Author Topic: basic 220v question  (Read 218 times)
avalonmin3r (OP)
Newbie
*
Offline Offline

Activity: 17
Merit: 2


View Profile
August 04, 2020, 03:35:34 PM
 #1

I have only one NEMA 6-20 (220v) plug in my garage. I ran only one asic at a time before the halving which was not a problem.

I see there are more efficient machines out from Antminer (like 1700w at 50+ths) Problem is that they require two (2) power cables.

is there any alternative you guys can think of so I can turn one outlet into 2? Or is it not advised since 2 circuits are needed at 10 amp each and my single 6-20 is only 20 amps? (which would not give me enough headroom).

Just trying to think outloud before I commit to a used antminer , cant seem to find them new for now. from what I read buying directly from them is the best route.
1714655870
Hero Member
*
Offline Offline

Posts: 1714655870

View Profile Personal Message (Offline)

Ignore
1714655870
Reply with quote  #2

1714655870
Report to moderator
1714655870
Hero Member
*
Offline Offline

Posts: 1714655870

View Profile Personal Message (Offline)

Ignore
1714655870
Reply with quote  #2

1714655870
Report to moderator
1714655870
Hero Member
*
Offline Offline

Posts: 1714655870

View Profile Personal Message (Offline)

Ignore
1714655870
Reply with quote  #2

1714655870
Report to moderator
The Bitcoin network protocol was designed to be extremely flexible. It can be used to create timed transactions, escrow transactions, multi-signature transactions, etc. The current features of the client only hint at what will be possible in the future.
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
1714655870
Hero Member
*
Offline Offline

Posts: 1714655870

View Profile Personal Message (Offline)

Ignore
1714655870
Reply with quote  #2

1714655870
Report to moderator
1714655870
Hero Member
*
Offline Offline

Posts: 1714655870

View Profile Personal Message (Offline)

Ignore
1714655870
Reply with quote  #2

1714655870
Report to moderator
DaveF
Legendary
*
Offline Offline

Activity: 3472
Merit: 6259


Crypto Swap Exchange


View Profile WWW
August 04, 2020, 03:53:04 PM
Last edit: August 05, 2020, 12:16:38 AM by frodocooper
 #2

If it's really a 20A 220V circuit:

220V * 20A = 4400W

Since you really do not want to go above 70% full time power pull 4400 *.7 = 3080 round down to 3000 for even more of a margin. An S17+ is 2800 so you still have a 7.5% space on top of that in terms of what is good to do.

You can get a PDU to split it to the 2 inputs.

Not recommending this one or even sure it is the correct one, but something like it is what you need: https://www.ebay.com/itm/233486154937

-Dave

█▀▀▀











█▄▄▄
▀▀▀▀▀▀▀▀▀▀▀
e
▄▄▄▄▄▄▄▄▄▄▄
█████████████
████████████▄███
██▐███████▄█████▀
█████████▄████▀
███▐████▄███▀
████▐██████▀
█████▀█████
███████████▄
████████████▄
██▄█████▀█████▄
▄█████████▀█████▀
███████████▀██▀
████▀█████████
▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀
c.h.
▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄
▀▀▀█











▄▄▄█
▄██████▄▄▄
█████████████▄▄
███████████████
███████████████
███████████████
███████████████
███░░█████████
███▌▐█████████
█████████████
███████████▀
██████████▀
████████▀
▀██▀▀
Steamtyme
Legendary
*
Offline Offline

Activity: 1540
Merit: 2036


Betnomi.com Sportsbook, Casino and Poker


View Profile WWW
August 04, 2020, 05:40:02 PM
Merited by DaveF (1)
 #3

To be sure also check the breaker. When I bought my house I found all sorts of outlet ratings (50, 40,30, 20), running on a mix of 20 and 30 amp breakers.

The 2 power cords do not require 2 different circuits (his used to be done by people running S9's on 110V circuits), it's actually just to reduce the load on the power cord and it's connections. Dave gave you the basic breakdown of how to calculate your load and good advice on a PDU. That's a better option than say wiring another plug onto the same circuit.


