January 15, 2018, 07:33:03 PM
 #21

Okay, so you  really don't know but you think you do. That's dangerous.

https://www.homedepot.com/p/Sheetrock-UltraLight-1-2-in-x-4-ft-x-8-ft-Gypsum-Board-14113411708/202530243

This is not fire rated sheet rock. It is for sale today at home depot. Generally, if it's 1/2" it's not fire rated, if it's 5/8" it is. That's because they add the fiber layer which is fire rated that is 1/8" thick.

CPUs burn more power as temperature rises. Not a little more power but a significant amount. Enough for me to pay for mechanical cooling systems and the power required to run them. Oh, don't forget, all the fans have to speed up. So the warmer the intake air is, the more air you must move over the heatsink to cool the processors. If you double fan speed, fan power is cubed. Check the affinity laws.
https://en.wikipedia.org/wiki/Affinity_laws


Very few enterprise class data centers are actually using outside air cooling but yes a few are. I have at least met every large enterprise class colo developer in the US. Even when Washington state tried to force everyone to use direct outside air cooling, I presented how my design was more energy efficient and therefore meets the spirit of the law. That design is currently being built. I have won that argument in Washington now 3 times, because I can show the proof.

I can also argue that all direct outside air cooling systems are vulnerable to attack. All someone has to do is shoot enough poison into the air intake to kill everyone inside. Even a smoke bomb will cause a clean agent dump and ventilation closures. That a solid $250k recovery problem.

How do you cool your data center if there's too much chaff in the air at harvest time? The filters will all clog really quickly. Then you are spending more money of filters than you would have spent on a standard cooling system. That even happened to a colleague in Dallas. I wouldn't have expected there'd be much harvest in Dallas, but then I read his data. They installed a giant system that is less cost efficient than a standard cooling system. Tragic.

PUE is a flawed method of measuring efficiency. I can improve the PUE of any data center by simply increasing the temperature. The rub is that I have proven that this method does not improve the efficiency of the data center, in fact it's slightly worse. You don't have believe me, it's what I get paid to do. Headlines are designed to grab attention, not to tell the whole truth.

Yes, I've been on the recovery effort after a colleague suffered thermal runaway on a large VRLA battery. I've spoken with a few other colleagues who had thermal runaway destruction on large Lithium-ion batteries. One actually destroyed their power room. I don't think that's the context you were using. I've had several cooling system failures, usually a control or power failure. The room will get hot. I've never had server failure because of it. My data center in Puerto Rico just survived the recent hurricane despite utility power failure for 6 weeks. Some of my competitors did fail, so I helped them get going again, as hopefully anyone would do in during a tragedy. Fair competition does not include kicking them when they're down.

Ironically, I use outside air to cool my miners. LOL. That's really because my miner rooms started really small. Now I'm looking to build larger rooms so I'm now more serious about the design, efficiency and cost. I am working through an analysis that looks promising. I think I can get the ROI reduced by 40% with my new design. I'm beginning small scale experiments now.






1714491472
Hero Member
*
Offline Offline

Posts: 1714491472

View Profile Personal Message (Offline)

Ignore
1714491472
Reply with quote  #2

1714491472
Report to moderator
1714491472
Hero Member
*
Offline Offline

Posts: 1714491472

View Profile Personal Message (Offline)

Ignore
1714491472
Reply with quote  #2

1714491472
Report to moderator
The forum was founded in 2009 by Satoshi and Sirius. It replaced a SourceForge forum.
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
1714491472
Hero Member
*
Offline Offline

Posts: 1714491472

View Profile Personal Message (Offline)

Ignore
1714491472
Reply with quote  #2

1714491472
Report to moderator
1714491472
Hero Member
*
Offline Offline

Posts: 1714491472

View Profile Personal Message (Offline)

Ignore
1714491472
Reply with quote  #2

1714491472
Report to moderator
QuintLeo
Legendary
*
Offline Offline

Activity: 1498
Merit: 1030


View Profile
January 15, 2018, 08:54:40 PM
 #22

Okay, so you  really don't know but you think you do. That's dangerous.

https://www.homedepot.com/p/Sheetrock-UltraLight-1-2-in-x-4-ft-x-8-ft-Gypsum-Board-14113411708/202530243

This is not fire rated sheet rock. It is for sale today at home depot. Generally, if it's 1/2" it's not fire rated, if it's 5/8" it is. That's because they add the fiber layer which is fire rated that is 1/8" thick.

