Hair dryer? Please think of them like an air conditioner unit. You see how they usually dedicate a separate circuit for those? Same thing.
An S9 (1400w) can take around 8amps at 208v or 5amps at 240v, so at 230 it would be like 6 i think. But that was before asicboost, they are probably a little less demanding nowdays....
Now of course you DON'T plug BOTH of them on the SAME circuit, you just don't. There is the 80/20 rule as well (don't exceed over 80%, leave 20% margin). If you have a 13amp circuit breaker (with 13 amp rated wiring) that only serves a SINGLE S9 unit, períod.
You may serve two units with 20amps. The L3+ are 800w, you could squeeze two to a single 13a circuit as they should be like 4a each. No, you won't burn your house down if everything was installed correctly, meaning the cabling and circuit breakers. If you foolishly swap a circuit breaker with a higher rated one without upgrading its corresponding circuit wire, then you COULD cause a fire...
Do you happen to have a clothes dryer? those usually have a 30amp circuit, you could power 3 units from that.
Please note that according to
EMA, it is currently unprofitable to mine in Singapore. You will lose more money in electricity than what the miners produce at current rates. If your plan is hold for the future, you are essentially purchasing bitcoins.
You will be losing about 4 USD per day per S9. You will also be losing about 2 USD per day for each L3+.
That is, unless you plan to invest in solar panels, etc.