Author Topic: BTU Output of L3+ AntMiner  (Read 1027 times)
chipmonk1999 (OP)
Newbie
*
Offline Offline

Activity: 2
Merit: 0


View Profile
July 15, 2017, 10:04:26 AM
 #1

Does anyone know that the BTU output is on the L3+ Miners?

I purchased Qty. 10, L3+ Bitminers that will be powered via antminer power supplies running at 240VAC.

These units are going to be in a 10 by 10 enclosed room.

Want to size a AC Unit that will keep them at room temp.

However not finding any information on how much heat they produce.

THank you
jasemoney
Legendary
*
Offline Offline

Activity: 1610
Merit: 1008


Forget-about-it


View Profile
July 16, 2017, 01:55:16 AM
 #2

Hi, im not a miner but here are some helpful calculations consider that a miner basically turns electricity into hashes and creats tons of heat doing it.
https://shop.bitmain.com/antminer_l3_litecoin_asic_scrypt_miner.htm?flag=specifications
L3+ uses ~800 watts at the wall
http://www.rapidtables.com/convert/power/Watt_to_BTU.htm 800 watts = 2700 btu/hr per device. someone can step in and say whether this would be overkill for a miner. but your looking at a maximum of needing nearly 30k btu/hr in cooling for 10 L3+ miners.

Take care, keep cool Wink !

$MAID & $BTC other than that some short hodls and some long held garbage.
jstefanop
Legendary
*
Offline Offline

Activity: 2105
Merit: 1397


View Profile
July 16, 2017, 04:28:23 AM
 #3

I hope your not seriously thinking to cool down 10 units in an enclosed room by A/C alone. If your doing it by A/C at all in the first place your doing it wrong. You'll end up with as much A/C power to cool then as they put out.

Ill help you out:

1. Cut a hole in your wall
2. stick an attic fan to it
3. sip on your espresso

Project Apollo: A Pod Miner Designed for the Home https://bitcointalk.org/index.php?topic=4974036
FutureBit Moonlander 2 USB Scrypt Stick Miner: https://bitcointalk.org/index.php?topic=2125643.0
pdpanzer
Newbie
*
Offline Offline

Activity: 56
Merit: 0


View Profile
July 16, 2017, 04:38:03 AM
 #4

What to do in places with 84F or over 32C? Fan alone can't possibly work. Ideas?
Ericgw
Newbie
*
Offline Offline

Activity: 34
Merit: 0


View Profile
October 15, 2017, 05:53:03 PM
 #5

Reading this thread and searching on line as well, I also seem unable to locate the specifics of how much heat each unit produces

I have 4 L3's on the way right now and my intention is to look at a small farm in the approx 100qty range in the next 6 months, part of the research is to calculate heat output and cooling requirements

Does anyone know if heat output has been tested or of a resource where data of this type is posted?
dagarair
Sr. Member
****
Offline Offline

Activity: 847
Merit: 383



View Profile WWW
October 15, 2017, 05:54:25 PM
 #6

how many watts?  watts x 3.41 = BTU output

4MW Data Center - I BUILT Tongue  - Full story below:
https://bitcointalk.org/index.php?topic=4789787.msg43227027#msg43227027
HagssFIN
Legendary
*
Offline Offline

Activity: 2436
Merit: 1706


Electrical engineer. Mining since 2014.


View Profile WWW
October 15, 2017, 05:57:43 PM
 #7

It is roughly 800W per miner with stock settings.

https://www.youtube.com/watch?v=PPIlHbqms3Y
Measured with a Kill-A-Watt electricity usage monitor.

Ten miners - roughly 8kW.

This equals about 27300 BTU/hr.

VuValley
Member
**
Offline Offline

Activity: 121
Merit: 10


View Profile
October 15, 2017, 06:06:35 PM
 #8

Pushing air into the room is more effective & efficient than trying to exhaust it. Give it a try both ways and take temperature readings, youll be surprised. Good luck!
dagarair
Sr. Member
****
Offline Offline

Activity: 847
Merit: 383



View Profile WWW
October 15, 2017, 07:01:28 PM
 #9

800 x 10 = 8000 watts x 3.41 = 27,280 BTU / 12000 = 2.3 Tons of air if you want to cool it.    

4MW Data Center - I BUILT Tongue  - Full story below:
https://bitcointalk.org/index.php?topic=4789787.msg43227027#msg43227027
Ericgw
Newbie
*
Offline Offline

Activity: 34
Merit: 0


View Profile
October 16, 2017, 05:50:48 PM
 #10

Pushing air into the room is more effective & efficient than trying to exhaust it. Give it a try both ways and take temperature readings, youll be surprised. Good luck!

I am considering placing my 4 x L3's in my garage to assist with cooling and air movement.  I live in the Northern hemisphere and my garage in between the sun and my house so usually in the shade.

I am wondering about humidity, dust and -30* temperatures, as humidity, dust levels and temperature changes outside, how much of an effect will this have on the units?

Also If I use an air intake approach, I am concerned about intaking snow and/or rain, anyone have experience with the above?