CPUs burn more power as temperature rises. Not a little more power but a significant amount. Enough for me to pay for mechanical cooling systems and the power required to run them. Oh, don't forget, all the fans have to speed up. So the warmer the intake air is, the more air you must move over the heatsink to cool the processors. If you double fan speed, fan power is cubed. Check the affinity laws.
https://en.wikipedia.org/wiki/Affinity_laws


Very few enterprise class data centers are actually using outside air cooling but yes a few are. I have at least met every large enterprise class colo developer in the US. Even when Washington state tried to force everyone to use direct outside air cooling, I presented how my design was more energy efficient and therefore meets the spirit of the law. That design is currently being built. I have won that argument in Washington now 3 times, because I can show the proof.

I can also argue that all direct outside air cooling systems are vulnerable to attack. All someone has to do is shoot enough poison into the air intake to kill everyone inside. Even a smoke bomb will cause a clean agent dump and ventilation closures. That a solid $250k recovery problem.

How do you cool your data center if there's too much chaff in the air at harvest time? The filters will all clog really quickly. Then you are spending more money of filters than you would have spent on a standard cooling system. That even happened to a colleague in Dallas. I wouldn't have expected there'd be much harvest in Dallas, but then I read his data. They installed a giant system that is less cost efficient than a standard cooling system. Tragic.

PUE is a flawed method of measuring efficiency. I can improve the PUE of any data center by simply increasing the temperature. The rub is that I have proven that this method does not improve the efficiency of the data center, in fact it's slightly worse. You don't have believe me, it's what I get paid to do. Headlines are designed to grab attention, not to tell the whole truth.

Yes, I've been on the recovery effort after a colleague suffered thermal runaway on a large VRLA battery. I've spoken with a few other colleagues who had thermal runaway destruction on large Lithium-ion batteries. One actually destroyed their power room. I don't think that's the context you were using. I've had several cooling system failures, usually a control or power failure. The room will get hot. I've never had server failure because of it. My data center in Puerto Rico just survived the recent hurricane despite utility power failure for 6 weeks. Some of my competitors did fail, so I helped them get going again, as hopefully anyone would do in during a tragedy. Fair competition does not include kicking them when they're down.

Ironically, I use outside air to cool my miners. LOL. That's really because my miner rooms started really small. Now I'm looking to build larger rooms so I'm now more serious about the design, efficiency and cost. I am working through an analysis that looks promising. I think I can get the ROI reduced by 40% with my new design. I'm beginning small scale experiments now.


 That particular type of sheetrock is UNAVAILABLE in my area.
 Like I said, it might be a "local codes" type of thing that the only sheetrock I've ever seen was the fire-rated stuff.

 I wasn't talking thermal runaway on batteries (though that's actually MORE dangerous) but on semiconductor gear.

 I can't speak to chaff out of current experience - there isn't much of that around here and I'm upwind from the only close sources, and I didn't have it at all in my previous "in the edge of a city" location - but the SMOKE levels last year were bad.
 I was having to change the filters every week or two at MOST as a result - there are reasons I have always been a strong proponent of "positive pressure with filtered intake air".
 I'd have had to be doing that to some degree anyway even without the miners.
 Chaff shouldn't even be getting TO the filters themselves - there should be insect screening getting clogged by that stuff instead, just make a point of daily inspection during harvest season and cleanout as needed.
 You also pretty much have to be directly downwind and usually adjacent to a farm field that is being harvested for it to be a noticeable issue (based on when I was growing up in a place surrounded by farms), and that's normally going to be a week OR LESS out of the year.

 The "poison" argument is serious strawman.

 Fan power draw isn't the cube of fan speed, but it's not linear.
 Falls somewhere inbetween, based on the fan curves I've seen from manufacturers.
 Academic point though in the servers I've used as the case fans weren't set up for PWM at all and ran at 100% all the time anyway.
 I do grant they were "low end" server designs.

