Bitcoin Forum
May 23, 2024, 06:55:19 PM *
News: Latest Bitcoin Core release: 27.0 [Torrent]
 
   Home   Help Search Login Register More  
Pages: [1] 2 »  All
  Print  
Author Topic: Mining room Cooling  (Read 926 times)
Icarusfixius (OP)
Member
**
Offline Offline

Activity: 97
Merit: 10


View Profile
January 21, 2018, 08:59:47 PM
Last edit: January 21, 2018, 09:40:18 PM by Icarusfixius
 #1

I am trying to work on a new strategy to cool my rigs. As usual I start down a path and it just isnt working as effectively as I would like it to. Things were working out alright when I was able to pull in -10C intake air from outside. Today it is 17C outside and it just isnt cutting it. It seems like there are two main approaches to take. You can contain the airflow to carefully direct it through all the cards or circulate so much air in the room that it doesnt matter. I figured I would post a few pics and see what suggestions others had.


Front of the rack, I was thinking of taking the rigs apart so I can space the cards out a bit more. Seems like if I could give them a bit more air space heat may be less of an issue


View of the rear of the rack and exhaust fan. I was planning on maybe upgrading this to a 24" fan that moves x4 air. As well as maybe putting an intake below that and ducting it to the other side of the room I have also considered putting some 30" warehouse fans behind the rack to move air through things better.


This is my current exhaust/intake. It seems that I have better luck when this fan is being used as an intake


philipma1957
Legendary
*
Online Online

Activity: 4130
Merit: 7912


'The right to privacy matters'


View Profile WWW
January 21, 2018, 10:54:43 PM
 #2

Great name for heat issues.

How many cards do you have and how many watts?


How much cfm for the exhaust fan?


I see at least 50. Cards.

So if they are 1080ti. You are 10000 watts

That needs at least 3000 cfm.

Lower the intake and make an awning over it.

I will find a photo.


▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
jimmykl
Full Member
***
Offline Offline

Activity: 349
Merit: 102


View Profile
January 21, 2018, 11:03:52 PM
Merited by MATHReX (1)
 #3

All the hot air is probably stuck in top of the room. While the fan is pulling fresh air in from outside it will stay near the floor and not forcing out the hot air trapped above. So you're heating the room slowly from the top down. The rigs mostly being higher up in the the shelving will increase this effect.



You could probably improve things a bit by moving the rigs as low on the shelves as possible. But that will make access harder and they'll get more dust near the floor too.

First I'd say try extending the ducting and relocating the fan to extract the stale hot air from the top of the room as quickly as possible:



If that works you could even make a rough 'hood' to increase the exhaust area and catch as much of the air rising directly above the shelving as possible. You could also try changing the location of the fan along the ducting to see where it pulls the best.



If you can add another exterior vent for the exhaust then you could keep the existing intake and might get it working like this:

xxcsu
Hero Member
*****
Offline Offline

Activity: 1498
Merit: 597


View Profile WWW
January 21, 2018, 11:11:03 PM
 #4

maybe a stupid idea Smiley but im going to give a try for this soon Smiley
"zero-electricity air cooler made from plastic bottles"
if i can lower the "incoming air" temp just with 5C during peak summer heat , that would be a great help Smiley

Learn about Merit & new rank requirements , Learn how to use MERIT , make this community better
If you like the answer you got for your question from any member ,
If you find any post useful , informative use the +Merit button.
philipma1957
Legendary
*
Online Online

Activity: 4130
Merit: 7912


'The right to privacy matters'


View Profile WWW
January 21, 2018, 11:13:13 PM
 #5

he has intake and exhaust on same wall






intake  must be lower

exhaust must not  suck  intake  up and out


@ op is this close to what is happening?


▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
TheYankeesWin!
Sr. Member
****
Offline Offline

Activity: 462
Merit: 300


View Profile
January 21, 2018, 11:17:28 PM
 #6

So  op buys  a second rack  rolls it against the intake

then tarps it
                                                     >   exhaust







equipment  rack   < air tunnel rack   < intake window
MagicSmoker
Full Member
***
Offline Offline

Activity: 420
Merit: 182



View Profile
January 21, 2018, 11:20:03 PM
 #7

Good advice so far, I would just add that there are two components to cooling things like this (I'm an EE that specializes in power electronics for my day job so I have some relevant experience): first is to remove heat from the cards themselves, which requires fans blowing directly on them - either at the rear or the top - and second is to remove heat from the room, which requires an intake vent and exhaust fan separated as far apart from each other as possible. Ideally, the room ventilation should cause air to flow diagonally from floor to ceiling, crossing over the miners along the way.

