
 -Sole remaining active Primary developer of cgminer, Kano's repo is here  Discord support invite at https://kano.is/
-Support Sidehacks miner development. Donations to:   1BURGERAXHH6Yi6LRybRJK7ybEm5m5HwTr
strategiccryptoreserve (OP)
Newbie
*
Offline

Activity: 56
Merit: 0


View Profile WWW
Today at 06:25:43 PM
 #3

I see this more of blanket tariffs and rules mainly aimed at AI hyper data centers: most start at over 1GW. Compared to that crypto farms, while drawing 'only' up to several 100's of MW, still makes them a very significant load and the grid infra has to be able to support it. Crypto farms just happen to (rightly) fall into the same category as AI sites because of their very significant high-density loads.

Even the largest mining farms are just a fraction of what AI centers will pull from a states power grid. Case in point, Michigan has 5 AI centers under construction: The smallest has a final build out of 1.2GW and the largest will be 2.5GW.

The point of the new tarrifs is to set in stone who pays for the needed power and the infra to generate and carry it. In most states that is negotiated on a site by site basis. In Michigan after long negotiations with each company, the data centers are paying for all of the new transmission lines, substations, and any additional solar/wind/whatever power plants needed and rates are set so the Public does not pay for any of the power. Additionally, as is done in Texas, rules are setup regarding power cutbacks so power can be used elsewhere when needed to cover severe weather events.

Agreed, AI hyperscale is what these tariffs were written for. The problem for miners is where the thresholds are set. The target is 1 GW sites, but the trigger point is much lower:

  • TVA (Tennessee): data centre load above 5 MW
  • MDU (North Dakota): 10 MW at an 85% load factor
  • Nebraska's Large Load Customer Regulation Act: 20 MW at one site
  • AEP Ohio and Dominion GS-5 (Virginia): 25 MW
  • El Paso Electric Schedule 27 (Texas): 75 MW

So a 20-50 MW mining site that nobody had in mind still lands in the same rate class as a 2 GW campus. Idaho's Schedule 20 is the exception. That docket dates from 2021, before the AI wave, and it names crypto mining outright, so it isn't just AI spillover.

Quote from: NotFuzzyWarm
The point of the new tarrifs is to set in stone who pays for the needed power and the infra to generate and carry it.

Yes, and for miners the real issue is how they pay. Most of these tariffs include a minimum-take clause. AEP Ohio's large-load customers pay for at least 85% of the energy they expect to need each month, even if they use less. From 2027, Dominion's GS-5 bills 85% of contracted T&D demand and 60% of generation demand whether you draw it or not. That's fine for an AI campus that runs flat out. A miner's economics depend on switching off when hashprice drops or power spikes, and a take-or-pay floor turns those curtailment savings into a cost. You end up paying for power you chose not to use.

Quote from: NotFuzzyWarm
Additionally, as is done in Texas, rules are setup regarding power cutbacks so power can be used elsewhere when needed to cover severe weather events.

This is where miners have a real argument that AI sites don't. An AI data centre wants 99.99% uptime and treats a forced cutback as a crisis. A mining farm can go from full load to zero in minutes and happily does. MDU's tariff is literally called a Demand Response tariff for that reason. The flexibility is part of the deal, and that's why its threshold can sit at 10 MW. We think miners should push for that kind of structure (curtailable in exchange for no minimum-take) rather than accept hyperscale terms that assume a load that never shuts off.

On Michigan: the one we've covered in detail is the OpenAI/Oracle/Related Digital campus in Saline Township, about 1.4 GW and $7B, with around $300M a year in claimed affordability benefits for existing customers. Your point about the developers funding the transmission and substations matches what's in those filings. The tariffs there are Consumers Energy's Rate GPD, DTE's Rate D11 and I&M's Tariff LP.

Do you know if any mining sites in Michigan have been put under GPD or D11 yet, or are they all still on standard industrial rates? That's exactly the kind of real-world detail we'd like to add to the state pages.
FP91G
Legendary
*
Offline

Activity: 2506
Merit: 1715


#kycfree 🗽


View Profile
Today at 06:42:20 PM
 #4

I saw a rate of 14.08 cents/kWh, and when it comes to ASIC mining, there is no point in even starting under those conditions. It would be a guaranteed disaster unless the price of Bitcoin starts to skyrocket.
However, I see from US news reports that the government is willing to support data centers and sell them surplus electricity at a discount.

