Hello:  I have had a few power outages in the last few days and would like to buy a UPS.

I have a 1300Waat psu
I spend 900 watts on mining rig.

Do I buy a UPS that handles up to 1300watts or around 900 watts?  Any suggestion out there?  Thank you for any answers.



Kenshin
Sr. Member
****
Offline Offline

Activity: 280
Merit: 250


View Profile
January 12, 2014, 03:41:07 AM
 #2

Hello:  I have had a few power outages in the last few days and would like to buy a UPS.

I have a 1300Waat psu
I spend 900 watts on mining rig.

Do I buy a UPS that handles up to 1300watts or around 900 watts?  Any suggestion out there?  Thank you for any answers.





What is the point of having a UPS, if your power is down, so is your internet access. Just get a surge protector if you are worry about your equipment. UPS can only last maximum 2 hours, if you get an expensive one.
galtbit (OP)
Full Member
***
Offline Offline

Activity: 231
Merit: 100


View Profile
January 12, 2014, 04:14:12 AM
 #3

Hello:  I have had a few power outages in the last few days and would like to buy a UPS.

I have a 1300Waat psu
I spend 900 watts on mining rig.

Do I buy a UPS that handles up to 1300watts or around 900 watts?  Any suggestion out there?  Thank you for any answers.





What is the point of having a UPS, if your power is down, so is your internet access. Just get a surge protector if you are worry about your equipment. UPS can only last maximum 2 hours, if you get an expensive one.

The power has only gone out for a few minutes, and not hours.
AnonMZ
Newbie
*
Offline Offline

Activity: 11
Merit: 0


View Profile
January 12, 2014, 05:45:50 AM
 #4

Hello:  I have had a few power outages in the last few days and would like to buy a UPS.

I have a 1300Waat psu
I spend 900 watts on mining rig.

Do I buy a UPS that handles up to 1300watts or around 900 watts?  Any suggestion out there?  Thank you for any answers.





It may depend among other things, on the specs of your power supply. Is it Power Factor Corrected Power supply?

As an example:
From: http://www.pcguide.com/ref/power/ext/ups/funcSizing-c.html

“ Let's say we have a 650 VA UPS. The wattage limit is not specified, so to be safe, we use 60%, which yields a limit of 390W. This means any load we run cannot exceed either 650 VA or 390 W. Some sample power supply loads:
•   Regular Power Supply, 500 VA Rating: A regular power supply with a rating of 500 VA will run fine on this UPS, because its power factor is probably about 60%, much as the UPS manufacturer assumed (but you should check its specifications, if you can.). Even if the power factor is 70%, that's still 350 W, under the UPS's limit.
•   Power-Factor-Corrected Power Supply, 500 VA Rating: Some power supplies have circuitry added to them that corrects the power factor to approximately 100% (sometimes called power factor 1). In this case the power supply will have a 500 VA rating and also a 500 W rating. This power supply will overload the UPS we are discussing here because its W rating is too high.”

See also: Capacity and Run Time
http://www.pcguide.com/ref/power/ext/ups/funcCapacity-c.html

I hope this helps
Unacceptable
Legendary
*
Offline Offline

Activity: 2212
Merit: 1001



View Profile
January 12, 2014, 07:09:25 AM
 #5

Hello:  I have had a few power outages in the last few days and would like to buy a UPS.

I have a 1300Waat psu
I spend 900 watts on mining rig.

Do I buy a UPS that handles up to 1300watts or around 900 watts?  Any suggestion out there?  Thank you for any answers.





What is the point of having a UPS, if your power is down, so is your internet access. Just get a surge protector if you are worry about your equipment. UPS can only last maximum 2 hours, if you get an expensive one.

Wrong.....my power goes out quite often & randomly for 5 seconds - 5 minutes,my UPS keeps my miners running & internet up  Grin

It also "smoothes" the power,keeps spikes from damaging my equipment.

If the power is down for longer,well I'm SOL  Roll Eyes

I'd go with a 1500 watt,ALWAYS add 20% to your total.You don't want to stress your PSU or your UPS  Wink

Something like this would do just fine:

http://www.walmart.com/ip/Cyberpower-OR2200LCDRTXL2U-2200VA-UPS-AVR-2U-RM-T/23140122

"If you run into an asshole in the morning, you ran into an asshole. If you run into assholes all day long, you are the asshole."  -Raylan Givens
Got GOXXED ?? https://www.youtube.com/watch?v=9KiqRpPiJAU&feature=youtu.be
"An ASIC being late is perfectly normal, predictable, and legal..."Hashfast & BFL slogan Smiley
galtbit (OP)
Full Member
***
Offline Offline

Activity: 231
Merit: 100


View Profile
January 12, 2014, 07:26:10 AM
Last edit: January 12, 2014, 07:44:34 AM by galtbit
 #6

Maybe some more info would help:

I have a Rosewill LIGHTNING-1300 1300W PSU
http://www.newegg.com/Product/Product.aspx?Item=N82E16817182063

I know the PSU isnt using all 1300 watts but the mining rig uses around 900 watts.