░░░░░▄▄██████▄▄
░░▄████▀▀▀▀▀▀████▄
███▀░░░░░░░░░░▀█▀█
███░░░▄██████▄▄░░░██
░░░░░█████████░░░░██▌
░░░░█████████████████
░░░░█████████████████
░░░░░████████████████
███▄░░▀██████▀░░░███
█▀█▄▄░░░░░░░░░░▄███
░░▀████▄▄▄▄▄▄████▀
░░░░░▀▀██████▀▀
Ripmixer
░░░░░▄▄██████▄▄
░░▄████▀▀▀▀▀▀████▄
███▀░░░░░░░░░░▀█▀█
███░░░▄██████▄▄░░░██
░░░░░█████████░░░░██▌
░░░░█████████████████
░░░░█████████████████
░░░░░████████████████
███▄░░▀██████▀░░░███
█▀█▄▄░░░░░░░░░░▄███
░░▀████▄▄▄▄▄▄████▀
░░░░░▀▀██████▀▀
Philipma1957cellphone
Full Member
***
Offline Offline

Activity: 416
Merit: 125


View Profile
August 04, 2020, 05:41:34 PM
 #4

At the moment my internet is down. Storm knock me out. I would need to see the wall socket  that you have. There are a few ways to hook the gear up. But I need to see your wall socket.

This is philipma1957 alt. Do not conduct business  with this account
avalonmin3r (OP)
Newbie
*
Offline Offline

Activity: 17
Merit: 2


View Profile
August 04, 2020, 06:35:50 PM
Last edit: August 05, 2020, 12:18:15 AM by frodocooper
Merited by frodocooper (2)
 #5

happy to provide a picture of my socket. it was put in by an electrician I hired for rather cheap. i think It is a true 20 amp, as it has 2 20 amp breakers, I assume one for each of the 2 positives.

https://i.ibb.co/m9YsVtN/IMG-20200726-202919.jpg

The PDU seems like the answer to what I need. I googled 220v power strip and obviously got nothing.
NotFuzzyWarm
Legendary
*
Offline Offline

Activity: 3626
Merit: 2520


Evil beware: We have waffles!


View Profile
August 04, 2020, 07:44:14 PM
 #6

You can also look for a power cable splitter - 1 male 6L-20 end with 2 female ends that are C15(?) such as Stayonline has

- For bitcoin to succeed the community must police itself -    My info useful? Donations welcome! 1FuzzyWc2J8TMqeUQZ8yjE43Rwr7K3cxs9
 -Sole remaining active developer of cgminer, Kano's repo is here
-Support Sidehacks miner development. Donations to:   1BURGERAXHH6Yi6LRybRJK7ybEm5m5HwTr
avalonmin3r (OP)
Newbie
*
Offline Offline

Activity: 17
Merit: 2


View Profile
August 04, 2020, 09:58:34 PM
Last edit: August 05, 2020, 12:18:47 AM by frodocooper
 #7

this is what I was thinking originally!  Now I have an alternative to a PDU, though I may go with the PDU for peace of mind/safety.

THANK YOU as always.

thanks for shedding some light on all of this.
gmaxwell
Moderator
Legendary
*
Offline Offline

Activity: 4158
Merit: 8382



View Profile WWW
August 04, 2020, 10:13:55 PM
Last edit: August 05, 2020, 12:19:17 AM by frodocooper
 #8

Your outlet is a NEMA 6-20.

I'm personally not a huge fan of NEMA 6-15/6-20, and prefer the locking kind... but that's what you've got, so you'll need to match your PDU up to that.

It's more common to find PDUs with L6-20 than 6-20 so you might need to get an adaptor or swap out the plug or outlet (it's pretty easy to swap out an outlet, assuming it was wired up correctly in the first place... turn off the breaker, unscrew it.. move the wires over...).
NotFuzzyWarm
Legendary
*
Offline Offline

Activity: 3626
Merit: 2520


Evil beware: We have waffles!


View Profile
August 05, 2020, 01:03:01 AM
Last edit: August 06, 2020, 12:42:25 PM by NotFuzzyWarm
 #9

Just saw the pic. You have a standard outlet box so easiest would be to replace the single NEMA 6-20 with a duplex version like this from McMaster The outlet cover for it is standard duplex, same as a normal 120v 15A outlet. Home Depot and such should also carry the outlet and cover. Yes it is a dual 20A 250v outlet but that rating is TOTAL amps for either a single cord or 20A split between 2 cords.

As always, current ratings should be de-rated to 80% for sustained loads like miners putting you at 16A total load and on par with what the miner pulls.

Query: Did the miner come with any cords? If so, what kind? That outlet ^ mates with either 6-15 or 6-20 plugs.

