I am not an electrician , I am a technician of sorts but I don't have an answer on how many 6 gpu rigs running 1200 watt power supply could run on a circuit , in a standard American home. Yes I have tried googling this. Anyone have any kind pointers on how to figure this out ?
|
|
|
|
|
|
|
You can see the statistics of your reports to moderators on the "Report to moderator" pages.
|
|
|
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
|
|
toptek
Legendary
Offline
Activity: 1274
Merit: 1000
|
|
May 28, 2017, 07:13:43 PM Last edit: May 28, 2017, 07:42:53 PM by toptek |
|
I am not an electrician , I am a technician of sorts but I don't have an answer on how many 6 gpu rigs running 1200 watt power supply could run on a circuit , in a standard American home. Yes I have tried googling this. Anyone have any kind pointers on how to figure this out ?
is your home a 200 amp service ?. I think you Have about 4000 kwh to play with..use 220 lines if you can ...you should be able to put two 6 card rigs per 220/240 40 amp line... id say maybe 5 tops in rigs, 6 is pushing it. I'm taking my Home farm to 4 4 card rigs because i also run two Script miners that total @ 300 MH . i can make if i can deal with it all on for a month closes to 2 k ... before power cost with the price of coins going up,even more over time. Also With coins going up like they are i may even look into a few upgrade kits some one is selling on the BTC forums ( not side hack, I don't think he is yet . ) for my old S3, C1, two S1, and two S5 heat sinks with the controller, no hash boards.. I have laying around for BTC mining .
|
|
|
|
philipma1957
Legendary
Offline
Activity: 4116
Merit: 7851
'The right to privacy matters'
|
|
May 28, 2017, 07:28:42 PM |
|
a 15 amp 120 volt circuit can run 1x 6 card rig
so if you have a 200 amp home with only 120 volts setup
how many rigs you can run comes down to:
do you run an A/C?
do you run an electric clothes dryer or a gas one?
do you have an electric stove or a gas one?
do you hear your hot water with electric or gas ?
I have all gas so I can do more then many home with all electric. a/c is electric.
I also setup 240 volts for mining which allows for more.
I run as high as 24 amps at 240 in the winter
I run at 10 amps in the summer.
that is 10 1080 ti's and 2 1070 's
|
|
|
|
Mister305 (OP)
|
|
May 28, 2017, 07:42:46 PM |
|
I am not an electrician , I am a technician of sorts but I don't have an answer on how many 6 gpu rigs running 1200 watt power supply could run on a circuit , in a standard American home. Yes I have tried googling this. Anyone have any kind pointers on how to figure this out ?
is your home a 200 amp service ?. I think you Have about 4000 kwh to play with..use 220 lines if you can ...you should be able to put two 6 card rigs per 220/240 40 amp line... id say maybe 5 tops in rigs, 6 is pushing it. I'm taking my Home farm to 4 4 card rigs because i also run two Script miners that total @ 300 MH . i can make if i can deal with it all on for a month closes to 2 k ... before power cost with prices of coins going up,even more over time. Also With coins going up like they are i may even look into a few upgrade kits some one is selling on the BTC forums ( not side hack, I don't think he is yet . ) for my old S3, C1, two S1, and two S5 heat sinks with the controller, no hash boards.. I have laying around for BTC mining . Thank you, good info
|
|
|
|
Mister305 (OP)
|
|
May 28, 2017, 07:48:21 PM |
|
a 15 amp 120 volt circuit can run 1x 6 card rig
so if you have a 200 amp home with only 120 volts setup
how many rigs you can run comes down to:
do you run an A/C?
do you run an electric clothes dryer or a gas one?
do you have an electric stove or a gas one?
do you hear your hot water with electric or gas ?
I have all gas so I can do more then many home with all electric. a/c is electric.
I also setup 240 volts for mining which allows for more.