Thank you Anon and Unacceptable for your answers.
vapourminer
Legendary
*
Offline Offline

Activity: 4508
Merit: 4104


what is this "brake pedal" you speak of?


View Profile
January 12, 2014, 11:53:31 AM
 #7

What is the point of having a UPS, if your power is down, so is your internet access.

not true.

people with DSL/EVDO (plus maybe satellite?) still have internet when the power goes out.

my mining hardware itself is just on surge protectors, but the controlling computer has a UPS. I just prefer clean shutdowns for my rigs rather than just yanking the power out from under them.

I use APC and cyberpower to keep my various boxes up.



erre
Legendary
*
Offline Offline

Activity: 1680
Merit: 1205



View Profile
January 12, 2014, 05:11:05 PM
 #8

Will frequent blackout damage hardware?

I'll install my miner in a place when i expect at least 1 short blackout/day, but as far as i understand i need only a good surge protection to be pretty sure to not damage my hardware...

Roll a dice FOR FREE every hour, and win up to $200 in btc ---> CLICK HERE

Tip me using the LIGHTING NETWORK! -->https://tippin.me/@Erre96344121
AnonMZ
Newbie
*
Offline Offline

Activity: 11
Merit: 0


View Profile
January 12, 2014, 05:19:46 PM
 #9

Maybe some more info would help:

I have a Rosewill LIGHTNING-1300 1300W PSU
http://www.newegg.com/Product/Product.aspx?Item=N82E16817182063

I know the PSU isnt using all 1300 watts but the mining rig uses around 900 watts.






Thank you Anon and Unacceptable for your answers.

From your link, and going to the more expanded specs from the Rosewill page:
http://www.rosewill.com/products/1799/ProductDetail_Overview.htm
“Active-PFC with auto AC-input voltage adjustment(100-240V)”

It appears that your PSU is equipped with Active PFC (Power Factor Correction), so it falls under the second example I’ve posted above.

To be safe, you’d require a higher VA rating UPS to handle the power. A 1.6 to 2KVA as Unaccptable noted should be sufficient, for the load. That would cover your capacity (load) needs, and run time would ofc depend on battery(s) Ah size.

In addition, due to the PFC, the UPS would need to be “highend/smart” or closer to true sine wave output.


This maybe of help: https://www.dougv.com/2010/03/01/active-pfc-enabled-psus-are-not-compatable-with-most-low-end-ups/
“In short, if you send a high-end PSU the current created by a lower-end UPS, the PSU’s built-in power factor correction hates it, and cuts power to the PC immediately. As in, the exact thing you bought the UPS to prevent in the first place is exactly what happens.

While I understand the value in having a high-performing PSU — less heat, more power, protection for internal components — a straight-up power off of the PC is never a good thing. So your choices are either to forgo a UPS, purchase a really expensive UPS, or purchase a low-cost PSU”
galtbit (OP)
Full Member
***
Offline Offline

Activity: 231
Merit: 100


View Profile
January 12, 2014, 09:21:44 PM
 #10

Maybe some more info would help:

I have a Rosewill LIGHTNING-1300 1300W PSU
http://www.newegg.com/Product/Product.aspx?Item=N82E16817182063

I know the PSU isnt using all 1300 watts but the mining rig uses around 900 watts.






Thank you Anon and Unacceptable for your answers.

From your link, and going to the more expanded specs from the Rosewill page:
http://www.rosewill.com/products/1799/ProductDetail_Overview.htm
“Active-PFC with auto AC-input voltage adjustment(100-240V)”

It appears that your PSU is equipped with Active PFC (Power Factor Correction), so it falls under the second example I’ve posted above.

To be safe, you’d require a higher VA rating UPS to handle the power. A 1.6 to 2KVA as Unaccptable noted should be sufficient, for the load. That would cover your capacity (load) needs, and run time would ofc depend on battery(s) Ah size.

In addition, due to the PFC, the UPS would need to be “highend/smart” or closer to true sine wave output.


