vapourminer
Legendary
*
Offline Offline

Activity: 4312
Merit: 3518


what is this "brake pedal" you speak of?


View Profile
August 27, 2023, 11:08:10 PM
Merited by mikeywith (4)
 #21

this just shows my ignorance but with that kind of airflow from the water curtain so close (a few feet looks like?) to the shelves the asics will live  on that there is no water mist that could get sucked in. but that box looks to be pretty well thought out so obviously it must work somehow.

when you say you might raise the box to above the level of the concrete/cinder block wall are you talking a few feet (looks to be 1/2 way up that door so 3-4 feet)?

1714498756
Hero Member
*
Offline Offline

Posts: 1714498756

View Profile Personal Message (Offline)

Ignore
1714498756
Reply with quote  #2

1714498756
Report to moderator
1714498756
Hero Member
*
Offline Offline

Posts: 1714498756

View Profile Personal Message (Offline)

Ignore
1714498756
Reply with quote  #2

1714498756
Report to moderator
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
1714498756
Hero Member
*
Offline Offline

Posts: 1714498756

View Profile Personal Message (Offline)

Ignore
1714498756
Reply with quote  #2

1714498756
Report to moderator
philipma1957 (OP)
Legendary
*
Offline Offline

Activity: 4102
Merit: 7817


'The right to privacy matters'


View Profile WWW
August 27, 2023, 11:19:22 PM
Merited by vapourminer (1)
 #22

this just shows my ignorance but with that kind of airflow from the water curtain so close (a few feet looks like?) to the shelves the asics will live  on that there is no water mist that could get sucked in. but that box looks to be pretty well thought out so obviously it must work somehow.

when you say you might raise the box to above the level of the concrete/cinder block wall are you talking a few feet (looks to be 1/2 way up that door so 3-4 feet)?



Yeah I think it is 42 inches.

As for the moisture question if it is an issue we will put a layer of material like weed screen on the inside of the box along the water media. I also suspect at the rate we fill the box and when we get it running.
Say Oct 15 2023 we may not need the water curtain till may.

The fans are beasts 10000 cfm each so 40000 cfm will be far more than we use now. Say 22000 cfm

this should be fun project. we will grow a lot of hash from now till june.

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
Nexus9090
Member
**
Offline Offline

Activity: 75
Merit: 44

Beam me up Scotty


View Profile
August 28, 2023, 02:11:45 PM
 #23

It is in the warehouse. It can do as many as 150 s19s or about 500kwatts

I will photo it soon.

Our goal is to relocate 150kwatts of miners  from the other spot

then add 75kwatts of miners.

hoping to add 25 s19 xp's or

20 s19 xp's and 5 L7 units.

This may be a silly question, but how can you afford 500KW of power with todays energy rates do you have your own solar farm and power station as well?

Its mind boggling!  Huh Grin

Donations greatfully received : 3MbtxahpbkC1fGhvcWR7Ja38u8cwN9wzY8
philipma1957 (OP)
Legendary
*
Offline Offline

Activity: 4102
Merit: 7817


'The right to privacy matters'


View Profile WWW
August 28, 2023, 02:56:14 PM
Merited by vapourminer (1)
 #24

It is in the warehouse. It can do as many as 150 s19s or about 500kwatts

I will photo it soon.

Our goal is to relocate 150kwatts of miners  from the other spot

then add 75kwatts of miners.

hoping to add 25 s19 xp's or

20 s19 xp's and 5 L7 units.

This may be a silly question, but how can you afford 500KW of power with todays energy rates do you have your own solar farm and power station as well?

Its mind boggling!  Huh Grin

our solar does 1.5 megawatts a day. that is about 20 s19s nonstop.

our on site transformer is 320kva that is about 90 s19s nonstop.

the 320kva transformer is the master limit. So even though the box can do 150 s19s and even though the solar can do 20 s19s our practical limit is 90 s19s

we are in talks with the power company to add a second 320 kva transformer to run in parrallel.

We have a longterm prepaid contract for power.
The warehouse owner had purchased 5 years of power for the icecream business he was renting freezers to.
the icecream place went out of business and he was stuck with a prepaid power contract and was not using the power. we stepped in dec 2018 and had 4 s9s. we now have quite a bit more than that.

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
Nexus9090
Member
**
Offline Offline

Activity: 75
Merit: 44

Beam me up Scotty


View Profile
August 28, 2023, 09:07:55 PM
 #25

our solar does 1.5 megawatts a day. that is about 20 s19s nonstop.

our on site transformer is 320kva that is about 90 s19s nonstop.

the 320kva transformer is the master limit. So even though the box can do 150 s19s and even though the solar can do 20 s19s our practical limit is 90 s19s

we are in talks with the power company to add a second 320 kva transformer to run in parrallel.

