Like this title says..
I currently have a 12 1080 ti rig running from an 12 gauge extension cord (2 1200w bitmain psu to power 12 gpu's and a 1050w psu to power mb and risers. The extension wire do get a little warm. I also have another 6 1080 rig which i put it upstair (afraid ill trip my 20 amp fuse). My real question is....how do you manage to run multiple rigs without re-doing all your house wires?
|
|
|
|
whoismoses
Member
Offline
Activity: 247
Merit: 59
|
|
March 04, 2018, 02:34:41 AM |
|
The limits are pretty simple. You can’t run more than 20A on a 20A circuit. The only option other than running a lot of dedicated 20A circuits or 30A circuits is to spread your miners around your house.
|
|
|
|
yrk1957
Member
Offline
Activity: 531
Merit: 29
|
|
March 04, 2018, 03:22:20 AM |
|
The limits are pretty simple. You can’t run more than 20A on a 20A circuit. The only option other than running a lot of dedicated 20A circuits or 30A circuits is to spread your miners around your house.
...and might as well get 240v circuits if you are re-wiring.
|
|
|
|
CointoHash411
Newbie
Offline
Activity: 84
Merit: 0
|
|
March 04, 2018, 03:22:53 AM |
|
Like this title says..
I currently have a 12 1080 ti rig running from an 12 gauge extension cord (2 1200w bitmain psu to power 12 gpu's and a 1050w psu to power mb and risers. The extension wire do get a little warm. I also have another 6 1080 rig which i put it upstair (afraid ill trip my 20 amp fuse). My real question is....how do you manage to run multiple rigs without re-doing all your house wires?
As others have said if you are wanting to runs as efficient & safely as possible it is really important to use dedicated circuits. I currently have 3 new 20A breakers in the main circuit panel powering all two of my ASIC miners and one of my GPU miners. Also, you have to keep in mind what the main breaker can draw for power as well or you could risk overheating it and tripping the main, a this can be a very bad issue i.e. burning down your house - https://www.youtube.com/watch?v=xNnAvTTaJjM status.
|
|
|
|
cashen
|
|
March 04, 2018, 05:07:05 AM |
|
Also if it is continuous you really should only do 80% of the rating. This would be 1920 watts for 120v on a 20 amp circuit. I would only run one 8 x 1080TI rig on this setup. I use 225-250w per 1080TI. You really should run 240v with this kind of draw. Below is my 125amp panel dedicated to mining. Yes, I did it all myself.
|
|
|
|
duhjeff (OP)
Newbie
Offline
Activity: 106
Merit: 0
|
|
March 04, 2018, 05:15:13 AM |
|
Also if it is continuous you really should only do 80% of the rating. This would be 1920 watts for 120v on a 20 amp circuit. I would only run one 8 x 1080TI rig on this setup. I use 225-250w per 1080TI. You really should run 240v with this kind of draw. Below is my 125amp panel dedicated to mining. Yes, I did it all myself. I undervolt them and runs roughly 180ish watt each.. so that's why I ran 3 psu instead of 2... Problem of rewiring is that my electric panel is @ basement and I have to run some seriously wires to first floor laundry room (which I'm using it for mining)..it's a weird NYC townhouse set up I know..... On top of this....I never ran electric wires before. I mean I'm pretty handy (I can build a honda engine with my eyes closed) but I don't want to be on the news And hiring an electrician is going to cost heck lot more money. sigh....maybe I should youtube and do it myself Jeff-
|
|
|
|
whoismoses
Member
Offline
Activity: 247
Merit: 59
|
|
March 04, 2018, 11:29:12 PM |
|
I undervolt them and runs roughly 180ish watt each.. so that's why I ran 3 psu instead of 2... Problem of rewiring is that my electric panel is @ basement and I have to run some seriously wires to first floor laundry room (which I'm using it for mining)..it's a weird NYC townhouse set up I know..... On top of this....I never ran electric wires before. I mean I'm pretty handy (I can build a honda engine with my eyes closed) but I don't want to be on the news And hiring an electrician is going to cost heck lot more money. sigh....maybe I should youtube and do it myself Jeff- If you run 2x 240v 30A circuits to your laundry room it is only two lines. Then get two PDUs.
|
|
|
|
CointoHash411
Newbie
Offline
Activity: 84
Merit: 0
|
|
March 06, 2018, 01:43:00 AM |
|
Also if it is continuous you really should only do 80% of the rating. This would be 1920 watts for 120v on a 20 amp circuit. I would only run one 8 x 1080TI rig on this setup. I use 225-250w per 1080TI. You really should run 240v with this kind of draw. Below is my 125amp panel dedicated to mining. Yes, I did it all myself.