 As it happens, in the place I'm in right now, I CAN'T get enough "massive airflow" to do most of the cooling, except in mid-winter - the evap units I have are doing most of the work, and are certainly more efficient than any mechanical A/C unit ever dreamed of being to date.
 Don't believe the "change every 3 months" claims about the media - if you demineralize the water, they can easily go a year and I had one set still working fairly well after almost 2 years of near-continuous usage (I just replaced them last week in a unit I bought in May of 2016) even on aspen media.



I'm no longer legendary just in my own mind!
Like something I said? Donations gratefully accepted. LYLnTKvLefz9izJFUvEGQEZzSkz34b3N6U (Litecoin)
1GYbjMTPdCuV7dci3iCUiaRrcNuaiQrVYY (Bitcoin)
HoleShot
Member
**
Offline Offline

Activity: 70
Merit: 34


View Profile
January 15, 2018, 09:40:34 PM
 #23

Interesting points, thanks. I'm glad some places force fire resistant wall board.

Affinity laws are always true as in shows the relationship between flow, pressure and power. It is not exactly a cubed proportion with pump or fan speed depending performance at different speeds.  The heat removal requirement will follow the affinity laws. So the fan speed may need to more than double to accomplish the same heat removal when the delta T is halved. Regardless, half the delta T will result in the cube of the fan power required. All this is a bit tricky to calculate as the pressure may change as well. Each time I measured the cube function was within experimental error. I have also done whole office comparisons to demonstrate the point. I know it is contrary to common thoughts.

I hope to find the most economical way to run these miners. I'll let you know if/when I prove something.

Thanks for the spirited converstation



777miner
Newbie
*
Offline Offline

Activity: 4
Merit: 1


View Profile
January 21, 2018, 01:24:27 AM
 #24

I’m currently working on a project for this to accommodate up to 40 ASICs.  Looking at using two 2 Fujitsu models AOU45RLXFZ running mini splits providing T 90,000 BTU cooling.  Portable filtration. Industrial curtain for climate area.  Working out the zone distribution and total amps. I’m out of panel space. So I’m bringing my house up 320 amps nominal with capacity to 400 amp peak intermittent.  Cooling may require 2 240 volt outlets with 50 amps. That’s the plan...waiting to hear back on a couple bids. Then I can do some modeling on costs.  It’s been a week since the HVAC review and not heard back from contractors.  I’d really like to avoid this expense but my space can’t accommodate cooling with just mass flow.  Let me know if you want any updates.

Let me know how it goes - my electrician recommended 24,000 BTU for my set up in a 12x13 ft. room. For now I am going to put 2 800 CFU fans in the one window and leave my 2 other basement windows open. Keep me updated though, a split AC unit might work better - just not sure how much it would cost to run them.

The bid came in using two Daikin units rated at 50,000 BTU each 100,000 BTU total.  Two mini split units cooling an area that would be separated off with and insulated curtain.  Curtain also reduces about 17 dB.  That’s enough gear to maintain 40 ASIC’s at optimal temps, humidity, and air quality. All that a/c gear installed and curtain $25,600.  The power out lines will be two 240V circuits at 30 amps each.  It’s not as cost effective as mass-flow cooling.  In a suburban area I’m troubleshooting an enclosed area and have to mitigate noise and heat without large circulation fans.  I keep looking at the numbers versus rapid rise in complexity.  The front end cost on mini-splits and scaling over time...it’s a very difficult choice to build out with unknowns in valuations.  There are several tax breaks, credits, and rebates. I’m doing this under a specific LLC, which helps with cost structure.  If you want to discuss down to brass tacks, I’d be happy to.
DelTorro
Newbie
*
Offline Offline

Activity: 7
Merit: 0


View Profile
January 21, 2018, 01:53:31 AM
 #25

Just my two cents -- we run 24 S9s in our farm. It is very much about removing the heat as opposed to cooling the machines. Put your focus on venting heat out as opposed to trying to keep everything cold in a static room. It's much more cost effective. Not that you won't need cooling -- you may, but the main issue is heat removal.

Hope this helps in some way! Godspeed.
HoleShot
Member
**
Offline Offline

Activity: 70
Merit: 34


View Profile
January 21, 2018, 05:07:33 AM
 #26

100k BTU is not enough to keep 40 ASICs cool.

54kW heat, 29kW heat rejection.