▄███████████████████████▄
██████████▀███▄██████████
████████▀████▀▀██████████
█████████████████▀███████
███████▀▄████▄▄██████████
██████████▄███▀██████████
████████▐███████▌████████
██████████▄███▀██████████
██████████▀▀████▀▄███████
███████▄█████████████████
██████████▄▄████▄████████
██████████▀███▄██████████
▀███████████████████████▀
 
 MoBit 
████
██
██
██
██
██
██
██
██
██
██
██
████
 NO   LOGS
 
 LOW  FEES
 
 PGP  GUARANTEE
████
██
██
██
██
██
██
██
██
██
██
██
████
▄██████▄▄▄
█████████████▄▄
███████████████
███████████████
███████████████
███████████████
███░░█████████
███▌▐█████████
█████████████
███████████▀
██████████▀
████████▀
░▀▀██▀▀
NotFuzzyWarm
Legendary
*
Offline

Activity: 4494
Merit: 3591


Evil beware: We have waffles!


View Profile
Today at 07:10:28 PM
Last edit: Today at 07:41:11 PM by NotFuzzyWarm
 #5

I only found info on there being 3 large mining farms in MI, all located in the Upper Peninsula, https://bridgemi.com/business-watch/crypto-mines-noisy-nuisance-some-should-michigan-regulate-them/ Regarding their operations, no mention of their rates but;
Quote
In the Upper Peninsula, three crypto mines — one in Newberry and two in Dafter — operate within the service area of Cloverland Electric Cooperative, spokesperson Abby Moran said in an email to Bridge.

Cloverland has ample capacity to service the mines, Moran said. The mines run on an interruptible rate, meaning they must shut down during peak demand for the grid. The mines add to a shrinking customer base for the utility, helping to offset rising infrastructure costs.

“Without their large, consistent load, members would face significantly higher rate increases,” Moran said.
Emphasis mine. The article also mentions that regulations are being worked on to allow unused (and often remote) gas wells to be used for on-site mining operations.

- For bitcoin to succeed the community must police itself -    My info useful? Donations welcome!  3NtFuzyWREGoDHWeMczeJzxFZpiLAFJXYr
 -Sole remaining active Primary developer of cgminer, Kano's repo is here  Discord support invite at https://kano.is/
-Support Sidehacks miner development. Donations to:   1BURGERAXHH6Yi6LRybRJK7ybEm5m5HwTr
strategiccryptoreserve (OP)
Newbie
*
Offline

Activity: 56
Merit: 0


View Profile WWW
Today at 08:41:05 PM
 #6

I saw a rate of 14.08 cents/kWh, and when it comes to ASIC mining, there is no point in even starting under those conditions. It would be a guaranteed disaster unless the price of Bitcoin starts to skyrocket.
However, I see from US news reports that the government is willing to support data centers and sell them surplus electricity at a discount.

Since we operate under those very conditions .14 cents in BC Canada BCHYDRO has slightly more competitive commercial plans at .12 cents thats canadian of course still the law itself as it stands puts a moratorium on new data center builds on large industrial scales however super small projects still mining bitcoin not professional like marathon etc are still allowed to operate.  While we are positive that number has to be massive in undertaking to product a ban at the government of canada we aren't there yet and wont be it still has to be a hobby of ours until the laws change.

Of course you can check out the website and research our current applications regarding bitcoin mining we are starting small and just covering everything as thouroughly as we can without going to industry scales that are not allowed according to bchydro and government rules.

OF course a work around would be creating our own power so some do that exact thing like with bloom energy because they can't stand downtime and can pay up to .24 cents and remain profitable because of AI retrofits.

Not sure do you plan on building or have a farm already and where in the world are you?
strategiccryptoreserve (OP)
Newbie
*
Offline

Activity: 56
Merit: 0


View Profile WWW
Today at 08:44:35 PM
 #7

I only found info on there being 3 large mining farms in MI, all located in the Upper Peninsula, https://bridgemi.com/business-watch/crypto-mines-noisy-nuisance-some-should-michigan-regulate-them/ Regarding their operations, no mention of their rates but;
Quote
In the Upper Peninsula, three crypto mines — one in Newberry and two in Dafter — operate within the service area of Cloverland Electric Cooperative, spokesperson Abby Moran said in an email to Bridge.

Cloverland has ample capacity to service the mines, Moran said. The mines run on an interruptible rate, meaning they must shut down during peak demand for the grid. The mines add to a shrinking customer base for the utility, helping to offset rising infrastructure costs.

“Without their large, consistent load, members would face significantly higher rate increases,” Moran said.
Emphasis mine. The article also mentions that regulations are being worked on to allow unused (and often remote) gas wells to be used for on-site mining operations.


You would need to research on our website some info regarding the latest projects in Alberta doing that very thing.  The new builds for ai datacenters in particular are the new standard and they are using LPG to power the generators for the power.