I am usa based I have 3 of them..
One) they will burn up most power supplies. -----------killed 2 power supplies
Two) If you get a good power supply and run 49 sticks you may over heat the hub. ------------melted the fuse supplied
it was a 40 amp fuse. they issue is a 40 amp fuse will not blow but it will get hot enough to melt shit. I put in 30 amp fuses and problem stopped.
Three) If you are willing to run 35-42 sticks they are okay.-------- I now run 2 of them with 36 and 39 sticks each no worries
here are 3 in action before I melted the 40 amp fuse