Bitcoin Forum
May 06, 2024, 07:59:25 AM *
News: Latest Bitcoin Core release: 27.0 [Torrent]
 
   Home   Help Search Login Register More  
Pages: [1] 2 »  All
  Print  
Author Topic: Introduction - 126 GPU & 13 ASics - Help with Massive heat & ventilation problem  (Read 599 times)
ssaleen (OP)
Newbie
*
Offline Offline

Activity: 13
Merit: 0


View Profile
July 06, 2018, 08:38:12 PM
 #1

Hello Guys,

I have a 126 GPU farm that was cooled by 5 split ac's 2 ton each  (total 10 ton capacity). I recently added 13 antminer s9i and the following is what happened

1. Without a room for the antminers the ambient temperature for the mining room became 41 degree celsius with all 5 ac's on.
2. The room that i use for mining is 8m x 5m x 3.8m (LxWxH)
3. outside temperature reach to 47 degrees in UAE
4. Fresh air intake without cooling wont work.
5. my dream is to turn off all ac's

My attempt to resolve the problem is as follows

-I built a room (Hot isle) for the antminers that included a window (I just put partition from gipson board on the back of the rack and the back wall is a window. I also put a gibson board on the back of the rack with holes for the 120cm exhaust fans and sealed it. However the exhaust air is removed from the window using a 2600cfm HD exhaust fan -(200cfm per miner x 13)
-I built a hot isle for the GPU rigs and i figured i need 250cfm per 13 gpu rig with total capacity of 2200cfm. Put 2 inline fans in series with 12" ducting for total capacity  of 2200cfm


Problem:

-the antminers and the exhaust fans now take all the air from the room and is alot of air is coming from the door edges and alot of air noises in my house etc.
-I have a total of 4800 cfm of air being exhausted

My questions
-Will an evaporative AC with high cfm be a good option since our humidity level is at 30-40% in Abu Dhabi (build a room inside mining room with an evaporative ac inside with the window open and a dehumidifier - the outlet for air from the evaporative ac will be the only thing exposed from the room pointing towards the rigs and antminers) or Duct option
-what other options i have to bring in cool 4800 cfm of fresh air


thanks for the help,. I will post pictures soon



1714982365
Hero Member
*
Offline Offline

Posts: 1714982365

View Profile Personal Message (Offline)

Ignore
1714982365
Reply with quote  #2

1714982365
Report to moderator
1714982365
Hero Member
*
Offline Offline

Posts: 1714982365

View Profile Personal Message (Offline)

Ignore
1714982365
Reply with quote  #2

1714982365
Report to moderator
1714982365
Hero Member
*
Offline Offline

Posts: 1714982365

View Profile Personal Message (Offline)

Ignore
1714982365
Reply with quote  #2

1714982365
Report to moderator
I HATE TABLES I HATE TABLES I HA(╯°□°)╯︵ ┻━┻ TABLES I HATE TABLES I HATE TABLES
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
Philopolymath
Sr. Member
****
Offline Offline

Activity: 558
Merit: 295

Walter Russell's Cosmogony is RIGHT!


View Profile
July 06, 2018, 08:43:24 PM
 #2

Move to Iceland

Support Alien Beer Circle research...www.youtube.com/watch?v=MRXDk2RMQ4A
ssaleen (OP)
Newbie
*
Offline Offline

Activity: 13
Merit: 0


View Profile
July 06, 2018, 08:54:48 PM
 #3

HA

wont leave UAE anytime soon haha.

ccgllc
Copper Member
Full Member
***
Offline Offline

Activity: 658
Merit: 101

Math doesn't care what you believe.


View Profile
July 06, 2018, 08:57:57 PM
 #4

Evaporative cooling, presuming water is cheap, would be a good option.  Yahoo does this on some of their data centers.

Would also suggest bumping that air flow.  I run my datacenter based on 300 cfm/miner (combined flow between the 2 fans) and it works out reasonably well.

