Here's my setup:
- 22x24 wood stove heat exchanger
https://www.outdoorfurnacesupply.com/22x24-water-to-air-heat-exchanger-hot-water-coil-outdoor-wood-furnace.html- 40 LPM 1/24hp March pump (ignore the pump in the picture, it has been replaced with this)
https://burtprocess.com/march-0135-0037-0100-series-mdx-magnetic-drive-pump- CPVC hardware
-metal tank with two champers and flowplate
- Shell Diala s4 ZX-i dialectic fluid
I got a T17 40T for testing, and I can't say I'm happy with the temp readings. It's currently hashing at 36T dawing 1.9Kw.
Temperature readings are as follows:
- max chip: 85C
- PCB: 60C
- Fluid: 45C
- Ambient: 32C (89F)
My ambient in other rooms is no more than 24C (75F). Could the reason be the unshrouded fan? Because I can feel warm air coming out of the sides of the fan. I opened the window next to with to try to get the hot air out, but it always has been in the 30-32C range.
Setup picture here :
https://imgur.com/a/LFZIk8EMiner dahsboard:
https://imgur.com/a/Vb8eFLoI asked around and it seems people are complaining about T17s temp sensors being excessively high either air or immersed. Am I correct to assume an S19 would do better with this setup?