I run as high as 24 amps at 240 in the winter
I run at 10 amps in the summer.
that is 10 1080 ti's and 2 1070 's
How are you connecting the miners to the 240 plug? Are you using a sort of power strip to connect to? If you could link one that would be great
|
|
|
|
VyprBTC
|
|
May 28, 2017, 07:52:17 PM |
|
worst case scenario is you can either upgrade the panel or run a sub panel - i have a horrible panel only 100amp 120v so will be installing a subpanel or maybe even trying to upgrade to 200amp panel depending on what the electrician says. we were already in the middle of getting solar panels before I decided to start mining so we'll see how much that helps
|
|
|
|
toptek
Legendary
Offline
Activity: 1274
Merit: 1000
|
|
May 28, 2017, 08:00:41 PM Last edit: May 28, 2017, 09:51:48 PM by toptek |
|
worst case scenario is you can either upgrade the panel or run a sub panel - i have a horrible panel only 100amp 120v so will be installing a subpanel or maybe even trying to upgrade to 200amp panel depending on what the electrician says. we were already in the middle of getting solar panels before I decided to start mining so we'll see how much that helps I want solar panels bad and looking into it but ATM can't get approved due to some credit issue that are just about cleared up ...once they are, I'm going solar ..and NO more CC's for me unless it's a bank card there nothing but trouble, this year i paid off a few and by next year the rest are paid off ,and I only pay with cash now .. Id also buy one of these with a Syder kit, it's also solar ready .. if you can afford to, it's right on the money, so far and good @ letting me see just how much my 220 lines are pulling, i bought one with a Syder kit so i can monitor the 220 lines without using a hard ware meter and it tells me by the second , min , hour, something the power company were i live doesn't do .. they only report by the day, but it's gonna cost close to 500 bucks or more for a full kit with add on's. http://www.theenergydetective.com/tedprohome.html home kit only http://www.theenergydetective.com/spyder spyder kit and there is a few of them ...
|
|
|
|
Elder III
|
|
May 28, 2017, 09:05:58 PM |
|
You need to take a look at your electric panel and determine what kind of service you have and how many circuits that are (typically) 15 or 20 Amps. You then need to determine what is connected to each individual circuit, how many watts each circuit has on it already etc.... Then you can determine how many watts are left for mining rigs. It's a bit daunting if you aren't familiar with electricians work, or even general contracting.
If you happen to have a 20 Amp circuit in your house that has nothing connected to it at all then you have ~1920 watts to use for mining. --- 20 Amps x 120 Volts = 2400 Watts x 80% "safe load" = 1920 usable Watts on that circuit. If you are fortunate enough to have a 240 Volt circuit (rarer in the USA) you have double the Watts to use. A 14 Amp circuit gives you 1440 Watts. You can manage to have two 6 GPU rigs on a 20 Amp circuit if you do some undervolting and/or power limiting, but it's not not too likely that you will fit more then one 6 GPU rig on a 15 Amp circuit.
Buy a KillaWatt (or other brand) electric meter (plugs into an outlet and then you plug the appliance etc. into it) for $20 and you will know exactly how many Watts anything in your house is using.
|
|
|
|
VyprBTC
|
|
May 28, 2017, 09:26:59 PM |
|
You need to take a look at your electric panel and determine what kind of service you have and how many circuits that are (typically) 15 or 20 Amps. You then need to determine what is connected to each individual circuit, how many watts each circuit has on it already etc.... Then you can determine how many watts are left for mining rigs. It's a bit daunting if you aren't familiar with electricians work, or even general contracting.
If you happen to have a 20 Amp circuit in your house that has nothing connected to it at all then you have ~1920 watts to use for mining. --- 20 Amps x 120 Volts = 2400 Watts x 80% "safe load" = 1920 usable Watts on that circuit. If you are fortunate enough to have a 240 Volt circuit (rarer in the USA) you have double the Watts to use. A 14 Amp circuit gives you 1440 Watts. You can manage to have two 6 GPU rigs on a 20 Amp circuit if you do some undervolting and/or power limiting, but it's not not too likely that you will fit more then one 6 GPU rig on a 15 Amp circuit.
Buy a KillaWatt (or other brand) electric meter (plugs into an outlet and then you plug the appliance etc. into it) for $20 and you will know exactly how many Watts anything in your house is using.
Elder is right on the money with this - make sure you don't buy the killa watt ez, you want the regular Kill A Watt and not the EZ version
|
|
|
|
toptek
Legendary
Offline
Activity: 1274
Merit: 1000
|
|
May 28, 2017, 09:31:33 PM Last edit: May 28, 2017, 09:46:06 PM by toptek |
|
The killa watt meters any of them in the US will not plug into 220 lines they are only made for 120 lines in the US and if you can, i would have at least two 220 lines with 30 or 40 amp breakers installed and buy a cheap used PDU off Ebay for 20 bucks ,to plug into the 220 and then plug your rigs into the PDU once you know what your house can handle and make sure it's covered by your insurance ..
