With that much space, do you think I could install 40KW worth of Antminer S5's w/o having to worry about a cooling system? SE Idaho isn't that hot of a place (mid 90's in July, but cooler the rest of the year).
40kw = 40 x 4000 btu = 160,000 btu
my ac is 25000 btu and will drop a 2000 square foot home 10f in 10 hours say 82 to 72 f
so your 160000 btu of heat would jump a 14000 square foot space 10f say 82 f to 92 f
I think you need two big fans like these
http://www.lowes.com/pd_416730-11292-SFDC2-600T_1z11on0__?productId=4755305&pl=1&Ntt=fans1 brings air in 1 brings air out
shed 150 ft long
____________________________________________
l l
l l
door or window l
F>may need a fan here? push-fan>>>Miners>>>pull-fan>> window door
l l
l l
l___________________________________________l
the push fan and the pull could be moved around for best spots