moe007 (OP)
Newbie
Offline
Activity: 11
Merit: 1
|
|
September 26, 2022, 02:22:12 AM |
|
ok here me out. im in the country with hydro pegged at 0.11$ perkwh(when i had it locked in) i was paying 2500$ per month on power with 130amp on my home single phase power. i noticed we some how have 3phase power at the road. im thinking of putting 600v in my shop to power tools anyways. so if i was to put a 400amp 600v feed in my shop then step down my voltage to 240v 3ph. and keep using 130amps of 240V would my amp draw (assuming no other loads) still be 2500$ per month or would the theoretical amp draw be less at my 600V side would lets way use use half the amps to make the 240V? if my math/guess lines up. ive seen 3ph 600v 80 amp breakers feed a step down transformer over 130 amp on 208v... what do you guys think. i was looking at doing a grid tie but our electrical grid will not let me tie more the 18k kwh per year... i used that in one month.
|
|
|
|
sidehack
Legendary
Offline
Activity: 3402
Merit: 1864
Curmudgeonly hardware guy
|
|
September 26, 2022, 01:34:30 PM |
|
Power is volts times amps. 130A 240V makes 31.2KW and at 208V that means 150 amps. From 600V it's 52 amps.
Any step-down transformer stage will lose a bit of power. If your 600V three-phase is significantly cheaper than your single phase (probably split phase 240?) you could probably come out ahead. When I ran a small DC, we switched into a "small industrial" rate schedule when we crossed 100KW draw on a 3-phase 400V feed and it dropped the average rate from 8.9c to 6.5c per KWh.
Since power is billed by KWh, raising your voltage to drop the current won't necessarily save on your bill. It'll depend on if they bill 600V 3ph at a lower rate than residential single phase.
|
|
|
|
moe007 (OP)
Newbie
Offline
Activity: 11
Merit: 1
|
Ah yes. Thanks for clearing the math up. I know that formula well. I used it lots... why I could not wrap my head around that answer is beyond me lol. Makes sense all the way thanks once more.
|
|
|
|
sidehack
Legendary
Offline
Activity: 3402
Merit: 1864
Curmudgeonly hardware guy
|
|
September 27, 2022, 01:21:49 AM |
|
NotFuzzyWarm and some others who know power could probably chip in with better specifics. My knowledge is largely academic.
|
|
|
|
NotFuzzyWarm
Legendary
Online
Activity: 3808
Merit: 2698
Evil beware: We have waffles!
|
|
September 27, 2022, 01:40:50 AM Last edit: September 27, 2022, 02:51:24 PM by NotFuzzyWarm |
|
NotFuzzyWarm and some others who know power could probably chip in with better specifics. My knowledge is largely academic.
No, you pretty much nailed it. The efficiency of any decent large power transformer ranges from at least 97% and for premium ones is over 99%. That leaves only the rate plan as a variable when it comes to incoming voltage & power. Oh, and of course the 1-time cost of the transformer if you have to pay for it If you are the one supplying the transformer this is certainly a case for spending more to get a premium high-efficiency one vs the cheapest you can get. Considering that all of the power will be going through it, when pulling say 100kva through it every 1% difference is 1kva saved or lost. Using a 30 day month that = 720kWh/month so that cost adds up fast.
|
|
|
|
moe007 (OP)
Newbie
Offline
Activity: 11
Merit: 1
|
|
September 27, 2022, 12:31:21 PM |
|
Great stuff! Ya 1% adds up what you put it that way.
|
|
|
|
philipma1957
Legendary
Online
Activity: 4298
Merit: 8793
'The right to privacy matters'
|
|
October 04, 2022, 01:43:07 AM |
|
Great stuff! Ya 1% adds up what you put it that way.
Note I gave you some merits for following up keep posting and you will leave 'newbie' status.
|
|
|
|
moe007 (OP)
Newbie
Offline
Activity: 11
Merit: 1
|
|
October 04, 2022, 04:49:41 AM |
|
Great stuff! Ya 1% adds up what you put it that way.
Note I gave you some merits for following up keep posting and you will leave 'newbie' status. Nice thanks. Do you guys think oil cool step-down would be worth it? I know the transformer on the pole did not like me when it boiled its oil at -30. Mindyou it was a 30 year old unit. But this new one humms just as bad when I put 140amps to het 247 lol
|
|
|
|
spectre71
Member
Offline
Activity: 360
Merit: 23
|
|
October 04, 2022, 02:12:56 PM |
|
Great stuff! Ya 1% adds up what you put it that way.