We have a longterm prepaid contract for power.
The warehouse owner had purchased 5 years of power for the icecream business he was renting freezers to.
the icecream place went out of business and he was stuck with a prepaid power contract and was not using the power. we stepped in dec 2018 and had 4 s9s. we now have quite a bit more than that.

Thanks for the info, nice deal. I can imagine industrial freezers chew up quite a bit of juice so exchanging it for a mining farm is a good one.

I'm a bit confused, you say your solar does 1.5MW for 20 S19 but grid supplied transformer 320KVA (~320KW PF1.0) is 90 S19's. Something's not quite right here.

Anyway, 500KW my head hurts just thinking about it, thats 1000 times more than my average home usage.

 Roll Eyes Grin

Donations greatfully received : 3MbtxahpbkC1fGhvcWR7Ja38u8cwN9wzY8
mikeywith
Legendary
*
Online Online

Activity: 2212
Merit: 6365


be constructive or S.T.F.U


View Profile
August 28, 2023, 11:38:54 PM
Merited by vapourminer (2)
 #26

I'm a bit confused, you say your solar does 1.5MW for 20 S19 but grid supplied transformer 320KVA (~320KW PF1.0) is 90 S19's. Something's not quite right here.

Ya i noticed that too, phill forgot to write the unit

instead of

Quote
our solar does 1.5 megawatts a day. that is about 20 s19s nonstop.

it should be

Quote
Quote
our solar does 1.5 Megawatt-day. that is about 20 s19s nonstop.


another more popular term to use would be megawatt-hours, so 1.5mw / 24 = 0.0625 or 62.5kw which is enough to run 20 S19s each does roughly 3kw.

However, the last representation of numbers would need to have the word "average" in it, since his solar arrays don't actually generate 62.5kw every hour, it's probably 4-5 hours that net him the 1500kw, so you can take a wild guess and assume his arrays do 300kw/h, if those are 200w panels, then you looking at 1500 of them, that's a whole lot of panels.


this just shows my ignorance but with that kind of airflow from the water curtain so close (a few feet looks like?) to the shelves the asics will live  on that there is no water mist that could get sucked in.

No water as in liquid form would be coming out from the other end of the evap cooler, it will be cooler air with more humidity, as long as the miner's temp remains above dew point condensing won't happen, running evap coolers in humid places could be somewhat risky and would cause damage to the miners in the long run, but if the humidity levels are moderate or low, there should be no issue at all.

One thing you need to be careful about would be having a faulty internet connection while using custom firmware like Vnish, The devs of those custom firmware wanted to outsmart Bitmain by saving energy during internet outages, so they keep the fan spinning but the miner doesn't generate any heat (unlike the stock firmware), now if you got those evap coolers throwing in air with high humidity, and your miners' fans spinning, the surrounding of the miner fan will go below dew point and then kaboom.

█▀▀▀











█▄▄▄
▀▀▀▀▀▀▀▀▀▀▀
e
▄▄▄▄▄▄▄▄▄▄▄
█████████████
████████████▄███
██▐███████▄█████▀
█████████▄████▀
███▐████▄███▀
████▐██████▀
█████▀█████
███████████▄
████████████▄
██▄█████▀█████▄
▄█████████▀█████▀
███████████▀██▀
████▀█████████
▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀
c.h.
▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄
▀▀▀█











▄▄▄█
▄██████▄▄▄
█████████████▄▄
███████████████
███████████████
███████████████
███████████████
███░░█████████
███▌▐█████████
█████████████
███████████▀
██████████▀
████████▀
▀██▀▀
philipma1957 (OP)
Legendary
*
Offline Offline

Activity: 4102
Merit: 7817


'The right to privacy matters'


View Profile WWW
August 29, 2023, 12:12:42 AM
 #27

yeah mikeywith has it right.

we backfeed to the grid 280-60= 220 .

so the 280kwatt does around 1500k-watt  in the summer maybe 1200k-watt in the winter.

so 60 k-watts is used 24/7/365 and the grid is the battery which stores the energy.

we have around 700 x 400 watt in panels. giving the 280kwatt peak number.

the main transformer is 320kva

so in the day we can do around 250kwatt  from the transformer and 60kwatt from the solar.

