Is this 3 phase or single phase? Huge difference!
600 volt is 3 phase the transformers I have links for are Wye 600 to 208/120. I have more then basic knowledge but I am not an expert in this field.
I am not an engineer or electrician.
Here's how I think the math works, and I will explain each step:
600 volts RMS < ----This is ACROSS the phases, not phase to neutral
347 volts RMS <--- Phase to neutral
400 amps is 3-phase < ---- This is the most important part.
You have 3 phase power but are running 1 phase units. Using
https://canadatransformers.com/transformer-phase/ to calculate KW/KVA using all 3 phases:
600v x 400 amps = 415.69 KVA
(600 x 400 x 1.732)
Calculate using a single phase:
347v x 400 amps = 138.8 KVA
Yup checks out, it's 1/3 of the 3 phase. So we have a total system KVA of 415.69. To translate to KW we need to multiply by the power factor:
415.69 KVA x 0.99 = 411.5 KW
So we have a total system KW available of 411.5, multiply by 0.8 (80%) to get available power:
411.5 * 0.8 = 329.23 KW available
Divide by 1.475 KW:
329.23 / 1.475 = 223 units
That's a lot!
Where are you located? I'm in Winnipeg. What is the size of the transformer in kva?
Edit: I did not include transformer losses since we need to knock down that 600v further.