Author Topic: S15/S17 20% KVAR energy loss  (Read 250 times)
Extralarstig (OP)
Newbie
*
Offline Offline

Activity: 9
Merit: 10


View Profile
February 27, 2020, 08:45:20 AM
Last edit: February 28, 2020, 12:08:15 AM by frodocooper
Merited by frodocooper (7), philipma1957 (1), o_e_l_e_o (1), Heisenberg_Hunter (1)
 #1

Hey guys,

while analyzing the efficiency of our farm i noticed a high current running trough our neutral wire (3F+N). Naturally we started checking for any load imbalances but could not find any. Time to get out the old Fluke and start measuring.

Turns out the system was producing a lot of (3th) harmonics. 20% of the total load to be exact. which means our generator consumes 20% more gas due to the VAR energy the transformer has to give. Also skin effect is definitely taking place in our cables, but luckily we over-dimensioned.

currently we are preforming the same measurements on our farms with S17's because there has been running a big current trough the neutral wire as well. Not a good forecast.

My best guess is that the power supply's are distorting the net. Placing a filter could work, but is not very cost efficient.

Has anyone else come across this problem? is this because of the Bitmain power supply's? Do other brands have the same amount of harmonics?

thanks,

Lars
1714560772
Hero Member
*
Offline Offline

Posts: 1714560772

View Profile Personal Message (Offline)

Ignore
1714560772
Reply with quote  #2

1714560772
Report to moderator
The trust scores you see are subjective; they will change depending on who you have in your trust list.
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
1714560772
Hero Member
*
Offline Offline

Posts: 1714560772

View Profile Personal Message (Offline)

Ignore
1714560772
Reply with quote  #2

1714560772
Report to moderator
NotFuzzyWarm
Legendary
*
Offline Offline

Activity: 3612
Merit: 2509


Evil beware: We have waffles!


View Profile
February 27, 2020, 03:48:22 PM
Last edit: March 02, 2020, 02:00:45 PM by NotFuzzyWarm
Merited by frodocooper (3), philipma1957 (1), o_e_l_e_o (1)
 #2

High neutral currents is a common problem when running any sort of non-linear load, in this case, scads of switch-mode PSU's. All of them (not just ones from Bitmain) cause it. For powering large farms, using K-factor rated transformers which are designed to accommodate these loads is a must. Ref this from Jefferson Electric.

Poking around the Jefferson Electric site I do see that they also carry a line of Harmonic Suppression Systems to use with existing distribution transformers and gensets.

- For bitcoin to succeed the community must police itself -    My info useful? Donations welcome! 1FuzzyWc2J8TMqeUQZ8yjE43Rwr7K3cxs9
 -Sole remaining active developer of cgminer, Kano's repo is here
-Support Sidehacks miner development. Donations to:   1BURGERAXHH6Yi6LRybRJK7ybEm5m5HwTr
Extralarstig (OP)
Newbie
*
Offline Offline

Activity: 9
Merit: 10


View Profile
March 01, 2020, 10:03:42 PM
 #3

Alright, thanks for the info!
lightfoot
Legendary
*
Offline Offline

Activity: 3094
Merit: 2239


I fix broken miners. And make holes in teeth :-)


View Profile
March 09, 2020, 06:33:38 PM
Merited by NotFuzzyWarm (1)
 #4

Just as a side note: I was wondering about the power factor of Bitmain and Halong supplies. So I went out to the lab today and did a quick check:

The Bitmain 1600 was showing a power factor of .99 (highly aligned) at 1,000 watts
The Halong supply from a Dragonmint T1 was showing a PF of .99 as well at 500 watts
HP power supplies (700 watt) units I use for testing also show a PF of .99

By comparison a standard ATX supply shows a PF of about .8 and a Gold/80 specification one will show a PF of about .9.

I don't know if Bitmain put crap power supplies in the S15's, but I would say it's probably worth your while to pick up a power factor meter and see what a sample of your units are pulling. Because a 20% reactance would indicate some pretty crappy supplies or something else wrong in the setup that could be addressed.
danieleither
Full Member
***
Offline Offline

Activity: 203
Merit: 407


View Profile
June 28, 2020, 01:23:27 PM
 #5

Yes - I came across the same problem, and learned the hard way. It resulted in the supply cable for the mining room overheating, which then had to be changed for a larger spec cable. 30m of wasted 50mm 4-core plus labour and downtime.

What's really annoying though, is that during the research phase (I'm very new to mining) I came across a number of other topics on here regarding harmonics from miner power supplies where people had asked if this was an issue to take into consideration, with many reputed forum members dismissing it as nonsense.
lightfoot
Legendary
*
Offline Offline

Activity: 3094
Merit: 2239


I fix broken miners. And make holes in teeth :-)


View Profile
June 28, 2020, 02:16:04 PM
Last edit: June 29, 2020, 03:12:59 AM by frodocooper
 #6

Interesting. In your case, what was the source of the problem? I know PF and unbalanced loads can screw up a 3 phase system, did something else catch your mining farm as well?