At night all power runs from transfomer so the max night run is about 270kwatt as no other use the transformer..

this complex is two or more acres and a few buildings.

a second mining room is across the street and does 50kwatts.

we will need a second transformer in parallel  say 320kva + 320kva

for now we are doing 160-190 kwatt in the solar/transformer grid setup

and 50kwatts min in the building on the other side of the street.

we will keep the small room with gpus a few whatsminers and l7s

the box room will gain 60 to 90 kwatts of gear. all in the box.

this will max us and we will order a new transformer to run in parrallel.


best case is

250/260 in the box

50 in room on other side of the street

all no later than oct 2023..



if that all that happens in summer of 2024 we would get the second outdoor tranformer.

giving us 500 kwatts in the box  and maybe 50-60 kwatts across the street.

all that is a maybe 🤔 but

the october numbers should be good.

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
Nexus9090
Member
**
Offline Offline

Activity: 75
Merit: 44

Beam me up Scotty


View Profile
August 29, 2023, 10:16:14 PM
 #28

Thanks for the explanations. After consideration I realised that MW/day was probably what was being discussed but thank you for confirming.

Mind blown! Thats one heck of a set-up, good luck with it.

I'll keep an eye on this thread to see the progress.

cheers.

G.






Donations greatfully received : 3MbtxahpbkC1fGhvcWR7Ja38u8cwN9wzY8
NotFuzzyWarm
Legendary
*
Online Online

Activity: 3612
Merit: 2509


Evil beware: We have waffles!


View Profile
August 29, 2023, 11:29:32 PM
Last edit: August 30, 2023, 12:22:07 PM by NotFuzzyWarm
 #29

Will be interesting see how the power company handles adding a 2nd xmfr. I can't see them just strapping 2 together in parallel and running a single set of much heavier lines coming out of the pair. Parallel feeds to them from the utility HV lines sure, bonded together as a single output - no.

No matter what the incoming service panel would of course have to be upgraded and it would/will probably be cheaper and certainly easier to just have a 2nd service panel to distribute incoming power from the 2nd xmfr. Of course you will need to monitor the 2 service loads to they stay within their power limits. As I recall you have some decent 3-phase power monitors in place for that  Wink

With the incoming lines from the transformers to service panels being independent of each other, balancing the load between them is not really an issue. Just 80% max out your existing transformer and add future loads to the new xmfr distribution panel or shift some loads around if desired.

- For bitcoin to succeed the community must police itself -    My info useful? Donations welcome! 1FuzzyWc2J8TMqeUQZ8yjE43Rwr7K3cxs9
 -Sole remaining active developer of cgminer, Kano's repo is here
-Support Sidehacks miner development. Donations to:   1BURGERAXHH6Yi6LRybRJK7ybEm5m5HwTr
philipma1957 (OP)
Legendary
*
Offline Offline

Activity: 4102
Merit: 7817


'The right to privacy matters'


View Profile WWW
August 29, 2023, 11:34:10 PM
 #30

Will be interesting see how the power company handles adding a 2nd xmfr. I can't see them just strapping 2 together in parallel and running a a single set of much heavier lines coming out of the pair. Parallel feeds to them from the utility HV lines sure, bonded together as a single output - no.

No matter what the incoming service panel would of course have to be upgraded and it would/will probably be cheaper and certainly easier to just have a 2nd service panel to distribute incoming power from the 2nd xmfr. Of course you will need to monitor the 2 service loads to they stay within their power limits. As I recall you have some decent 3-phase power monitors in place for that  Wink

With the incoming lines from the transformers to service panels being independent of each other, balancing the load between them is not really an issue. Just 80% max out your existing and add future loads to the new xmfr distribution panel or shift some loads around if desired.

yeah we are in talks with setting up a set of 4 Tesla superchargers.

This will take us over the 320kva transformer.

State of NJ will subsidy it.
Power company would like power sales for charging cars.

May or may not happen that is the if part.

But using what we have now to the max possible (the 320kva) is going to happen.

Which will be nice.

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
mikeywith
Legendary
*
Online Online

Activity: 2212
Merit: 6365


be constructive or S.T.F.U


View Profile
August 30, 2023, 01:26:26 AM
 #31

No matter what the incoming service panel would of course have to be upgraded and it would/will probably be cheaper and certainly easier to just have a 2nd service panel to distribute incoming power from the 2nd xmfr. Of course you will need to monitor the 2 service loads to they stay within their power limits. As I recall you have some decent 3-phase power monitors in place for that  Wink

I rather have a few smaller service panels than one huge panel, Our setup is 2 main 4-pole 1000A circuit breakers, each feeds 2*400 control panels (400A contactor attached to phase failure + voltage protection relays as well as SONOFF smart switch) and then each contactor feeds a 400A service panel which consists of 4*100A 3P MCBc (we run the netural directly from the busbar to the PDUs) each 100A supplies a 125A PDU so we have 4 PDUs for each 400A panel.