ciborgue
Newbie
*
Offline Offline

Activity: 8
Merit: 0


View Profile
January 21, 2018, 11:21:10 PM
 #8

I am using my old marijuana grow tent with lighting removed.
2 x 4 ft tent holds two 8 GPU rigs no problem with an old exhaust.
TheHas
Full Member
***
Offline Offline

Activity: 616
Merit: 167


View Profile
January 21, 2018, 11:21:22 PM
 #9

I remember watching a youtube clip of someone with a mini mining factory, and he said one of his greatest lessons learned was the importance of 'keeping heating off' instead of 'putting cool air on'. I guess if the cool air you're putting on is -17C from outside that might not apply quite as much.
philipma1957
Legendary
*
Online Online

Activity: 4130
Merit: 7912


'The right to privacy matters'


View Profile WWW
January 21, 2018, 11:27:26 PM
 #10

 I think his air flow is this :




If he  takes   theyankees   idea and does this

add awning for sun and rain shield
make inside cold air tunnel
add a floor fan  he should be good.





▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
Za1n
Legendary
*
Offline Offline

Activity: 1078
Merit: 1011



View Profile
January 21, 2018, 11:34:17 PM
 #11

I had this issue before too and the "solution" is to remove the hot air that naturally rises in your room. While you do need some intakes, trying to cool this intake air is not as important as just simply removing the heat.

The solution I found that worked for me, both in wintertime and during 100 degree plus summer days is to move the exhaust fans as high as you can. Going through the roof would be ideal, but at a minimum the height they need to be at is above the height of your highest rig.

It may seem strange, but even 100 degree F (38C) intake air will cool your GPUs as long as you have adequate exhaust ventilation at or above the maximum height of your rigs. It is best for the air intakes to be positioned lower toward the ground, but even if they are higher the main factor was keeping the exhaust fans high.

You will also need to calculate the CFM of air movement that you will need. I only run one out of three exhaust fans I have during the winter, but each of my fans is 20" and can move up to 4000 CFM on high. I went with the shuttered wall mount fans and had to frame in the openings, but ever since I put them in all my heat issue went away as my rigs will run around 60-70 degrees C even on 100 degree F (38C) days. In the winter they run a mild 30C.

Here are similar fans to what I bought, not the exact same as I bought mine from a local building supply company but very similar. http://www.airdistributor.net/p-414-ves-environmental-solutions-brand-3-speed-shutter-mount-direct-drive-agriculturalindustrial-wall-exhaust-fan-cfm-range-880-4874-sizes-12-thru-24.aspx
Icarusfixius (OP)
Member
**
Offline Offline

Activity: 97
Merit: 10


View Profile
January 23, 2018, 03:21:17 AM
 #12

he has intake and exhaust on same wall






intake  must be lower

exhaust must not  suck  intake  up and out


@ op is this close to what is happening?





I was afraid this is what may happen. Right now all I have is that one 12" intake fan. There are 80 cards in that room as well as a server rack behind there. Total power consumption in the space is close to 20-25Kw. The fan was supposed to be an exhaust but since it is so cold outside I had better luck with it setup as an intake
BennyT
Full Member
***
Offline Offline

Activity: 259
Merit: 108


View Profile
January 23, 2018, 04:11:49 AM
 #13

Lots of clever engineering ideas. Wouldn’t a 24” fan blowing on each rig not only solve the air issues but also be easier?
MagicSmoker
Full Member
***
Offline Offline

Activity: 420
Merit: 182



View Profile
January 23, 2018, 11:43:35 AM
 #14

Lots of clever engineering ideas. Wouldn’t a 24” fan blowing on each rig not only solve the air issues but also be easier?

No, and the reasons why have been covered in many of the above posts. You need to get the heat out of the room, not just out of the cards.

ajqjjj
Hero Member
*****
Offline Offline

Activity: 1498
Merit: 507


Not your Keys, not your Bitcoin


View Profile
January 23, 2018, 12:57:32 PM
 #15

he has intake and exhaust on same wall

intake  must be lower

exhaust must not  suck  intake  up and out


@ op is this close to what is happening?



I was afraid this is what may happen. Right now all I have is that one 12" intake fan. There are 80 cards in that room as well as a server rack behind there. Total power consumption in the space is close to 20-25Kw. The fan was supposed to be an exhaust but since it is so cold outside I had better luck with it setup as an intake


You mean is that you are using the exhaust fan to exit the heat out from the room? I am right. You are also have the set up same thing like me. Keeping the rig towards the window will be give better way exhaust out the heat.

If you are affordable to set up the air conditioner to the room you completely have the rig. You can have that on 27 degree temperature means that is enough the keep the 3 rigs safe with in the room.