This maybe of help: https://www.dougv.com/2010/03/01/active-pfc-enabled-psus-are-not-compatable-with-most-low-end-ups/
“In short, if you send a high-end PSU the current created by a lower-end UPS, the PSU’s built-in power factor correction hates it, and cuts power to the PC immediately. As in, the exact thing you bought the UPS to prevent in the first place is exactly what happens.

While I understand the value in having a high-performing PSU — less heat, more power, protection for internal components — a straight-up power off of the PC is never a good thing. So your choices are either to forgo a UPS, purchase a really expensive UPS, or purchase a low-cost PSU”


Hello Anon:  Thank you for the info you supplied.  I was able to plug my rig directly into my Kill A Watt and see that the total amount of Watts is only 720 the most.  Thats  without the monitor, fan an other things not connected to it.  Thats what I really want.  Just to cover the rig.  In that case, what do you think of this UPS?  It can 850VA and t says it has a pure sine wave.  New Egg says it handles 1350 VA 810 w  which may cover it.  Am I on the right track?

http://www.newegg.com/Product/Product.aspx?Item=N82E16842102133
philipma1957
Legendary
*
Offline Offline

Activity: 4298
Merit: 8837


'The right to privacy matters'


View Profile WWW
January 12, 2014, 10:37:48 PM
Last edit: January 12, 2014, 11:17:39 PM by philipma1957
 #11

Maybe some more info would help:

I have a Rosewill LIGHTNING-1300 1300W PSU
http://www.newegg.com/Product/Product.aspx?Item=N82E16817182063

I know the PSU isnt using all 1300 watts but the mining rig uses around 900 watts.






Thank you Anon and Unacceptable for your answers.

From your link, and going to the more expanded specs from the Rosewill page:
http://www.rosewill.com/products/1799/ProductDetail_Overview.htm
“Active-PFC with auto AC-input voltage adjustment(100-240V)”

It appears that your PSU is equipped with Active PFC (Power Factor Correction), so it falls under the second example I’ve posted above.

To be safe, you’d require a higher VA rating UPS to handle the power. A 1.6 to 2KVA as Unaccptable noted should be sufficient, for the load. That would cover your capacity (load) needs, and run time would ofc depend on battery(s) Ah size.

In addition, due to the PFC, the UPS would need to be “highend/smart” or closer to true sine wave output.


This maybe of help: https://www.dougv.com/2010/03/01/active-pfc-enabled-psus-are-not-compatable-with-most-low-end-ups/
“In short, if you send a high-end PSU the current created by a lower-end UPS, the PSU’s built-in power factor correction hates it, and cuts power to the PC immediately. As in, the exact thing you bought the UPS to prevent in the first place is exactly what happens.

While I understand the value in having a high-performing PSU — less heat, more power, protection for internal components — a straight-up power off of the PC is never a good thing. So your choices are either to forgo a UPS, purchase a really expensive UPS, or purchase a low-cost PSU”


Hello Anon:  Thank you for the info you supplied.  I was able to plug my rig directly into my Kill A Watt and see that the total amount of Watts is only 720 the most.  Thats  without the monitor, fan an other things not connected to it.  Thats what I really want.  Just to cover the rig.  In that case, what do you think of this UPS?  It can 850VA and t says it has a pure sine wave.  New Egg says it handles 1350 VA 810 w  which may cover it.  Am I on the right track?

http://www.newegg.com/Product/Product.aspx?Item=N82E16842102133



you need better then that .  there is a great ebay/refurbished seller  I will find the link.


http://www.ebay.com/sch/excessups/m.html?item=350959716966&pt=US_Uninterruptible_Power_Supplies&hash=item51b6d44a66&rt=nc&_trksid=p2047675.l2562

the one below is better
http://www.ebay.com/itm/APC-SMART-UPS-1500-1500VA-980W-SUA1500-USB-UPS-NEW-BATTERIES-/350972274739?pt=US_Uninterruptible_Power_Supplies&hash=item51b793e833

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
galtbit (OP)
Full Member
***
Offline Offline

Activity: 231
Merit: 100


View Profile
January 12, 2014, 10:57:49 PM
 #12

Newegg has one that goes up to 900watts.  That would be great Phillip.

http://www.newegg.com/Product/Product.aspx?Item=N82E16842102134
philipma1957
Legendary
*
Offline Offline

Activity: 4298
Merit: 8837


'The right to privacy matters'


View Profile WWW
January 12, 2014, 11:19:42 PM
 #13

Newegg has one that goes up to 900watts.  That would be great Phillip.

http://www.newegg.com/Product/Product.aspx?Item=N82E16842102134


yeah the newegg one is a better choice and I did find 1050 watt one above.  I have 5 ups units from the ebay seller.  he is good.  the 900 or the 1050 .  can run the router and your lcd screen .


