February 17, 2013, 04:31:46 PM
 #1

When will ordering open for the hashing modules?

Is a power supply upgrade required to power all 4 modules?

In Satoshi We Trust.
rudrigorc2
Legendary
*
Offline Offline

Activity: 1064
Merit: 1000



View Profile
February 17, 2013, 05:25:29 PM
Last edit: February 18, 2013, 07:06:37 AM by rudrigorc2
 #2

When will ordering open for the hashing modules?

Is a power supply upgrade required to power all 4 modules?

see, same question.
I would put at least a 650watts powering the default 3 modules. So if the unit is upgrade ready, is it? thats 1 module more the psu must be at least 850watts.

If were my choice I would like to purchase without PSUs, bit cheaper, much lighter shipping that way and I could plan my upgrade path while using some ATX already have here. Would that void the warranty? I dont know.
xempew (OP)
Jr. Member
*
Offline Offline

Activity: 45
Merit: 10



View Profile
February 18, 2013, 03:31:19 PM
 #3

From another thread...

the units are 620W max, I mean the power supply shipped it's a 650 Antec, so buy UPS accordingly.

Based on the information provided above, the Avalon units are not equipped to handle a 4th hashing module out-of-the-box.

In Satoshi We Trust.
mrb
Legendary
*
Offline Offline

Activity: 1512
Merit: 1028


View Profile WWW
February 18, 2013, 07:19:52 PM
 #4

From another thread...

the units are 620W max, I mean the power supply shipped it's a 650 Antec, so buy UPS accordingly.

Based on the information provided above, the Avalon units are not equipped to handle a 4th hashing module out-of-the-box.

The Avalon PSU would be running only 3.5% over its rated capacity with 4 modules. Not great, but it should be able to run 24/7 at least 1 or 2 years at this workload, assuming it is a normal quality PSU rated to run at its full power. The 1- to 2-year lifetime can be derived from the typical 10k hour lifetime of a PSU's electronic components such as capacitors.

nghzang reported a 82% efficiency of the PSU and a 5-20 Watt power consumption for the fans. Therefore:
(620 (Watt at the wall) * .82 (efficiency) - ~10 (Watt for the fans)) / 3 (modules) = 166 Watt at 12V per module

A 4-module Avalon would consume:
166 (Watt per module) * 4 (modules) + 10 (Watt for the fans) = 674 Watt at 12V which is 3.5% higher than 650W

674 Watt at 12V (output) translates, given a .82 efficiency, to 822 Watt at the wall (input), but do not forget that a PSU wattage rating refers to its output power, not input power.
Bogart
Legendary
*
Offline Offline

Activity: 966
Merit: 1000


View Profile
February 18, 2013, 08:03:53 PM
 #5

<-- Is hoping for a batch 2 Avalon with 6 module bays.

"All safe deposit boxes in banks or financial institutions have been sealed... and may only be opened in the presence of an agent of the I.R.S." - President F.D. Roosevelt, 1933
crazyates
Legendary
*
Offline Offline

Activity: 952
Merit: 1000



View Profile
February 18, 2013, 10:06:13 PM
 #6

<-- Is hoping for a batch 2 Avalon with 6 module bays.
Where you gonna find a PSU that can power 6 modules?

Tips? 1crazy8pMqgwJ7tX7ZPZmyPwFbc6xZKM9
Previous Trade History - Sale Thread
DeathAndTaxes
Donator
Legendary
*
Offline Offline

Activity: 1218
Merit: 1079


Gerald Davis


View Profile
February 18, 2013, 10:16:16 PM
 #7

<-- Is hoping for a batch 2 Avalon with 6 module bays.
Where you gonna find a PSU that can power 6 modules?

166W per module + 20W for fans & controller.

6*166W + 20W ~= 1016W DC.  Note the AC load will be higher but ATX PSU are rated by the DC wattage they can deliver not the AC load required to produce that DC load.   A high end PSU like a SeaSonic X1250 (or possibly even X1050) should be able to drive it just fine.

http://www.newegg.com/Product/Product.aspx?Item=N82E16817151109

One should be looking for a good high quality brand, single massive 12V rail, and power distribution rating that allows ~100% load on 12V rail.  Using some off brand, multi railed junk PSU is a good way to destroy it but SeaSonic 1250s worked fine for me pushing >1000W DC loads (quad 5970s rigs).

Someone running a multi-rig setup should really but running off a dedicated 30A 240V circuit.  Good datacenter PDU with safe locking connector can be found on ebay (i.e. AP9571) so no reason not to do it right.

30A *80% derate * 240V = 5760W AC
1016W DC / 0.92 = 1116W AC * 5 = 5760W AC.