Mined for a living since 2017.  Dabbled for years before that.
Linux admin since 0.96 kernel and Slackware distributions on (4) floppies...
ssaleen (OP)
Newbie
*
Offline Offline

Activity: 13
Merit: 0


View Profile
July 06, 2018, 09:25:13 PM
 #5

I will try the evaporative cooling part.

can you please elaborate more on what you mean by bumping the airflow?

thanks
ccgllc
Copper Member
Full Member
***
Offline Offline

Activity: 658
Merit: 101

Math doesn't care what you believe.


View Profile
July 06, 2018, 10:55:29 PM
 #6

I will try the evaporative cooling part.

can you please elaborate more on what you mean by bumping the airflow?

thanks

You used 250 cfm/miner, recommend 300 cfm.

Mined for a living since 2017.  Dabbled for years before that.
Linux admin since 0.96 kernel and Slackware distributions on (4) floppies...
Rodrigo8
Newbie
*
Offline Offline

Activity: 52
Merit: 0


View Profile
July 07, 2018, 01:37:23 PM
Last edit: July 07, 2018, 01:49:05 PM by Rodrigo8
 #7

here your solution
https://www.google.com.au/search?q=Underground+Tubes+for+Passive+Cooling&newwindow=1&rlz=1C1CHBD_en-GBAU751AU751&source=lnms&tbm=isch&sa=X&ved=0ahUKEwidoJi2j43cAhUBHJQKHXPvBg4Q_AUICigB&biw=1680&bih=917

I use this solution on a smaller scale, sorry no photos
https://desertcommunity.wordpress.com/2013/03/03/underground-tubes-for-passive-cooling/
Dagamus(NM)
Newbie
*
Offline Offline

Activity: 48
Merit: 0


View Profile
July 07, 2018, 05:29:07 PM
 #8

Evaporative cooling is limited to a ceiling of about 95F, really falls off after that. Probably best to get them out of your house and into a purpose made shed. Put it on your roof or a garage or an outbuilding made for that purpose.

You can also add insulating materials around the door to help with the noise.

But yeah, more airflow. Even at 47C there is still a large temperature difference to your GPUs and ASICs. Turn off the A/C, increase air flow. Consider purpose built structure outside with massive airflow.
ssaleen (OP)
Newbie
*
Offline Offline

Activity: 13
Merit: 0


View Profile
July 08, 2018, 08:56:30 PM
 #9

thanks for your reply's guys

i have brought in an evaporative ac to rated at 12000 cfm. I was able to turn off 3 ac's from 5 and the average temperature is around 65 degrees at 70% fan speed. problem this pulled alot of dust. i need to do a major cleanup + add filters for the fresh air.

I will upload some photo's of the setup soon and would like to hear your feedback.

principino1984
Newbie
*
Offline Offline

Activity: 72
Merit: 0


View Profile
July 08, 2018, 10:04:24 PM
 #10

thanks, please post some pictures of what you did cause I will need some ideas from further upgrade.

Marco
ssaleen (OP)
Newbie
*
Offline Offline

Activity: 13
Merit: 0


View Profile
July 09, 2018, 03:51:10 PM
Last edit: July 11, 2018, 09:23:35 PM by ssaleen
 #11

Old setup (GPU rigs)

https://ibb.co/k8mTnT
https://ibb.co/k34W7T

Evap Cooler

https://ibb.co/dAQFZ8
https://ibb.co/jj0cgo
https://ibb.co/eZDV1o

Dust Storm Sad

https://ibb.co/c6cJnT

ASIC's
https://ibb.co/dobHgo
https://ibb.co/fWeg7T  2 inline exhaust fans and the Electric Panel or DB

Aisc exhaust @ 2600 CFM for 13 antminers
https://ibb.co/mAmuST

NEW racks and tear down
https://ibb.co/c4Ungo
https://ibb.co/hhi2E8
https://ibb.co/my7JnT
https://ibb.co/g3Xq1o

Box Fan
https://www.homedepot.com/p/Lasko-20-in-3-Speed-Weather-Shield-Performance-Box-Fan-3720/203749141


any recommendation on anything that i should try?

thanks
principino1984
Newbie
*
Offline Offline

Activity: 72
Merit: 0


View Profile
July 10, 2018, 01:11:21 PM
 #12

can you post full image link please? With those thumbnail is almost impossible to understand anything