777miner
Newbie
*
Offline Offline

Activity: 4
Merit: 1


View Profile
January 22, 2018, 01:19:06 AM
 #27

Just my two cents -- we run 24 S9s in our farm. It is very much about removing the heat as opposed to cooling the machines. Put your focus on venting heat out as opposed to trying to keep everything cold in a static room. It's much more cost effective. Not that you won't need cooling -- you may, but the main issue is heat removal.

Hope this helps in some way! Godspeed.

I have four MaxAir 10” axial fans I’ve configured for air cycling. Based on recommendations here, those can be reconfigured for exhaust heat extraction. (Vent to manifold, blown out thru foundation vent blocks). They currently are used for room air exchange, each draw about 4 watts.  These axials are only adequate with low seasonal temps.

Thank you all for sharing you expertise and awareness of pros/cons.
777miner
Newbie
*
Offline Offline

Activity: 4
Merit: 1


View Profile
January 23, 2018, 05:42:17 AM
 #28

100k BTU is not enough to keep 40 ASICs cool.

54kW heat, 29kW heat rejection.



I have to look up what you mean by, heat and heat rejection in determining adequate cooling.
Thank you for the reply.
HoleShot
Member
**
Offline Offline

Activity: 70
Merit: 34


View Profile
January 23, 2018, 01:31:27 PM
 #29

Heat is the amount of heat produced, also known as the load. It is equal to the amount of power consumed by the miners.


Heat Rejection means to reject the heat to the atmosphere. It's the capacity of the system. The system moves heat from indoors to outdoors.

12000 BTU = 1 Ton
1 Ton = 3.51kW

ruinous
Jr. Member
*
Offline Offline

Activity: 94
Merit: 3


View Profile
February 06, 2018, 05:24:50 PM
 #30

Find the cubic footage of the room. I have a small mine and am using a 300 CFM vent fan above the main mining area venting up through the attic to outside. Just don't forget about air flow into the room (opposite of side of room from fan). My mining room is 13x20x8. So calculate the cubic feet and get a vent fan with enough CFM or more to remove the air from the room in the amount of time you desire.
KevinCookeMMA (OP)
Jr. Member
*
Offline Offline

Activity: 48
Merit: 1


View Profile
February 13, 2018, 03:03:16 AM
 #31

Just an update - got 2 exhaust fans that pull 800 CFM each and put that small 400 CFM inline fan in the old dryer duct and they are cooling the space very well. The room is not closed off so exposed to whole basement. I have2 windows open for intake to balance the basement. It is still winter so works well - real test will be during summer. I would like to sell my 741's before then but the recent dip in prices is forcing me to hold onto the rigs for now. I expect it will have no problem cooling my 12 GPU rigs.
mikeywith
Legendary
*
Offline Offline

Activity: 2212
Merit: 6363


be constructive or S.T.F.U


View Profile
May 31, 2021, 11:07:52 PM
 #32

Damn, I'd never think that people can use AC units for their cooling farms. I have an old AC which is old but still works. It'd be pretty nice to sell it for mining purposes.

They do, in one of the small farms I have I still use an AC to help cool down the miners when the outside temperature is above 35c, but after doing this for many years, I got to the conclusion that you don't need an AC if you can move enough air, these miners will run just fine even at an ambient temperature of over 40c, we have 150 gears in one of the places that have 0 ACs in it, we run most of them at stock settings and a few days ago the outside temperature was as high as 40c and the miners were running pretty cool.

█▀▀▀











█▄▄▄
▀▀▀▀▀▀▀▀▀▀▀
e
▄▄▄▄▄▄▄▄▄▄▄
█████████████
████████████▄███
██▐███████▄█████▀
█████████▄████▀
███▐████▄███▀
████▐██████▀
█████▀█████
███████████▄
████████████▄
██▄█████▀█████▄
▄█████████▀█████▀
███████████▀██▀
████▀█████████
▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀
c.h.
▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄
▀▀▀█











▄▄▄█
▄██████▄▄▄
█████████████▄▄
███████████████
███████████████
███████████████
███████████████
███░░█████████
███▌▐█████████
█████████████
███████████▀
██████████▀
████████▀
▀██▀▀
DaveF
Legendary
*
Offline Offline

Activity: 3458
Merit: 6250


Crypto Swap Exchange


View Profile WWW
June 04, 2021, 12:47:24 AM
 #33

Damn, I'd never think that people can use AC units for their cooling farms. I have an old AC which is old but still works. It'd be pretty nice to sell it for mining purposes.