Five 6 module Avalon "could" be powered by a single 30A 240V circuit.  5KW is a lot of heat though so make plans accordingly.
crazyates
Legendary
*
Offline Offline

Activity: 952
Merit: 1000



View Profile
February 19, 2013, 03:48:21 AM
 #8

<-- Is hoping for a batch 2 Avalon with 6 module bays.
Where you gonna find a PSU that can power 6 modules?

166W per module + 20W for fans & controller.

6*166W + 20W ~= 1016W DC.  Note the AC load will be higher but ATX PSU are rated by the DC wattage they can deliver not the AC load required to produce that DC load.   A high end PSU like a SeaSonic X1250 (or possibly even X1050) should be able to drive it just fine.

http://www.newegg.com/Product/Product.aspx?Item=N82E16817151109

One should be looking for a good high quality brand, single massive 12V rail, and power distribution rating that allows ~100% load on 12V rail.  Using some off brand, multi railed junk PSU is a good way to destroy it but SeaSonic 1250s worked fine for me pushing >1000W DC loads (quad 5970s rigs).

Someone running a multi-rig setup should really but running off a dedicated 30A 240V circuit.  Good datacenter PDU with safe locking connector can be found on ebay (i.e. AP9571) so no reason not to do it right.

30A *80% derate * 240V = 5760W AC
1016W DC / 0.92 = 1116W AC * 5 = 5760W AC.

Five 6 module Avalon "could" be powered by a single 30A 240V circuit.  5KW is a lot of heat though so make plans accordingly.

Jeff said his 3 module unit pulls 620W. Take away the 20W for the fans and controller, and you're looking at 200W for each module, not 166W. That means 6 modules is  (6x200 + 20) 1220W. You could run that on a 1250W, but you'd be pushing the limits. You're either looking at a $300-400 PSU, or 2 750W PSUs.

Tips? 1crazy8pMqgwJ7tX7ZPZmyPwFbc6xZKM9
Previous Trade History - Sale Thread
mrb
Legendary
*
Offline Offline

Activity: 1512
Merit: 1028


View Profile WWW
February 19, 2013, 04:10:02 AM
 #9

Jeff said his 3 module unit pulls 620W. Take away the 20W for the fans and controller, and you're looking at 200W for each module, not 166W. That means 6 modules is  (6x200 + 20) 1220W. You could run that on a 1250W, but you'd be pushing the limits. You're either looking at a $300-400 PSU, or 2 750W PSUs.

No. DeathAndTaxes is right. He took the 166W from my computation: https://bitcointalk.org/index.php?topic=144648.msg1537338#msg1537338
Basically you fail to take into account the PSU efficiency. For example a 1000W PSU could power 6 modules (100% load), but if it is 82% efficient it would pull 1220W from the wall. All this without exceeding its ratings.
DeathAndTaxes
Donator
Legendary
*
Offline Offline

Activity: 1218
Merit: 1079


Gerald Davis


View Profile
February 19, 2013, 05:12:38 AM
 #10

Jeff said his 3 module unit pulls 620W. Take away the 20W for the fans and controller, and you're looking at 200W for each module, not 166W. That means 6 modules is  (6x200 + 20) 1220W. You could run that on a 1250W, but you'd be pushing the limits. You're either looking at a $300-400 PSU, or 2 750W PSUs.

Simple version.  AC vs DC.  I even included DC vs AC in my calculations.  It helps to prevent errors like in your post above.
Measured at the wall = AC load.
Power supplies are rated on DC load.


crazyates
Legendary
*
Offline Offline

Activity: 952
Merit: 1000



View Profile
February 19, 2013, 07:18:33 AM
 #11

Ah you guys were right. I was looking at the at the wall numbers as the draw from the PSU numbers. My bad.

Tips? 1crazy8pMqgwJ7tX7ZPZmyPwFbc6xZKM9
Previous Trade History - Sale Thread
bvoid
Member
**
Offline Offline

Activity: 77
Merit: 10



View Profile
February 19, 2013, 12:12:49 PM
 #12

It's just a ATX PSU? It should be easy replacable no?
DeathAndTaxes
Donator
Legendary
*
Offline Offline

Activity: 1218
Merit: 1079


Gerald Davis


View Profile
February 19, 2013, 07:48:00 PM
 #13

It's just a ATX PSU? It should be easy replacable no?

Yes it is just a normal ATX PSU and it should be easily replaceable.