- For bitcoin to succeed the community must police itself -    My info useful? Donations welcome! 1FuzzyWc2J8TMqeUQZ8yjE43Rwr7K3cxs9
 -Sole remaining active developer of cgminer, Kano's repo is here
-Support Sidehacks miner development. Donations to:   1BURGERAXHH6Yi6LRybRJK7ybEm5m5HwTr
mikeywith
Legendary
*
Offline Offline

Activity: 2212
Merit: 6366


be constructive or S.T.F.U


View Profile
August 05, 2020, 07:07:19 PM
Last edit: August 06, 2020, 02:34:36 AM by frodocooper
 #10

Bitmain doesn't ship any power cords with their miners, unlike MicroBt, NFW, according to your experience how safe is it you use screw wire terminal/connectors?



These come with 30Amps ratings, I use them on 99% of my miners and never an issue, I find them a lot more robust than using the regular plug, he would need to take that socket out (while the MCB is disconnected) and then directly wire the power cord to the source wire, of course, this could be against the law/standards in his country, so he needs to confirm that, but here we can do anything because are cool  Cool "kidding".

█▀▀▀











█▄▄▄
▀▀▀▀▀▀▀▀▀▀▀
e
▄▄▄▄▄▄▄▄▄▄▄
█████████████
████████████▄███
██▐███████▄█████▀
█████████▄████▀
███▐████▄███▀
████▐██████▀
█████▀█████
███████████▄
████████████▄
██▄█████▀█████▄
▄█████████▀█████▀
███████████▀██▀
████▀█████████
▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀
c.h.
▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄
▀▀▀█











▄▄▄█
▄██████▄▄▄
█████████████▄▄
███████████████
███████████████
███████████████
███████████████
███░░█████████
███▌▐█████████
█████████████
███████████▀
██████████▀
████████▀
▀██▀▀
HagssFIN
Legendary
*
Offline Offline

Activity: 2436
Merit: 1706


Electrical engineer. Mining since 2014.


View Profile WWW
August 05, 2020, 07:48:17 PM
Last edit: August 06, 2020, 02:37:38 AM by frodocooper
Merited by NotFuzzyWarm (1), mikeywith (1)
 #11

Mikey, it is not recommendable in any way to do it like that. One of your miners start burning and you need to go to the distribution panel and find the right MCB to disconnect it? Hell no.

Thats against the code in many places, Finland at least. And a serious safety hazard.

You need a safety switch if you connect the power cord directly without an outlet: https://www.katko.com/products/enclosed-isolators/

mikeywith
Legendary
*
Offline Offline

Activity: 2212
Merit: 6366


be constructive or S.T.F.U


View Profile
August 05, 2020, 09:15:45 PM
Last edit: August 06, 2020, 02:38:53 AM by frodocooper
 #12

... it is not recommendable in any way to do it like that.

This has been my set-up for years and so far 0 problems, we did this even on a med-sized farm of 300KVA, but I sure won't recommend it if it's against the standards in someone else's coutry.

One of your miners start burning and you need to go to the distribution panel and find the right MCB to disconnect it? Hell no.

That makes sense, but many farms are not guarded 24/7, so there is always a chance that one miner will catch fire and it makes no difference if it's plugged this way or another, so I just have to make sure that no miner gets set on fire, also if something serious like this happens and I happen to be around I would simply disconnect the main breaker, the distance between the breaker and the socket "if there was any" is only a couple meters anyway.

Thats against the code in many places, Finland at least.

Ya, I figured that much out, that's why I asked, thanks for letting me know.

You need a safety switch if you connect the power cord directly without an outlet: https://www.katko.com/products/enclosed-isolators/

HagssFin, how does this differ from the regular main 3/4 pole breaker like this one? https://breakeroutlet.com/circuit-breakers/abb-s5h-sace-s5-400-a-circuit-breaker/

█▀▀▀











█▄▄▄
▀▀▀▀▀▀▀▀▀▀▀
e
▄▄▄▄▄▄▄▄▄▄▄
█████████████
████████████▄███
██▐███████▄█████▀
█████████▄████▀
███▐████▄███▀
████▐██████▀
█████▀█████
███████████▄
████████████▄
██▄█████▀█████▄
▄█████████▀█████▀
███████████▀██▀
████▀█████████
▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀
c.h.
▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄
▀▀▀█











▄▄▄█
▄██████▄▄▄
█████████████▄▄
███████████████
███████████████
███████████████
███████████████
███░░█████████
███▌▐█████████
█████████████
███████████▀
██████████▀
████████▀
▀██▀▀
NotFuzzyWarm
Legendary
*
Offline Offline

Activity: 3626
Merit: 2520


Evil beware: We have waffles!