So despite having a total of 1600A on each phase, we don't have to deal with the complexity of heavy setup, just 4 small 400A service panels that we can control and shutdown individually, Keeping a perfect load balance between all of them isn't the easiest thing in the world, we were never able to keep them near even since some miners run at different clocks, some have dead hashboards, some would reboot some would not, but we were within 5-10% range most of the time.

█▀▀▀











█▄▄▄
▀▀▀▀▀▀▀▀▀▀▀
e
▄▄▄▄▄▄▄▄▄▄▄
█████████████
████████████▄███
██▐███████▄█████▀
█████████▄████▀
███▐████▄███▀
████▐██████▀
█████▀█████
███████████▄
████████████▄
██▄█████▀█████▄
▄█████████▀█████▀
███████████▀██▀
████▀█████████
▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀
c.h.
▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄
▀▀▀█











▄▄▄█
▄██████▄▄▄
█████████████▄▄
███████████████
███████████████
███████████████
███████████████
███░░█████████
███▌▐█████████
█████████████
███████████▀
██████████▀
████████▀
▀██▀▀
philipma1957 (OP)
Legendary
*
Offline Offline

Activity: 4102
Merit: 7817


'The right to privacy matters'


View Profile WWW
August 30, 2023, 02:15:21 AM
 #32

No matter what the incoming service panel would of course have to be upgraded and it would/will probably be cheaper and certainly easier to just have a 2nd service panel to distribute incoming power from the 2nd xmfr. Of course you will need to monitor the 2 service loads to they stay within their power limits. As I recall you have some decent 3-phase power monitors in place for that  Wink

I rather have a few smaller service panels than one huge panel, Our setup is 2 main 4-pole 1000A circuit breakers, each feeds 2*400 control panels (400A contactor attached to phase failure + voltage protection relays as well as SONOFF smart switch) and then each contactor feeds a 400A service panel which consists of 4*100A 3P MCBc (we run the netural directly from the busbar to the PDUs) each 100A supplies a 125A PDU so we have 4 PDUs for each 400A panel.

So despite having a total of 1600A on each phase, we don't have to deal with the complexity of heavy setup, just 4 small 400A service panels that we can control and shutdown individually, Keeping a perfect load balance between all of them isn't the easiest thing in the world, we were never able to keep them near even since some miners run at different clocks, some have dead hashboards, some would reboot some would not, but we were within 5-10% range most of the time.

In the current room we have
3x 220 amp panels giving a steady 225-235 volts.

they come from an 800 amp main panel doing 480 volts.  that feeds to a 160kva transformer. which feeds the  3x  220 amp panels at 225-235 volts.

we are looking to feed the box from the 800 amp 480 volt panel. and eventually shut the current room off.

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
philipma1957 (OP)
Legendary
*
Offline Offline

Activity: 4102
Merit: 7817


'The right to privacy matters'


View Profile WWW
September 07, 2023, 09:45:15 PM
 #33

box is now at a height where the venting clears the concrete foundation.



▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
Artemis3
Legendary
*
Offline Offline

Activity: 2016
Merit: 1563


CLEAN non GPL infringing code made in Rust lang


View Profile WWW
September 09, 2023, 05:27:07 PM
 #34

What is the usual ambient relative humidity there?

██████
███████
███████
████████
BRAIINS OS+|AUTOTUNING
MINING FIRMWARE
|
Increase hashrate on your Bitcoin ASICs,
improve efficiency as much as 25%, and
get 0% pool fees on Braiins Pool
philipma1957 (OP)
Legendary
*
Offline Offline

Activity: 4102
Merit: 7817


'The right to privacy matters'


View Profile WWW
September 12, 2023, 03:35:23 PM
 #35

What is the usual ambient relative humidity there?

okay the warehouse has a large garage door that opens to the outside.

So the humidity will match Clifton NJ humidity.

well under 45 percent most days.

But some summer days we go over 60 percent which means the water curtain will suffer a bit.
We rarely go over 70 percent humidity.

 which means the water curtain will work well over 300 close to 330 days a year.

This unit will move 40,000 cfm

and we do not have enough power to run over 75-80 s19s even though the unit claims to do 150 s19s or L7s

we have a 320 k-watt transformer to feed it which will allow us to do 250k-watts.

My gut tells me on a 95f day with high humidity we may need to down clock the gear just a little.  That means 5-15 days a year it could struggle


▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
philipma1957 (OP)
Legendary
*
Offline Offline

Activity: 4102
Merit: 7817


'The right to privacy matters'


View Profile WWW
October 13, 2023, 02:24:20 AM
 #36

videos of box getting closer to it working.

https://www.youtube.com/watch?v=S_3Svub_TP0

https://www.youtube.com/watch?v=LnjSK0gldUk



▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.