Bitcoin Forum
May 06, 2024, 03:31:03 AM *
News: Latest Bitcoin Core release: 27.0 [Torrent]
 
   Home   Help Search Login Register More  
Pages: [1]
  Print  
Author Topic: How many s9 can run on a 3 phase 400amp panel?  (Read 927 times)
kingofkens (OP)
Newbie
*
Offline Offline

Activity: 5
Merit: 0


View Profile
October 10, 2017, 04:06:22 PM
Last edit: October 17, 2018, 09:44:38 PM by frodocooper
 #1

I try to set a small size mining farm. I try to understand 3 phase electricity, but it is difficult to understand. I asked many electricians but everyone has different answers and I am kind of confuse.

I want to know the capacity of my 400 amp panel. It is 3 phase. I believe it can make 240v with two lines. It has a wildleg(208v? delta system?).

How many s9 can run on this panel?

My simple head calculate like this...I feel like something missing...
---------------------
Each Machine operate
1440w/240v = 6 amp
400Amp panel
so 400amp / 6amp =66 S9s
 
Constant electricity so 80%
66.66*0.8 =53 S9s
----------------------
Is this a right way to calculate?
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
1714966263
Hero Member
*
Offline Offline

Posts: 1714966263

View Profile Personal Message (Offline)

Ignore
1714966263
Reply with quote  #2

1714966263
Report to moderator
1714966263
Hero Member
*
Offline Offline

Posts: 1714966263

View Profile Personal Message (Offline)

Ignore
1714966263
Reply with quote  #2

1714966263
Report to moderator
1714966263
Hero Member
*
Offline Offline

Posts: 1714966263

View Profile Personal Message (Offline)

Ignore
1714966263
Reply with quote  #2

1714966263
Report to moderator
sidehack
Legendary
*
Offline Offline

Activity: 3318
Merit: 1848

Curmudgeonly hardware guy


View Profile
October 10, 2017, 04:16:00 PM
 #2

I'm running my whole shop off a 3-phase wye (so, 120V line-neutral and 208V line-line) through a 400A panel. Got 350A of sub-breaker handling the hosting room, drawing roughly 100KW for 80-odd machines (most S9 but not all). I'm comfortable at 100KW, will run 110KW peak which puts my breakers at 90% capacity so I'd rather not do it for long. I've got meters on every leg so I can monitor the power use on the fly.

Every electrician is telling you something different because there are a lot of different ways 3-phase can be run. Different line voltages, delta or wye, each one does something different.

The first thing you're going to want to know is exactly what kind of 3-phase configuration you have coming in the building. I have 120V (208V L-L) 3-phase wye, which is probably the easiest kind to figure out.

Cool, quiet and up to 1TH pod miner, on sale now!
Currently in development - 200+GH USB stick; 6TH volt-adjustable S1/3/5 upgrade kit
Server PSU interface boards and cables. USB and small-scale miners. Hardware hosting, advice and odd-jobs. Supporting the home miner community since 2013 - http://www.gekkoscience.com
NotFuzzyWarm
Legendary
*
Online Online

Activity: 3626
Merit: 2533


Evil beware: We have waffles!


View Profile
October 10, 2017, 05:12:06 PM
 #3

You mentioned that it is a wild-leg setup and for the most part utilities do NOT want a full load running from that leg as it is intended more for moderate 3-phase motor loads in the building like HVAC with the lions share of load coming from the 2 legs working as part of the 110v taps.Those 2 legs together is where most of the 208V load should be drawn. Look up wikipedia's Wild-leg explanation. Now if you are in a light industrial zone area the normal wild-leg load restriction may not be an issue, it mostly crops up in commercial/office areas where most of a buildings load are 110v

edit: also, it is bad form to make duplicate posts in different areas asking the same question. I requested the mods remove the dupe in Mining > Support.

- For bitcoin to succeed the community must police itself -    My info useful? Donations welcome! 1FuzzyWc2J8TMqeUQZ8yjE43Rwr7K3cxs9
 -Sole remaining active developer of cgminer, Kano's repo is here
-Support Sidehacks miner development. Donations to:   1BURGERAXHH6Yi6LRybRJK7ybEm5m5HwTr
kingofkens (OP)
Newbie
*
Offline Offline

Activity: 5
Merit: 0


View Profile
October 10, 2017, 05:24:44 PM
 #4

I remember that few electricians told me that I can't use every third space in the panel because the wildleg, Delta.

Does it mean the delta system like my setup have less capacity than the wye system like the gentleman above has?
MoonMining
Newbie
*
Offline Offline

Activity: 1
Merit: 0


View Profile
October 11, 2017, 01:41:57 AM
 #5

98 S9s On a 400 amp 240v 3 phase panel

400*240v*1.73=166,080 Watts

Each S9 1,350 watts
166,080*80=132,864 continuous watts

132,864/1,350=

98 S9s
NotFuzzyWarm
Legendary
*
Online Online

Activity: 3626
Merit: 2533


Evil beware: We have waffles!


View Profile
October 11, 2017, 02:00:00 AM
 #6

I remember that few electricians told me that I can't use every third space in the panel because the wildleg, Delta.