My best unit  is this one:

http://www.ebay.com/itm/APC-SMART-UPS-2200VA-1600W-RM-3U-SU2200RM3U-BATTERY-BACKUP-RACKMOUNT-3U-UPS-/350887385482?pt=US_Uninterruptible_Power_Supplies&hash=item51b284998a

but it cost too much and is over kill for your needs

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
galtbit (OP)
Full Member
***
Offline Offline

Activity: 231
Merit: 100


View Profile
January 13, 2014, 12:06:22 AM
 #14

Thanks again.  I guess the 900 watt from NE is fine.

fr4nkthetank
Legendary
*
Offline Offline

Activity: 2294
Merit: 1182


Now the money is free, and so the people will be


View Profile
January 13, 2014, 03:45:15 PM
 #15

Hello:  I have had a few power outages in the last few days and would like to buy a UPS.

I have a 1300Waat psu
I spend 900 watts on mining rig.

Do I buy a UPS that handles up to 1300watts or around 900 watts?  Any suggestion out there?  Thank you for any answers.





What is the point of having a UPS, if your power is down, so is your internet access. Just get a surge protector if you are worry about your equipment. UPS can only last maximum 2 hours, if you get an expensive one.


my cable modem is plugged in the UPS, so internet does not go down when power goes down.

Power outages are mostly local and localised and not widespread.  Unless you live in a shithole or a third world country.  UPS FTW if you have frequent and short power cuts
Jahare
Member
**
Offline Offline

Activity: 77
Merit: 10


View Profile
January 14, 2014, 07:23:58 PM
 #16

http://www.overstock.com/Electronics/APC-Back-UPS-BR1500G-1500-VA-Tower-UPS/5613995/product.html?refccid=CC7KV3WD3OVL5HSOZKVG5TKMH4&searchidx=3

Overstock accepts bitcoin now, just got a few items, paid for with Bitcoin.

LTC:   LRsiHqFcSXGyP9zvYUvJxe7N7ivLcVb72z       FTC:  71rY4vP8wWEyKx9FNBvHM9MFrNH9QRboTf
BTC:  14NvriZHaLyTqaG8phYMagN2gB9WsB3Sj5    NMC:  N7XPo3E3fEDAFUhyrvQBHzYkA45kkjWDse
QRK:  QT5JhzHDU4pNeKzA9GWoaBh8bzjPK9cADS  DOGE: DK2wCYTux4JpcnmRGsKmnc5qCY615hsiAV
Kenshin
Sr. Member
****
Offline Offline

Activity: 280
Merit: 250


View Profile
January 14, 2014, 08:13:28 PM
 #17

Well, when there is a power cut in my area, it normally last a few hours.
crazyates
Legendary
*
Offline Offline

Activity: 952
Merit: 1000



View Profile
January 15, 2014, 12:50:37 AM
 #18

Please tell me that your mining motherboards are set to Power on after failure, and your miner software is set to start with the OS?! (Pretty Please?!) It's usually a simple BIOS setting to change, and the auto-start is not hard to do in Windows or Linux.

Even if the power would go out, your miners would be back hashing within 2 minutes of the power coming back on.

And think about it: Are you really going to mine enough in those few minutes you're down to justify the cost of hundreds of dollars spent on a UPS?

Tips? 1crazy8pMqgwJ7tX7ZPZmyPwFbc6xZKM9
Previous Trade History - Sale Thread
k2_1971
Newbie
*
Offline Offline

Activity: 45
Merit: 0


View Profile WWW
January 15, 2014, 01:11:18 AM
 #19

Please tell me that your mining motherboards are set to Power on after failure, and your miner software is set to start with the OS?! (Pretty Please?!) It's usually a simple BIOS setting to change, and the auto-start is not hard to do in Windows or Linux.

Even if the power would go out, your miners would be back hashing within 2 minutes of the power coming back on.

And think about it: Are you really going to mine enough in those few minutes you're down to justify the cost of hundreds of dollars spent on a UPS?

+1

You're better off running your gear through a decent surge protector (I run all my mining systems through a rackmount tripp lite) or even better, some type of line conditioner that keep the voltage to your components steady as well as providing surge/spike protection. Brown outs are much worse than any black out.