Personally I wish BitSyncom would consider selling just the modules and controllers.  I would gladly supply my own case, fans, and PSU.  Save on the cost and shipping.  Then again as long as they keep selling out within 24 hours I doubt they have much motivation to change what is working. Smiley
cypherdoc
Legendary
*
Offline Offline

Activity: 1764
Merit: 1002



View Profile
February 19, 2013, 09:46:54 PM
 #14


Someone running a multi-rig setup should really but running off a dedicated 30A 240V circuit.  Good datacenter PDU with safe locking connector can be found on ebay (i.e. AP9571) so no reason not to do it right.


so if i run three 4 module Avalons that would be 4*166W+20W=684W*3=2052W, correct?  would you install a dedicated 30A 240V circuit for that with a 3 plug MOV surge protector?
klondike_bar
Legendary
*
Offline Offline

Activity: 2128
Merit: 1005

ASIC Wannabe


View Profile
February 19, 2013, 10:15:14 PM
 #15


Someone running a multi-rig setup should really but running off a dedicated 30A 240V circuit.  Good datacenter PDU with safe locking connector can be found on ebay (i.e. AP9571) so no reason not to do it right.


so if i run three 4 module Avalons that would be 4*166W+20W=684W*3=2052W, correct?  would you install a dedicated 30A 240V circuit for that with a 3 plug MOV surge protector?

30A on 240V is over 7KW. If you only need to run 2052W, then 15A would be sufficient

24" PCI-E cables with 16AWG wires and stripped ends - great for server PSU mods, best prices https://bitcointalk.org/index.php?topic=563461
No longer a wannabe - now an ASIC owner!
Gomeler
Hero Member
*****
Offline Offline

Activity: 697
Merit: 500



View Profile
February 19, 2013, 11:02:57 PM
 #16


Someone running a multi-rig setup should really but running off a dedicated 30A 240V circuit.  Good datacenter PDU with safe locking connector can be found on ebay (i.e. AP9571) so no reason not to do it right.


so if i run three 4 module Avalons that would be 4*166W+20W=684W*3=2052W, correct?  would you install a dedicated 30A 240V circuit for that with a 3 plug MOV surge protector?

30A on 240V is over 7KW. If you only need to run 2052W, then 15A would be sufficient

But if you're having an electrician install a new drop from the breaker then check the cost difference. If you ever plan on expanding then don't get a drop that fits your power consumption at the time of purchase. If you're considering 4 Avalons then do yourself the favor and consider that you'll likely continue to expand your mining operation so long as it is profitable.
cypherdoc
Legendary
*
Offline Offline

Activity: 1764
Merit: 1002



View Profile
February 19, 2013, 11:11:30 PM
 #17

good suggestions
Dalkore
Legendary
*
Offline Offline

Activity: 1330
Merit: 1026


Mining since 2010 & Hosting since 2012


View Profile WWW
February 19, 2013, 11:16:12 PM
 #18

It would be nice to have a hobby-kit for Avalon modules so people could build custom mining rigs with ASICs. 

Hosting: Low as $60.00 per KW - Link
Transaction List: jayson3 +5 - ColdHardMetal +3 - Nolo +2 - CoinHoarder +1 - Elxiliath +1 - tymm0 +1 - Johnniewalker +1 - Oscer +1 - Davidj411 +1 - BitCoiner2012 +1 - dstruct2k +1 - Philj +1 - camolist +1 - exahash +1 - Littleshop +1 - Severian +1 - DebitMe +1 - lepenguin +1 - StringTheory +1 - amagimetals +1 - jcoin200 +1 - serp +1 - klintay +1 - -droid- +1 - FlutterPie +1
Beepbop
Full Member
***
Offline Offline

Activity: 126
Merit: 100



View Profile
February 19, 2013, 11:46:17 PM
 #19

They could have sold the modules and controllers even without the heat sinks, to keep the weight down. But I think they have to assemble the systems for final testing anyway, so disassembling is only more work to do for both them and the customer.

I would be genuinely interested to see people start water cooling their modules though. Maybe with geothermal or below ambient cooling. There's not really any need to do that except perhaps if the ASICs can be overclocked or draw less power when cooled. Realistically, though, you'd be stupid to do too much tinkering with it as long as it mines at high return levels. The time for optimising will be when power cost starts catching up with yield.
shmadz
Legendary
*
Offline Offline

Activity: 1512
Merit: 1000


@theshmadz


View Profile
February 20, 2013, 01:10:39 AM
 #20


Someone running a multi-rig setup should really but running off a dedicated 30A 240V circuit. 

Does anyone know what circuit your typical electric stove runs off? in north america? specifically Canada?

(*side note, I don't use my stove, but the plug on the front of it seems to run my AC quite nicely Wink