.oyea don't use 30amp 120 breakers you can buy them . but not a good idea ....to use for mining to save on not having a 220 installed ..
|
|
|
|
|
Elder III
|
|
May 28, 2017, 11:11:39 PM |
|
^^^ excellent information as always from Phillip Do make sure to get an electrician, 240v can easily kill you if you don't know what you are doing. We have a 50 Amp line run out in our barn last week that is 6 gauge wire (thick as a small garden hose and a hell of allot heavier) but it will power a small mining farm all by itself (with 240v PDU) so the cost of materials was worth every penny.
|
|
|
|
toptek
Legendary
Offline
Activity: 1274
Merit: 1000
|
|
May 28, 2017, 11:48:41 PM |
|
Phil left out you need these type plugs if you are gonna use a 220/240 line depending on the PSU https://www.amazon.com/gp/product/B007O0EIRU/ref=oh_aui_detailpage_o00_s00?ie=UTF8&psc=1 Don't worry if you use a ATX Power supply's they Switch for 220 /240 lines when plugged in to a 220/240 line,but make sure anyway, someplace on the ATX Box it comes in or ON the ATX PSU it should say something like 100 to 240 watt or volts it can used be used on , i can't remember the exact wording, Id have to look, plus the power cable that comes with most ATX psus sold in the US are plugged for 120 lines, so you need the cable linked above or a version of it to plug into a PDU for 220/240 and for all server power supply's that only work on 220/240, if you go that route...
|
|
|
|
philipma1957
Legendary
Offline
Activity: 4116
Merit: 7851
'The right to privacy matters'
|
|
May 29, 2017, 12:17:24 AM |
|
Phil left out you need these type plugs if you are gonna use a 220/240 line depending on the PSU https://www.amazon.com/gp/product/B007O0EIRU/ref=oh_aui_detailpage_o00_s00?ie=UTF8&psc=1 Don't worry if you use a ATX Power supply's they Switch for 220 /240 lines when plugged in to a 220/240 line,but make sure anyway, someplace on the ATX Box it comes in or ON the ATX PSU it should say something like 100 to 240 watt or volts it can used be used on , i can't remember the exact wording, Id have to look, plus the power cable that comes with most ATX psus sold in the US are plugged for 120 lines, so you need the cable linked above or a version of it to plug into a PDU for 220/240 and for all server power supply's that only work on 220/240, if you go that route... Correct left that out. Some times eBay has used lots cheaper price. Since it is 220/240. A 16 gauge can work for 1000 watts but I prefer 14 gauge Search c13 to c14 on ebay
|
|
|
|
VyprBTC
|
|
May 29, 2017, 07:23:13 AM |
|
Haven't gotten around to getting an electrician out yet - but here's my current cheap ol breaker box - Any ideas? I don't really know why the Washer/Dishwasher/Disposal/Dryer are all connected like they are - Also not sure if the main 100amps can handle a 60 amp sub panel or possibly more? Don't even know yet if the wiring would support a 200amp upgrade without digging. Guess that's why an electrician needs to come out?
|
|
|
|
ocl
Newbie
Offline
Activity: 28
Merit: 0
|
|
May 29, 2017, 08:44:28 AM |
|
Isn't there any correlation between max load capacity and line wire thickness ?
|
|
|
|
VyprBTC
|
|
May 29, 2017, 06:45:40 PM |
|
Dang holiday, contacted so many people this weekend even friend that's a general contractor can't get back to me. hahaha. impatience is killing me
|
|
|
|
jMEGA
Newbie
Offline
Activity: 18
Merit: 0
|
|
May 29, 2017, 06:51:36 PM |
|
Isn't there any correlation between max load capacity and line wire thickness ?
Yes, there is. It depends on the amperage and the distance/length of wire run.
|
|
|
|
VyprBTC
|
|
May 29, 2017, 06:55:57 PM |
|
Isn't there any correlation between max load capacity and line wire thickness ?
10A = 16 gauge 15A = 14 20A = 12 30A = 10 40A = 8 55A = 6
|
|
|
|
Mister305 (OP)
|
|
May 29, 2017, 07:32:16 PM |
|
All great info, thanks
|
|
|
|
|