-support Bitcoin Community Bitcointalk.org-
Always verify wallet to store your Bitcoin
Donations are open, send PM
crazydane
Full Member
***
Offline Offline

Activity: 558
Merit: 194



View Profile
January 23, 2018, 01:01:36 PM
Last edit: January 23, 2018, 02:25:08 PM by crazydane
 #16

Great topic about air flow and cooling so I figured I'd post about my plans here.

As I prepare for summer, I need to figure out what to do with all my rigs.  I'm at around 16kw right now, but anticipate being well above that by the time summer (and heat) rolls around.

My plan is to get a 40' shipping container (about $2,000 delivered) and ask if I can get it in white.  If not, I'll have to paint it myself.

I plan to install 3 10,000 CFM 36" exhaust fans, evenly space along the top, along one of the long walls.

These guys:

https://www.northerntool.com/shop/tools/product_200422375_200422375

Full specs here:

https://www.jdmfg.com/wall-master-exhaust-fan

They are very efficient and move about 20 CFM per watt.

On the opposite long wall, I'll cut out 6 24x24 inlets, evenly spaced along the bottom.  My mining racks will then go right down the center with a 36" isle on either side.

A 40' container is about 3,000 CF, so 30,000 CFM should be able to replace the air volume 10 times a minute.  That would be enough draft I would think, that I would not have to worry about any additional cooling, even when it is 100 degrees outside and the sun is baking down on top of the container.

Good idea or bad idea?
dagarair
Sr. Member
****
Offline Offline

Activity: 847
Merit: 383



View Profile WWW
January 23, 2018, 01:28:48 PM
 #17

I am using my old marijuana grow tent with lighting removed.
2 x 4 ft tent holds two 8 GPU rigs no problem with an old exhaust.

Win

4MW Data Center - I BUILT Tongue  - Full story below:
https://bitcointalk.org/index.php?topic=4789787.msg43227027#msg43227027
bitcad4u
Sr. Member
****
Offline Offline

Activity: 602
Merit: 255


View Profile
January 23, 2018, 04:10:27 PM
 #18

he has intake and exhaust on same wall

intake  must be lower

exhaust must not  suck  intake  up and out


@ op is this close to what is happening?



I was afraid this is what may happen. Right now all I have is that one 12" intake fan. There are 80 cards in that room as well as a server rack behind there. Total power consumption in the space is close to 20-25Kw. The fan was supposed to be an exhaust but since it is so cold outside I had better luck with it setup as an intake


You mean is that you are using the exhaust fan to exit the heat out from the room? I am right. You are also have the set up same thing like me. Keeping the rig towards the window will be give better way exhaust out the heat.

If you are affordable to set up the air conditioner to the room you completely have the rig. You can have that on 27 degree temperature means that is enough the keep the 3 rigs safe with in the room.

Keeping your rig near the windows will reduce the heat.Keep the rig with the cooler is the best option,instead of Air-conditioned room.You can try of coolant set up for the rig.I think this is not make huge difference.You expenses for cooler is cheaper than Air-conditioner.
dhouse
Jr. Member
*
Offline Offline

Activity: 266
Merit: 2


View Profile
January 23, 2018, 06:23:45 PM
 #19

can anyone recommend a simple cooling setup for a basement, i have only a 3-gpur rig now but would like to add a bunch more. Would like to just to have them on those plastic shelving units. They are in an unfinished basement area right now. There's a small window with a window well that i could use, plus another one at the other end of the room.

I'm thinking roughly of some sort of box/container/tent to store the rigs and thus confine the heat, with some kind of exhaust system that could pump air in and out of the window. Any ideas of where to start on this? the more straightforward the better.
P00P135
Full Member
***
Online Online

Activity: 1123
Merit: 136


View Profile
January 23, 2018, 06:30:46 PM
 #20

can anyone recommend a simple cooling setup for a basement, i have only a 3-gpur rig now but would like to add a bunch more. Would like to just to have them on those plastic shelving units. They are in an unfinished basement area right now. There's a small window with a window well that i could use, plus another one at the other end of the room.

I'm thinking roughly of some sort of box/container/tent to store the rigs and thus confine the heat, with some kind of exhaust system that could pump air in and out of the window. Any ideas of where to start on this? the more straightforward the better.

Grow tent with 6 or 8" intake/exhaust fans.
Pages: [1] 2 »  All
  Print  
 
Jump to:  

Powered by MySQL Powered by PHP Powered by SMF 1.1.19 | SMF © 2006-2009, Simple Machines Valid XHTML 1.0! Valid CSS!