View Profile
August 06, 2020, 12:55:22 AM
Last edit: August 12, 2020, 01:03:54 AM by NotFuzzyWarm
Merited by frodocooper (3), HagssFIN (1), mikeywith (1), Heisenberg_Hunter (1)
 #13

They differ in their design purpose. A MCB (Molded Case Breaker) is NOT designed to be used as a switch. They are purpose designed strictly for overload protection and to be used for occasionally manually interrupting power for maint/service operations.

btw: yes there are breakers designed to be installed into lighting power distribution/switching panels but they are purpose-designed for frequent switching and are identified & sold as such.

Power disconnect switches, fused or un-fused, are just that - power switches - and are designed for frequent usage as a main disconnect to switch power to equipment on & off. Also most will have provision for LOTO (Lock Out, Tag Out).

When it comes to 'on the fly' splitting of wires I love the WAGO 'Lever-Nuts" that Haggs mentioned a long while ago. They beat the hell outta the twist-on nuts I used to use and are available in 2,3,4,5 and I think 6 wires per block.

I would never use those nylon terminal strips for power distribution - too flimsy and too little material in them to hold up when things go bad. Think of what happens to nylon PCIe connectors when they get burnt - not pretty... Use real barrier strips or terminal blocks that will much better withstand overloads and poor connections.

- For bitcoin to succeed the community must police itself -    My info useful? Donations welcome! 1FuzzyWc2J8TMqeUQZ8yjE43Rwr7K3cxs9
 -Sole remaining active developer of cgminer, Kano's repo is here
-Support Sidehacks miner development. Donations to:   1BURGERAXHH6Yi6LRybRJK7ybEm5m5HwTr
DaveF
Legendary
*
Offline Offline

Activity: 3472
Merit: 6259


Crypto Swap Exchange


View Profile WWW
August 10, 2020, 01:00:16 AM
 #14

Because we has a tropical storm roll through here a few days ago and I have been doing cleanup work on replacing blown PCs and stuff since then.

If you have the $ you might want to invest in a UPS big enough to handle the miner. Not cheap but you might just save your miner, or your next miner, or the one after that.
Yeah, used with batts you are probably looking at close to $1k. But you can skip getting the PDU.

Not really affordable if you have a large farm, but for one circuit it you might want to think about it. Don't know where you are so if you don't have issues like coastal storms and the such it becomes less of an issue. If you are in coastal Florida you might want one.

-Dave

█▀▀▀











█▄▄▄
▀▀▀▀▀▀▀▀▀▀▀
e
▄▄▄▄▄▄▄▄▄▄▄
█████████████
████████████▄███
██▐███████▄█████▀
█████████▄████▀
███▐████▄███▀
████▐██████▀
█████▀█████
███████████▄
████████████▄
██▄█████▀█████▄
▄█████████▀█████▀
███████████▀██▀
████▀█████████
▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀
c.h.
▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄
▀▀▀█











▄▄▄█
▄██████▄▄▄
█████████████▄▄
███████████████
███████████████
███████████████
███████████████
███░░█████████
███▌▐█████████
█████████████
███████████▀
██████████▀
████████▀
▀██▀▀
philipma1957
Legendary
*
Offline Offline

Activity: 4116
Merit: 7824


'The right to privacy matters'


View Profile WWW
August 10, 2020, 01:34:34 AM
Last edit: August 11, 2020, 01:59:13 AM by frodocooper
 #15

I got a few high quality power conditioners that could work for him.

I will look for ebay link.

sold out on ebay I got mine for 200 they are great to run 1 s17 pro

this company wants to much  $$$
http://www.tynex.com/item.asp?PID=37538&CID=1236&menutype=P

these are great for 200 bucks. I grabbed 4 of them last year.  which is less then the guy wants for 1 .

let me look to see if I can find some.

https://smartpowersystems.com/wp-content/uploads/2020/04/AVRPlus-UG.pdf

they really run voltage tightly

https://smartpowersystems.com/automatic-voltage-regulators/

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.