Marco
yianni
Member
**
Offline Offline

Activity: 141
Merit: 18

BScEE, BScCS, MScCS


View Profile
July 11, 2018, 12:36:03 AM
 #13

Hello Guys,

I have a 126 GPU farm that was cooled by 5 split ac's 2 ton each  (total 10 ton capacity). I recently added 13 antminer s9i and the following is what happened

1. Without a room for the antminers the ambient temperature for the mining room became 41 degree celsius with all 5 ac's on.
2. The room that i use for mining is 8m x 5m x 3.8m (LxWxH)
3. outside temperature reach to 47 degrees in UAE
4. Fresh air intake without cooling wont work.
5. my dream is to turn off all ac's

My attempt to resolve the problem is as follows

-I built a room (Hot isle) for the antminers that included a window (I just put partition from gipson board on the back of the rack and the back wall is a window. I also put a gibson board on the back of the rack with holes for the 120cm exhaust fans and sealed it. However the exhaust air is removed from the window using a 2600cfm HD exhaust fan -(200cfm per miner x 13)
-I built a hot isle for the GPU rigs and i figured i need 250cfm per 13 gpu rig with total capacity of 2200cfm. Put 2 inline fans in series with 12" ducting for total capacity  of 2200cfm


Problem:

-the antminers and the exhaust fans now take all the air from the room and is alot of air is coming from the door edges and alot of air noises in my house etc.
-I have a total of 4800 cfm of air being exhausted

My questions
-Will an evaporative AC with high cfm be a good option since our humidity level is at 30-40% in Abu Dhabi (build a room inside mining room with an evaporative ac inside with the window open and a dehumidifier - the outlet for air from the evaporative ac will be the only thing exposed from the room pointing towards the rigs and antminers) or Duct option
-what other options i have to bring in cool 4800 cfm of fresh air


thanks for the help,. I will post pictures soon





I live in a similar climate as you do (Mediterranean). It gets close to 45 degrees in the summer.
I'm running 2x18000 CMH evaporative coolers mounted outside the warehouse and use insulated ducts to bring the cold air inside to cool 100 S9s.
Make sure your ducts are insulated otherwise they will rust.
The trick was to use a water cooler to cool the water supply to the cooler as 45 degrees is too high for these coolers.
No need to worry about moisture as these miners can handle up to 95% relative humidity. As long as the chips stay hot there will be no condensation.
I have a 7 meter tall ceiling so all the hot air goes up and don't even need exhaust fans. Just keep open windows on the top side and hot air is just pushed out due to positive pressure in the warehouse.
As far as I recall UAE has high humidity levels though so that's a serious negative factor for these swamp coolers.
Nice thing about swamp coolers is that in winter you can just use them as intake fans without any water supply.
Another thing to consider is that these industrial level swamp coolers go into self cleaning mode twice a day for about 5-8 minutes. So you need to watch your temperatures during that time.
Also better choose a 3 phase swamp cooler to better balance your load. It's a bit more expensive but it takes away the headache of load balancing.
Hope this helps.
Rkoshay
Jr. Member
*
Offline Offline

Activity: 96
Merit: 3


View Profile
July 11, 2018, 12:43:22 AM
 #14

If you can handle the initial expense I think the post with the ground source heat pump is a good way to go, get down about 100 feet and the temperature is nice and cool.
yianni
Member
**
Offline Offline

Activity: 141
Merit: 18

BScEE, BScCS, MScCS


View Profile
July 11, 2018, 12:54:10 AM
 #15

If you can handle the initial expense I think the post with the ground source heat pump is a good way to go, get down about 100 feet and the temperature is nice and cool.

You are talking about geothermal correct? I looked into that when I was doing my setup. This is a good option to cool your house. Unfortunately when you have a bunch of miners pushing hot air at a rate of 5.6CMM each, plus an outside temperature in the mid 40s the heat exchanger simply cannot keep up.
lunobird
Full Member
***
Offline Offline

Activity: 846
Merit: 115


View Profile
July 11, 2018, 02:50:04 AM
 #16

Go full open air. Mine it outside the house. No need for cooling or exhaust. Just make sure it doesnt rain and blow dust out every week
Metroid
Sr. Member
****
Offline Offline

Activity: 2142
Merit: 353


Xtreme Monster


View Profile
July 11, 2018, 05:22:01 AM
 #17

the exhausts you have are a joke, change to industrial grade and large ones 50cm and over, one 100cm 2000rpm could do the trick.

