July 31, 2017, 03:14:27 AM |
|
Hello,
I know in general we want to control the humidity levels for ASICS to a reasonable level, but I was curious what your experience has been if you're working with miners in un-airconditioned spaces.
In the climate I'm in (U.S. Desert Southwest), I can control the temperature pretty well with evaporative cooling because the weather is so dry. In the early summer, the humidity might only be 15% outside, so cooling with evap will lower temps by 20 degrees or so, and will raise humidity up to about 40-50% which should actually be healthier for the miners. In the late summer this gets worse, with a chance for humidity to reach 60 - 70% if I cool the miners down to a level that is suitable for running.
If there is no condensation risk due to the heat, and the humidity is still below the mfg's specs (90% for S9), do you see any risk in this or am I tempting fate?
The other option is powering down for the worst days of the year and accepting a $0.00 profit those days (Actually negative because of rent / depretiation etc.). That still seems cheaper than buying enough A/C to cover any sizable install of S9's.
Is anyone using AC to cool ambient from maybe 110 down to 85 or so and then exhausting the airflow outside? When I look at CFMs needed from the AC to keep each miner exhausting ~200cfm, the AC winds up having about 2x's the tonnage than would be expected based on the heat load of the actual miners.
thanks for any insights
|