Does it mean the delta system like my setup have less capacity than the wye system like the gentleman above has?
The 'not use every 3rd space' refers to trying to use a single-pole breaker in that slot which is fed by the wild leg thinking that it will provide 110V referenced to Neutral -- it doesn't. Is more like around 180V as I recall...

That said, using a 2-pole breaker for 208V single-phase is fine same as using a 3-pole for 3-phase power: You are now drawing power phase-to-phase in either case so it does not matter what slots are used.

As for can you draw full 400A from the wild leg, probably but if possible try to find out how your utility feels about it. Some will tack on a surcharge because their local grid was not setup a lot of people doing that. True full delta or Wye incoming service does not have any phase-to-phase load limitations but in turn in the case of delta require a transformer to provide building 110V service. Wye service is 4-wire with 3-hot legs and a center referenced neutral but generally have limitations to how much unbalanced single-phase (hot leg-to neutral) current is allowed.

- For bitcoin to succeed the community must police itself -    My info useful? Donations welcome! 1FuzzyWc2J8TMqeUQZ8yjE43Rwr7K3cxs9
 -Sole remaining active developer of cgminer, Kano's repo is here
-Support Sidehacks miner development. Donations to:   1BURGERAXHH6Yi6LRybRJK7ybEm5m5HwTr
T-Gee05
Member
**
Offline Offline

Activity: 67
Merit: 10


View Profile
October 11, 2017, 06:27:43 AM
Last edit: October 17, 2018, 09:45:22 PM by frodocooper
 #7

The 'not use every 3rd space' refers to trying to use a single-pole breaker in that slot which is fed by the wild leg thinking that it will provide 110V referenced to Neutral -- it doesn't. Is more like around 180V as I recall...

That said, using a 2-pole breaker for 208V single-phase is fine same as using a 3-pole for 3-phase power: You are now drawing power phase-to-phase in either case so it does not matter what slots are used.

As for can you draw full 400A from the wild leg, probably but if possible try to find out how your utility feels about it. Some will tack on a surcharge because their local grid was not setup a lot of people doing that. True full delta or Wye incoming service does not have any phase-to-phase load limitations but in turn in the case of delta require a transformer to provide building 110V service. Wye service is 4-wire with 3-hot legs and a center referenced neutral but generally have limitations to how much unbalanced single-phase (hot leg-to neutral) current is allowed.

I believe it is safer to say to have another single phase distribution panel connected to that 400A 3-phase breaker for proper load balancing with smaller rated circuit breakers. With the computation above, 98 S9 miners divided in 3, so you will connect 32 S9s in line 1-2, 32 in line 2-3 and 32 in line 3-1.
ConnerM
Member
**
Offline Offline

Activity: 61
Merit: 23


View Profile
October 11, 2017, 08:38:32 AM
Last edit: October 17, 2018, 09:46:05 PM by frodocooper
 #8

We run our small farm off a 400amp 3-phase Wye configuration. We have 2 pole 30amp circuits so we are taking single phase 208v (leg to leg) off the 3 phase panel. You have to remember to balance the load across all three phases as much as possible on a Wye system. We currently run a bout 82 miners on it (mostly S9's, couple of 741's) and still have some room to spare in the panel. Here's what it looks like including the panel:



We're pulling about 116KVa (it's a little more than the total wattage due to the 'power factor') through the panel and had the PoCo set a 150KVa 208v Wye distribution transformer to support it (it was only 75KVa originally and had to be upgraded). So even if you have a 400amp in the panel, make sure your transformer is large enough to support your load. Your total load should not draw more than 80% of your transformers total service rating, otherwise you'll reduce it's service life significantly. Datacenter operations like mining draw power much differently than typical commercial power usage. It's always on. You'll want to check with the PoCo that their facility to your building will support that load, and they may require you to submit a load letter describing how much you will be drawing and what it is for.

"Buying up the shovels as fast as possible..."
My Little Farm -or- How I learned to Stop Worrying and Spend All My Time --> https://imgur.com/a/T1z8q
BTCBusinessConsult
Sr. Member
****
Offline Offline

Activity: 546
Merit: 250


Active Trading on EPIC5k and Spectre.Ai


View Profile WWW
October 12, 2017, 05:22:39 PM
 #9

First off, I am NOT calling doubt into anything that experienced miners have said.

With that, I would HIGHLY recommend you get an extremely qualified electrician to have a sit down and explain everything to you.

A 240V 25 Amp circuit flashing will instantly fry you. A 400 amp circuit overloading and arching will literally make you explode.

You are right about the 80% continuous load, but man oh man please be careful.

EPIC5k Trading on https://spectre.ai/?ref=PassiveIncome. Paying WEEKLY rewards in ETH since 2017. 100% FRAUD FREE Binary Trading Platform. $SXDT. Ask me about the ONLY smart options trading platform with 400% payouts, and their unique EPIC5000 trading system.
Pages: [1]
  Print  
 
Jump to:  

Powered by MySQL Powered by PHP Powered by SMF 1.1.19 | SMF © 2006-2009, Simple Machines Valid XHTML 1.0! Valid CSS!