Is the 2350 cfm a calculation factoring the length of the ducting? The one on the quick price out is 2.8k cfm. So I should move to 3k+ for sure from you recommendation?
Reason for one hole is this is our garage, need to keep it aesthetically in tack more so than what I would once I get to the point of moving to find cheaper power.
the image was not very clear I thought it read 2350cfm.
but as to hole size and length of tubing.
the longer the tube = more friction
the smaller the diameter = more friction
so a 1600cfm fan with 1 foot tube length to move the air
and at the same 1 foot diameter moves air a lot better then
a 2800 cfm fan with a 10 inch tube and a six foot length .
when I read your chart I saw a reducer in it 12 to 10 inches
I saw a tube six feet long
I read a 2350 cfm fan
and I thought it may not work
if the tubing is 1 foot with no reducer
the fan is 2800cfm
and the tube length is six feet I think you will be close to okay