Author Topic: How do you run miners on 440 V/3 Phase ?  (Read 180 times)
pussyhunter6969 (OP)
Member
**
Offline Offline

Activity: 84
Merit: 12


View Profile WWW
March 05, 2019, 06:37:28 PM
Last edit: March 06, 2019, 02:22:33 AM by frodocooper
 #1

Hey the problem is i have 440 Volt / 3 Phase

Are there any power supplies ? that power on 440 V i want to power up few antminer s9

fanatic26_
Full Member
***
Offline Offline

Activity: 294
Merit: 129


View Profile
March 05, 2019, 08:58:32 PM
 #2

You would need a step down transformer to make that happen. there are no PSUs that will work for what you want.
philipma1957
Legendary
*
Online Online

Activity: 4130
Merit: 7907


'The right to privacy matters'


View Profile WWW
March 05, 2019, 09:25:07 PM
Last edit: March 06, 2019, 02:23:04 AM by frodocooper
 #3

try larsonelectronics

https://www.larsonelectronics.com/p-144789-.aspx

that one is bigger than you may want

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
NotFuzzyWarm
Legendary
*
Offline Offline

Activity: 3640
Merit: 2549


Evil beware: We have waffles!


View Profile
March 05, 2019, 09:35:23 PM
 #4

^^ is certainly a nice one but the OP should just check local electrical supply companies for one and save a ton on shipping the monsters.

- For bitcoin to succeed the community must police itself -    My info useful? Donations welcome! 1FuzzyWc2J8TMqeUQZ8yjE43Rwr7K3cxs9
 -Sole remaining active developer of cgminer, Kano's repo is here
-Support Sidehacks miner development. Donations to:   1BURGERAXHH6Yi6LRybRJK7ybEm5m5HwTr
mikeywith
Legendary
*
Offline Offline

Activity: 2226
Merit: 6405


be constructive or S.T.F.U


View Profile
March 06, 2019, 01:10:01 PM
Last edit: March 07, 2019, 12:15:25 AM by frodocooper
 #5

If you have 440v on 3phase this means that you already have 240v between every phase and neutral.

Even more good news is, if you have say total 100 amps on 3 phase 440v it means you have a total of 300 amps on single phase 240v

You can use a voltameter and check the voltage , place the black pin on the neutral wire and the red pin on one of the phases and it should read 240v.

█▀▀▀











█▄▄▄
▀▀▀▀▀▀▀▀▀▀▀
e
▄▄▄▄▄▄▄▄▄▄▄
█████████████
████████████▄███
██▐███████▄█████▀
█████████▄████▀
███▐████▄███▀
████▐██████▀
█████▀█████
███████████▄
████████████▄
██▄█████▀█████▄
▄█████████▀█████▀
███████████▀██▀
████▀█████████
▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀
c.h.
▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄
▀▀▀█











▄▄▄█
▄██████▄▄▄
█████████████▄▄
███████████████
███████████████
███████████████
███████████████
███░░█████████
███▌▐█████████
█████████████
███████████▀
██████████▀
████████▀
▀██▀▀
NotFuzzyWarm
Legendary
*
Offline Offline

Activity: 3640
Merit: 2549


Evil beware: We have waffles!


View Profile
March 06, 2019, 02:36:44 PM
Last edit: March 07, 2019, 12:15:10 AM by frodocooper
 #6

If you have 440v on 3phase this means that you already have 240v between every phase and neutral.

Even more good news is, if you have say total 100 amps on 3 phase 440v it means you have a total of 300 amps on single phase 240v

You can use a voltameter and check the voltage , place the black pin on the neutral wire and the red pin on one of the phases and it should read 240v.

No, 440 line-to-line gives 254.3V line-to-neutral which for most PSU's is above their max Vin rating of 240v.
Line-to-neutral V=440/1.73

As for amps for each phase-to-neutral, It is still only a maximum of 100A per leg but yes, 300A total is possible but only if the loads on all phases are in balance to minimize neutral currents.

ref https://en.wikipedia.org/wiki/Three-phase_electric_power

- For bitcoin to succeed the community must police itself -    My info useful? Donations welcome! 1FuzzyWc2J8TMqeUQZ8yjE43Rwr7K3cxs9
 -Sole remaining active developer of cgminer, Kano's repo is here
-Support Sidehacks miner development. Donations to:   1BURGERAXHH6Yi6LRybRJK7ybEm5m5HwTr
mikeywith
Legendary
*
Offline Offline

Activity: 2226
Merit: 6405


be constructive or S.T.F.U


View Profile
March 06, 2019, 05:05:42 PM
Last edit: March 07, 2019, 12:16:20 AM by frodocooper
 #7

No, 440 line-to-line gives 254.3V line-to-neutral which for most PSU's is above their max Vin rating of 240v.
Line-to-neutral V=440/1.73

As for amps for each phase-to-neutral, It is still only a maximum of 100A per leg but yes, 300A total is possible but only if the loads on all phases are in balance to minimize neutral currents.

ref https://en.wikipedia.org/wiki/Three-phase_electric_power

The calculation is right, if you divide 440 by root 3 you get exactly 254.03V , but i doubt he reads 440v exactly, so there is a good chance he ends up somewhere around 240v, i am not very familiar with the standards in the U.S tho i know the rest of the world uses 380/220v 3/1 phase.

but all that aside, even at 254v he would still be able to run S9s with no problem using APW7 psu from bitmain which has a range of 100v to 264V.

█▀▀▀











█▄▄▄
▀▀▀▀▀▀▀▀▀▀▀
e
▄▄▄▄▄▄▄▄▄▄▄
█████████████
████████████▄███
██▐███████▄█████▀
█████████▄████▀
███▐████▄███▀
████▐██████▀
█████▀█████
███████████▄
████████████▄
██▄█████▀█████▄
▄█████████▀█████▀
███████████▀██▀
████▀█████████
▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀
c.h.
▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄
▀▀▀█











▄▄▄█
▄██████▄▄▄
█████████████▄▄
███████████████
███████████████
███████████████
███████████████
███░░█████████
███▌▐█████████
█████████████
███████████▀
██████████▀
████████▀
▀██▀▀
pussyhunter6969 (OP)
Member
**
Offline Offline

Activity: 84
Merit: 12


View Profile WWW
March 06, 2019, 05:47:45 PM
Last edit: March 07, 2019, 12:16:35 AM by frodocooper
 #8

You would need a step down transformer to make that happen. there are no PSUs that will work for what you want.

ill see if i find any portable units

s_falahati
Newbie
*
Offline Offline

Activity: 21
Merit: 49


View Profile
March 08, 2019, 02:26:42 PM
 #9

I just found a PSU supporting both 180v-250v and 264v-380v ranges from a local vendor capable of providing 12v 200a with overcurrent, overvoltage and overheat protection. But it was priced at 600$. So there are PSUs capable of that. But with 600$ you can buy a miner (or up to 3 if you go with used miners) instead of a PSU.
pussyhunter6969 (OP)
Member
**
Offline Offline

Activity: 84
Merit: 12


View Profile WWW
March 08, 2019, 02:36:33 PM
 #10

I just found a PSU supporting both 180v-250v and 264v-380v ranges from a local vendor capable of providing 12v 200a with overcurrent, overvoltage and overheat protection. But it was priced at 600$. So there are PSUs capable of that. But with 600$ you can buy a miner (or up to 3 if you go with used miners) instead of a PSU.

i got you point but i need to buy a transformer anyways, ill try to find that cheaper