They do, in one of the small farms I have I still use an AC to help cool down the miners when the outside temperature is above 35c, but after doing this for many years, I got to the conclusion that you don't need an AC if you can move enough air, these miners will run just fine even at an ambient temperature of over 40c, we have 150 gears in one of the places that have 0 ACs in it, we run most of them at stock settings and a few days ago the outside temperature was as high as 40c and the miners were running pretty cool.

Even if you are moving enough air having something to drop the temperature a bit can help even more.

Years ago a HVAC person showed me some calculations for server rooms / data centers in general and there was a massive amount of math (that I did not understand at all  Grin)
It showed this many CFM of air movement at this temp could do this but dropping it by a degree and cutting the CFM could do that BUT moving more air at a slower speed (bigger fans but running slower) could do even more. Really interesting, but as I said didn't understand most of it beyond the basic theory. Came down to "Just make it cool and let me know how much it's going to cost me"

-Dave

█▀▀▀











█▄▄▄
▀▀▀▀▀▀▀▀▀▀▀
e
▄▄▄▄▄▄▄▄▄▄▄
█████████████
████████████▄███
██▐███████▄█████▀
█████████▄████▀
███▐████▄███▀
████▐██████▀
█████▀█████
███████████▄
████████████▄
██▄█████▀█████▄
▄█████████▀█████▀
███████████▀██▀
████▀█████████
▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀
c.h.
▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄
▀▀▀█











▄▄▄█
▄██████▄▄▄
█████████████▄▄
███████████████
███████████████
███████████████
███████████████
███░░█████████
███▌▐█████████
█████████████
███████████▀
██████████▀
████████▀
▀██▀▀
mikeywith
Legendary
*
Offline Offline

Activity: 2212
Merit: 6363


be constructive or S.T.F.U


View Profile
June 04, 2021, 01:58:50 AM
Merited by vapourminer (1)
 #34

Even if you are moving enough air having something to drop the temperature a bit can help even more.

Years ago a HVAC person showed me some calculations for server rooms / data centers in general and there was a massive amount of math (that I did not understand at all  Grin)
It showed this many CFM of air movement at this temp could do this but dropping it by a degree and cutting the CFM could do that BUT moving more air at a slower speed (bigger fans but running slower) could do even more. Really interesting, but as I said didn't understand most of it beyond the basic theory. Came down to "Just make it cool and let me know how much it's going to cost me"

-Dave

Of course, there is no argument about that, I believe everyone with common sense would agree to it, in fact, having enough ACs to cool down the hot air coming out from the miners, you will do just fine with no ventilation, but it all boils down to the most effienct way of doing it, cooling a server room is a completely different project.

My gears are located in one of the hottest cities on planet earth, they do just fine without ACs, which makes me positive that any other place would do just fine with enough fans, one important thing to note is pressure, our initial setup wasn't performing well enough because we were exhausting more air than we forced in, and you know that air will have to come in from somewhere, so this created negative pressure and the air was forced in from the exhaust side of the farm, we only noticed this after one of the exhaust fans died, it was spinning in the opposite direction (sucking air in), we also had miner fans failing at a high rate.

We ended up adding more intake fans to balance the pressure, the farm got A LOT cooler when the pressure issue was taken care of and so far, zero heat problem with absolutely ZERO ac units in that place.

One thing to keep in mind is that the power consumption and cost of a few large fans is a fraction of one large AC unit, also ACs require more regular maintenance/cleaning than fans do.

█▀▀▀











█▄▄▄
▀▀▀▀▀▀▀▀▀▀▀
e
▄▄▄▄▄▄▄▄▄▄▄
█████████████
████████████▄███
██▐███████▄█████▀
█████████▄████▀
███▐████▄███▀
████▐██████▀
█████▀█████
███████████▄
████████████▄
██▄█████▀█████▄
▄█████████▀█████▀
███████████▀██▀
████▀█████████
▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀
c.h.
▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄
▀▀▀█











▄▄▄█
▄██████▄▄▄
█████████████▄▄
███████████████
███████████████
███████████████
███████████████
███░░█████████
███▌▐█████████
█████████████
███████████▀
██████████▀
████████▀
▀██▀▀