Hello,
I'm a total newbie in electricity and I have 3 months to set up a warehouse with enough power for 35 L3+ miners.
For the cooling I will be using ducting tubes and air extractors (outflow from the miners and inflow from outside).
For internet I will be using a Lan Switch.
I'm not sure what I need for the electricity exactly.
I'm checking warehouses and they specify this kind of information :
45 amp 3 phase breaker
100 amp 3 phase breaker
How many L3+ can I use with 45 amp 3 phase breaker and with 100 amp 3 phase breaker ?
Also, what does the 3 phase breaker means ? How can I check which plug is on which breaker ?
What is the limit per wall plug ?
Best regards,
Antminer L3+ is 800Watt miner, with 10% variation, some energy is also consumed inside PSU in heating/fans etc so make it 1000W for safe side.
for 35 L3+ you would need 35000W, or 35kW straight for miners,
for cooling equippments, any computer, or other small devices you may add up 2kW,
so it comes up to 37kW, (make it 40kW if you need an air conditioner too.)
now there are two options
1. if you have 220v power line then total current required would be 37000/220=168 Amp, in three phases it would be devided so it becomes 168/3=56 Amp
2. if you have 1100v power line then total current required would be 37000/110=336 Amp, in three phases it would be devided so it becomes 336/3=112 Amp
About phase breakers i can only suggest if you can provide more details, like power line voltage, 45 amp per phase or 45 amp in total (generally they are total ones)
BTW, i am mining with GTX660ti GPU,
just to stay in game
donations
LYhy3PNL3kC9ZQkUKnmBqMviNpPk8VdZco (LTC)
1DWJo4kw1ph4fhQCsH4utCSBFyikBVYP6t (BTC)