Author Topic: 25 Asics power set up  (Read 578 times)
nimus (OP)
Newbie
*
Offline Offline

Activity: 7
Merit: 0


View Profile
August 08, 2017, 02:15:32 PM
 #1

HI all

i am receiving 25 asics in end of october and i have a big power set up problem
if someone of you can give me some help i will really apreciate it
here is the problem :
i have a 380 V installation ( 3 phases ) and i am living in France , my total power limit it's 36KVA and 60 amp per phase
how do i have to set up my installation in order to be ok
i have to set up 25 sockets 220 V each and each socket has to support 1200 W
how do i have to set up my electric board in term of breaker ( how many amp each breaker has to support ) and how do i equilibrate my phases
thanks again for any help given as i am really lost for the moment
VRobb
Hero Member
*****
Offline Offline

Activity: 1610
Merit: 538

I'm in BTC XTC


View Profile
August 08, 2017, 03:09:35 PM
 #2

Well I'd first suggest you get in touch with someone more versed in electrical hookups if you're unsure.  However, it appears that you have plenty of power for the number of units you want to run.  I'd setup duplex outlets on a 15A or 20A breaker each so you can run 2 miners on each duplex (2400W), setup 5 breakers/duplex outlets per phase pair, run 8 on two of them and 9 on the third for your 25 units running balanced as close as possible.  And, of course, wire everything appropriately for the amps/power involved.
See, get some help, I would!

I don't believe in superstition because it's bad luck: 13thF1oor6CAwyzyxXPNnRvu3nhhYeqZdc
These aren't the Droids you're looking for: S5 & S7 (Sold), R4B2, R4B4 (RIP), 2x S9 obsolete, 2xS15-28, S17-56, S17-70
Pushing a whopping 1/5 PH!  Oh The SPEED!!!
QuintLeo
Legendary
*
Offline Offline

Activity: 1498
Merit: 1030


View Profile
August 08, 2017, 06:35:55 PM
 #3


i have a 380 V installation ( 3 phases ) and i am living in France


 Sounds like you need to consult with an electrician.


I'm no longer legendary just in my own mind!
Like something I said? Donations gratefully accepted. LYLnTKvLefz9izJFUvEGQEZzSkz34b3N6U (Litecoin)
1GYbjMTPdCuV7dci3iCUiaRrcNuaiQrVYY (Bitcoin)
nimus (OP)
Newbie
*
Offline Offline

Activity: 7
Merit: 0


View Profile
August 09, 2017, 08:15:16 PM
 #4

Thanks for your help
So far after investigation it seems that I can plug 5 asics
On 1 breaker 20 amps as I am with 380 v tri phase and each breaker can support more than 7000 W
So I will need 5 breaker 20 amps and in each breaker
Will be 5 asics connected
It will take 100 amps ( to divide on 3 phases )from my 180 total
Amps
Hope I am not wrong
Again if someone don t agree with my calculation
I am focus to any suggestions
NotFuzzyWarm
Legendary
*
Offline Offline

Activity: 3668
Merit: 2604


Evil beware: We have waffles!


View Profile
August 10, 2017, 12:55:59 AM
 #5

Main problem you have is that you are running 380V which is Europe's version of 480V here in the US.

Either case that needs to be stepped down preferably with a single large transformer to the 208-240VAC single-phase power the miners PSU's use. I am not aware of ANY that will accept 380-400v input. If possible size it to supply the full main panel capacity. The output from that is then fed to a 220V breaker panel for circuit distribution.

The only other route is to use smaller individual transformers fed from each 380V circuit you have.

- For bitcoin to succeed the community must police itself -    My info useful? Donations welcome!  3NtFuzyWREGoDHWeMczeJzxFZpiLAFJXYr
 -Sole remaining active Primary developer of cgminer, Kano's repo is here
-Support Sidehacks miner development. Donations to:   1BURGERAXHH6Yi6LRybRJK7ybEm5m5HwTr
NiHaoMike
Full Member
***
Offline Offline

Activity: 236
Merit: 250



View Profile WWW
August 10, 2017, 02:54:06 AM
 #6

If it's 380V phase to phase, it would be 220V phase to neutral.

I use cryptocurrency and solar power to help my best friend Naomi Wu... And I'm proud of it!
NotFuzzyWarm
Legendary
*
Offline Offline

Activity: 3668
Merit: 2604


Evil beware: We have waffles!


View Profile
August 10, 2017, 12:44:38 PM
 #7

If it's 380V phase to phase, it would be 220V phase to neutral.
^^ If the incoming is wye and has a neutral that is. Many countries having incoming as delta and so no neutral. No idea what France uses for their grid.

- For bitcoin to succeed the community must police itself -    My info useful? Donations welcome!  3NtFuzyWREGoDHWeMczeJzxFZpiLAFJXYr
 -Sole remaining active Primary developer of cgminer, Kano's repo is here
-Support Sidehacks miner development. Donations to:   1BURGERAXHH6Yi6LRybRJK7ybEm5m5HwTr
Pages: [1]
  Print  
 
Jump to:  

Powered by MySQL Powered by PHP Powered by SMF 1.1.19 | SMF © 2006-2009, Simple Machines Valid XHTML 1.0! Valid CSS!