How much did getting the this panel installed set you back, I think in the very near future I am going to have to get a 400 amp service 200 on the house, and 200 on the mining shed quite possibly.
|
|
|
|
EricJH801
Jr. Member
Offline
Activity: 210
Merit: 1
|
|
March 06, 2018, 02:48:47 AM |
|
If all you have to do is put in some breakers and run the wire, it's probably something you could easily learn about on youtube or just google searching. As long as you have the open slots in the breaker panel. Basically it's turning off the panel, popping in 2 30AMP 240V breakers and running the correct size wire to an L6-30R receptacle. Then buy a PDU and that will give you some room for 3-4 miners usually. (Mine draw 5-5.5 amps so I can get 4 on a line and not violate the 80% rule). You could always call an electrician and explain what you want to do and see if they can give you an estimate at least on the phone. Also if it is continuous you really should only do 80% of the rating. This would be 1920 watts for 120v on a 20 amp circuit. I would only run one 8 x 1080TI rig on this setup. I use 225-250w per 1080TI. You really should run 240v with this kind of draw. Below is my 125amp panel dedicated to mining. Yes, I did it all myself. I undervolt them and runs roughly 180ish watt each.. so that's why I ran 3 psu instead of 2... Problem of rewiring is that my electric panel is @ basement and I have to run some seriously wires to first floor laundry room (which I'm using it for mining)..it's a weird NYC townhouse set up I know..... On top of this....I never ran electric wires before. I mean I'm pretty handy (I can build a honda engine with my eyes closed) but I don't want to be on the news And hiring an electrician is going to cost heck lot more money. sigh....maybe I should youtube and do it myself Jeff-
|
|
|
|
CointoHash411
Newbie
Offline
Activity: 84
Merit: 0
|
|
March 16, 2018, 03:30:25 AM |
|
I am currently looking to also get 240 ran, I would run it myself but I am afraid that my main isn't large enough for the power draw. Does anyone have any idea what the average cost is to get the main upgraded for a residence?
|
|
|
|
EricJH801
Jr. Member
Offline
Activity: 210
Merit: 1
|
|
March 16, 2018, 04:17:44 AM |
|
It really depends on what you are at now and what you want to go to. I was upgrading from 100amp to 200amp and it was 3600. I ended up getting lucky and the power company ran lines to my house that support 400amp so I just need to change the main box if I want to do that. (Currently it can support 250AMP). I then have 100 AMP ran to my house and a 200AMP ran to my mining rig setup. My total cost was $4100. This included them digging a 30 foot trench that was 3 feet deep to run the power from the transformer to my residence. A side note, when I was calling for quotes, most places said it would be $3800 if my power was ABOVE ground and it goes up a lot if they had to dig. I just happen to find a contractor who would do it cheaper. I suggest you upgrade to 400AMP if you can do it because it saves you running more lines in the future. Good luck! I am currently looking to also get 240 ran, I would run it myself but I am afraid that my main isn't large enough for the power draw. Does anyone have any idea what the average cost is to get the main upgraded for a residence?
|
|
|
|
Max Likelihood
Jr. Member
Offline
Activity: 140
Merit: 2
|
|
March 16, 2018, 01:26:40 PM |
|
Would echo others recommending 240s. I had rigs on about 4 120 volts spread about some, but am very careful and made sure that everything on the line stayed under 80%. With a bunch of 1080tis, other than splitting them across multiple rigs on different circuits, not sure what the best options are. You can get pdus for 240s.
I'll do hardwired light fixtures and replace receptacles and such but don't run lines of a panel, and definitely would not with 240s. I'm personal risk-averse and paid a bit more to have an electrician do it, though don't know what the NYC rates are.
Also, if it's in your basement, could add teeny bit of property value as electric dryers run off 240s, so if you have a gas dryer and no 240, it's not going to look out of place to add one.
|
|
|
|
QuintLeo
Legendary
Offline
Activity: 1498
Merit: 1030
|
|
March 16, 2018, 10:30:17 PM |
|
As I can't redo most of the wiring in my current location, I deliberately build my rigs to draw appx. 700 watts (which is a hair under 6 amps at the voltage I see at my outlets) then put 2 of them on each 15 amp outlet (but see below).
The weird part is that the WIRING in this place is sized for 20 amps per circuit (except for the one 30 amp 234VAC outlet) and most of the breakers are 20 amp, but almost all of the circuits feed a SINGLE duplex 15-amp outlet - if I could find a NEMA 5-20 duplex outlet that didn't cost an arm and a leg I could upgrade the rigs quite a bit (though PS tend to get a lot more expensive per watt past around the 860 watt range, and are starting to climb at THAT level).
