looking online and I see multiple brands but I haven't seen much talk online in the forums about powering there miners.
I will have 3 30AMP 240v plugs for the miners to run off of.
You want the miners to run off of 240V, so you need to make sure that you have 3 x 30A 240V breakers installed in the panel. Make sure you get them wired to a LP-30R as seen below.
Then, you need to have the PDUs to be 240V as well, not 120V as you mentioned to match the NEMA LP-30R receptacle. I have these because I like to see the amperage (as rigs can vary, and you want to distribute the load evenly), and are reasonably priced. You dont need the metered feature, but it is nice.
https://www.newegg.com/Product/Product.aspx?Item=9SIA1UH3715727Some other options are:
Basic PDUsMeteredAny other MFRs are fine too. That is just an idea! Good luck, and where are the progress pictures?
thanks Beerman,
I was going to shoot you a message about that. but got caught up at work with something just now. I will be having 3 240v outlets installed just as you said and they will be on dedicated 30 amp breakers each. Its hard for me to talk electrical since that's not my thing. I am honestly copying a ton off of your build just not as large.
shed is already built, and once its finished being wired, I will be adding insulation and so on. can you shoot me a PM with a email I could send pics to you cause I cant post them on the forum as easily if you wanna see the progress...