BTC Address: 1DH4ok85VdFAe47fSVXNVctxkFhUv4ujbR
ssaleen (OP)
Newbie
*
Offline Offline

Activity: 13
Merit: 0


View Profile
July 11, 2018, 08:59:38 PM
 #18

Guys sorry for the bad pictures earlier.

i was able to switch off 3 A/C when i got the evaporative cooler. However, i am facing high temp on few individual GPU here and there. I have decided to tear down the whole farm and build every thing again using new racks and using BOX fans to pull hot air from around GPU's into the hot isle where they will be exhausted by two 12" 1100 CFM inline fans.

The method that  Rodrigo8 recommended will need me to get some permits from the municipality and it will cost alot of money and its is no option for me.


Here are pictures that are not thumbnails of the:-

Old setup (GPU rigs)

https://ibb.co/k8mTnT
https://ibb.co/k34W7T

Evap Cooler

https://ibb.co/dAQFZ8
https://ibb.co/jj0cgo
https://ibb.co/eZDV1o

Dust Storm Sad

https://ibb.co/c6cJnT

ASIC's
https://ibb.co/dobHgo
https://ibb.co/fWeg7T  2 inline exhaust fans and the Electric Panel or DB

Aisc exhaust @ 2600 CFM for 13 antminers
https://ibb.co/mAmuST

NEW racks and tear down
https://ibb.co/c4Ungo
https://ibb.co/hhi2E8
https://ibb.co/my7JnT
https://ibb.co/g3Xq1o

Box Fan
https://www.homedepot.com/p/Lasko-20-in-3-Speed-Weather-Shield-Performance-Box-Fan-3720/203749141


any recommendation on anything that i should try?

thanks









bartjeyayo
Newbie
*
Offline Offline

Activity: 29
Merit: 0


View Profile
July 11, 2018, 09:11:47 PM
 #19

Hello,

I own a small mining farm with currently 162 1070ti/1080ti GPU's. I made some holes in the floor for sucking in fresh air, it's currently around 40 degrees in the room and on the top of the room i have two industrial fans sucking out all the air. Currently all GPU's won't get warmer then 70 degrees. The room itself is around 5m x 5m x 2,5m

https://image.ibb.co/eqjdMo/miners.png

Even when outside temperature is -10 degrees, cards are same temps. Hottest outside temp i got was 30 degrees. Inside the temp is around 20 ~ 40 degrees.

The two fans that I'm using are 350watt each and sucking out more air then they can. If you are interested I can make some pictures for you next time i visit the farm. Let me know.

Greetings.
ssaleen (OP)
Newbie
*
Offline Offline

Activity: 13
Merit: 0


View Profile
July 11, 2018, 09:17:27 PM
 #20

Hello,

I own a small mining farm with currently 162 1070ti/1080ti GPU's. I made some holes in the floor for sucking in fresh air, it's currently around 40 degrees in the room and on the top of the room i have two industrial fans sucking out all the air. Currently all GPU's won't get warmer then 70 degrees. The room itself is around 5m x 5m x 2,5m

https://image.ibb.co/eqjdMo/miners.png

Even when outside temperature is -10 degrees, cards are same temps. Hottest outside temp i got was 30 degrees. Inside the temp is around 20 ~ 40 degrees.

The two fans that I'm using are 350watt each and sucking out more air then they can. If you are interested I can make some pictures for you next time i visit the farm. Let me know.

Greetings.


yes please send me some pictures of your exhaust fans and setup

thanks
Pages: [1] 2 »  All
  Print  
 
Jump to:  

Powered by MySQL Powered by PHP Powered by SMF 1.1.19 | SMF © 2006-2009, Simple Machines Valid XHTML 1.0! Valid CSS!