If you're not a trained electrician though, I'd not recommend doing it yourself (I was a union-trained Journeyman and licensed electrician for a while in my youth, and I've kept up on the relevant Code changes).
|
I'm no longer legendary just in my own mind! Like something I said? Donations gratefully accepted. LYLnTKvLefz9izJFUvEGQEZzSkz34b3N6U (Litecoin) 1GYbjMTPdCuV7dci3iCUiaRrcNuaiQrVYY (Bitcoin)
|
|
|
philipma1957
Legendary
Offline
Activity: 4312
Merit: 8839
'The right to privacy matters'
|
|
March 17, 2018, 12:54:52 AM |
|
|
|
|
|
duhjeff (OP)
Newbie
Offline
Activity: 106
Merit: 0
|
|
March 17, 2018, 10:04:54 PM |
|
So I’ve decided to hire an electrician to come wire me some 220’s. I’m thinking 2 100 amp outlet (If possible since I live in ny and I’m hoping these old houses can handle that much power). Anyway, What do you guys do for extension cords since most pdu I see are 30 amps only....how do you guys do it?
|
|
|
|
philipma1957
Legendary
Offline
Activity: 4312
Merit: 8839
'The right to privacy matters'
|
|
March 18, 2018, 12:33:45 AM |
|
So I’ve decided to hire an electrician to come wire me some 220’s. I’m thinking 2 100 amp outlet (If possible since I live in ny and I’m hoping these old houses can handle that much power). Anyway, What do you guys do for extension cords since most pdu I see are 30 amps only....how do you guys do it? Do three 30 amp A 30 amp will do 4 s9 Or 4 six card rigs of 1080tis
|
|
|
|
duhjeff (OP)
Newbie
Offline
Activity: 106
Merit: 0
|
|
March 18, 2018, 12:51:26 AM |
|
So I’ve decided to hire an electrician to come wire me some 220’s. I’m thinking 2 100 amp outlet (If possible since I live in ny and I’m hoping these old houses can handle that much power). Anyway, What do you guys do for extension cords since most pdu I see are 30 amps only....how do you guys do it? Do three 30 amp A 30 amp will do 4 s9 Or 4 six card rigs of 1080tis Thank you! This is the type of answer I was looking for (in plain dumb english). I'm planning to run 3 13 card board (B250 board) and possibly upgrading to 19 on each board if I can ever get my hands on those....I read it somewhere that 30 amp should be good for 5000w so I guess 3 30 amp is probably my best bet right? Again, thanks for the answer guys! Jeff-
|
|
|
|
philipma1957
Legendary
Offline
Activity: 4312
Merit: 8839
'The right to privacy matters'
|
|
March 18, 2018, 12:57:38 AM |
|
So I’ve decided to hire an electrician to come wire me some 220’s. I’m thinking 2 100 amp outlet (If possible since I live in ny and I’m hoping these old houses can handle that much power). Anyway, What do you guys do for extension cords since most pdu I see are 30 amps only....how do you guys do it? Do three 30 amp A 30 amp will do 4 s9 Or 4 six card rigs of 1080tis Thank you! This is the type of answer I was looking for (in plain dumb english). I'm planning to run 3 13 card board (B250 board) and possibly upgrading to 19 on each board if I can ever get my hands on those....I read it somewhere that 30 amp should be good for 5000w so I guess 3 30 amp is probably my best bet right? Again, thanks for the answer guys! Jeff- 30 derates to 24 to be safe for a 24-7-365 run time 220 can be 217 to 242 volts in USA residential So 217 x 24 = 5200 watts. Minimum If you are near a hot transformer with no drop I am and I run 239- 242 volts Or 240 x 24 = 5760 watts. I have been able to run at 5500 watts year round
|
|
|
|
gotminer
Member
Offline
Activity: 644
Merit: 24
|
|
March 18, 2018, 01:03:43 AM |
|
My first comment. Listen to Phillip. He know's what he is talking about.
I wouldn't have felt comfortable re-arranging my breaker box, installing 30A breakers, running the wiring, and installing the outlets myself. I have a friend who is an electrician, so I paid him to do it. I had two 30A outlets installed in my mining room. They were short runs, so only ended up having to get 50' of romex. For two outlets, the materials shouldn't cost more than $200 or so. The L6 recepticals are around 20-25 each. 50ft of 10-3 romex was $75. The 30A breakers he already had and didn't charge me any extra for. There are some other odds and ends that you'll need.
I ended up paying him $100 for the labor and around $150-$175 for the materials.
|
Ok, I want you to walk back in there and very calmly, very politely tell the risk assessors to fuck off! -Mark Baum
|
|
|
philipma1957
Legendary
Offline
Activity: 4312
Merit: 8839
'The right to privacy matters'
|
|
March 18, 2018, 01:39:02 AM |
|
My first comment. Listen to Phillip. He know's what he is talking about.
I wouldn't have felt comfortable re-arranging my breaker box, installing 30A breakers, running the wiring, and installing the outlets myself. I have a friend who is an electrician, so I paid him to do it. I had two 30A outlets installed in my mining room. They were short runs, so only ended up having to get 50' of romex. For two outlets, the materials shouldn't cost more than $200 or so. The L6 recepticals are around 20-25 each. 50ft of 10-3 romex was $75. The 30A breakers he already had and didn't charge me any extra for. There are some other odds and ends that you'll need.
I ended up paying him $100 for the labor and around $150-$175 for the materials.
Nice price for that amount of work you have a good friend
|
|
|
|
|