Note I gave you some merits for following up keep posting and you will leave 'newbie' status. Nice thanks. Do you guys think oil cool step-down would be worth it? I know the transformer on the pole did not like me when it boiled its oil at -30. Mindyou it was a 30 year old unit. But this new one humms just as bad when I put 140amps to het 247 lol Are you talking about the transformer off the feeder circuit? Air cooled high voltage transformers are not common. Low voltage like 600 to 230 are almost all air cooled. Humming is normal (cool fact, since the the cycle breaks zero twice the sound you hear is actually 120hz) if it makes a buzz thats laminated core coming apart.
|
|
|
|
NotFuzzyWarm
Legendary
Online
Activity: 3808
Merit: 2698
Evil beware: We have waffles!
|
|
October 04, 2022, 02:29:07 PM |
|
You normally only see oil cooled transformers on the Utility side of the power feed where the *possible* fire hazard remains outside of the building and the transformer has to be sealed against the elements as well as handling the multi-kv feed from the Utility. The user side of power distribution is almost exclusively air-cooled dry transformers. Ja they can buzz and definitely get rather hot but that is just the nature of the beasties,
|
|
|
|
moe007 (OP)
Newbie
Offline
Activity: 11
Merit: 1
|
|
October 04, 2022, 02:33:10 PM |
|
Ahh ya that makes sense! Let me tell you the oil on the pole was boilling pretty good haha. When I called the utility I said make sure the boys bring a transformer former the dispatcher said how do you know what's the transformer... Well the sizzling popping boiling sound inside the canisters telling me that's probably what's going on.
The buzzing makes sense. Same with the hum! Love those little hidden facts! I'm a refrigeration mechanic so I sit near Transformers all the time in mechanical rooms The things that go on beside you and you have no idea
|
|
|
|
spectre71
Member
Offline
Activity: 360
Merit: 23
|
|
October 04, 2022, 02:33:24 PM |
|
Power is volts times amps. 130A 240V makes 31.2KW and at 208V that means 150 amps. From 600V it's 52 amps.
Across one phase. Across three phase 130A at 240V 3phase 130 x 240 x 1.73 = 53,976 W
|
|
|
|
moe007 (OP)
Newbie
Offline
Activity: 11
Merit: 1
|
|
October 04, 2022, 02:39:54 PM |
|
Power is volts times amps. 130A 240V makes 31.2KW and at 208V that means 150 amps. From 600V it's 52 amps.
Across one phase. Across three phase 130A at 240V 3phase 130 x 240 x 1.73 = 53,976 W 54kw... I forgot about the 1.73 rule. That said it gives .73 more available draw on the third leg. But the idea is will the utility see 130amp draw or will they see the lesser draw of the 600v. In ontario residential and commercial rates are the same unless you use 1mw or 0.5mw.
|
|
|
|
spectre71
Member
Offline
Activity: 360
Merit: 23
|
|
October 04, 2022, 03:18:41 PM |
|
[/quote] 54kw... I forgot about the 1.73 rule. That said it gives .73 more available draw on the third leg. But the idea is will the utility see 130amp draw or will they see the lesser draw of the 600v. In ontario residential and commercial rates are the same unless you use 1mw or 0.5mw. [/quote]
Utility side would see the same (minuscule difference). Ideally you would have your load balanced across the phases.
Bringing in 600 and stepping it down economics depend on many factors. The transformer cost and 3ph 600v panels/load boards and breakers are considerably more expensive. But have a lower copper cost so long runs could be a factor. If your not getting a break on the kwh cost it may be better to bring it in at 230 and use commodity gear. You can also find 230v switchgear pretty cheap used / craigslist /ebay.
|
|
|
|
sidehack
Legendary
Offline
Activity: 3402
Merit: 1864
Curmudgeonly hardware guy
|
|
October 04, 2022, 05:05:16 PM |
|
Power is volts times amps. 130A 240V makes 31.2KW and at 208V that means 150 amps. From 600V it's 52 amps.
Across one phase. Across three phase 130A at 240V 3phase 130 x 240 x 1.73 = 53,976 W Okay but he specified 130A on 240V single phase, which means he was drawing 31.2KW total. Switching to 3ph, let's say it steps down to 208V l-l, the equipment will still be asking for 31.2KW which means 150 amps total, 50 amps per leg. At the 600V side the total draw is around 52 amps (plus transformer losses), around 17 amps per leg. The 1.73 rule doesn't make power magically appear, just changes how it gets there.
|
|
|
|
|