October 10, 2023, 07:30:01 PM
 #1

Hi,
I am new to mining, and am about to get towards the end of the month a new Antminer S19 95TH, so, as I have some time to prepare/plan, I was wondering if I could get some advice on how to set it up:
- I was told that I need a separate line of 220V, however I was thinking to get a step-up trafo from 110 to 220V having 5000W. Is this OK?
- I understood that the antminer comes w/o any power cables, so I have to get 2 power cables (similar like those for PCs) from what I could see on its picture, correct?
- what software do I need in order to have it mine properly?
- in order to configure it, is it possible to connect it to a monitor and a keyboard?
- I saw on a tutorial video that the miner needs 2 cables, so would I also need a UPS to plug those cables?
- as sometimes most of tutorial videos are pretty old regarding pools, and software used, is it possible to get a link towards a more recent video?
- do I need a cold wallet? I have right now 2 wallets on Crypto and Shakepay, however I understood that more securely would be a cold wallet, so which one would be a good one to use?
I am going to consult also this forum and see what I can find as information.
Thank you
TalkImg was created especially for hosting images on bitcointalk.org: try it next time you want to post an image
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
1715364038
Hero Member
*
Offline Offline

Posts: 1715364038

View Profile Personal Message (Offline)

Ignore
1715364038
Reply with quote  #2

1715364038
Report to moderator
1715364038
Hero Member
*
Offline Offline

Posts: 1715364038

View Profile Personal Message (Offline)

Ignore
1715364038
Reply with quote  #2

1715364038
Report to moderator
philipma1957
Legendary
*
Online Online

Activity: 4116
Merit: 7864


'The right to privacy matters'


View Profile WWW
October 10, 2023, 09:49:45 PM
 #2

Hi,
I am new to mining, and am about to get towards the end of the month a new Antminer S19 95TH, so, as I have some time to prepare/plan, I was wondering if I could get some advice on how to set it up:
- I was told that I need a separate line of 220V, however I was thinking to get a step-up trafo from 110 to 220V having 5000W. Is this OK?
- I understood that the antminer comes w/o any power cables, so I have to get 2 power cables (similar like those for PCs) from what I could see on its picture, correct?
- what software do I need in order to have it mine properly?
- in order to configure it, is it possible to connect it to a monitor and a keyboard?
- I saw on a tutorial video that the miner needs 2 cables, so would I also need a UPS to plug those cables?
- as sometimes most of tutorial videos are pretty old regarding pools, and software used, is it possible to get a link towards a more recent video?
- do I need a cold wallet? I have right now 2 wallets on Crypto and Shakepay, however I understood that more securely would be a cold wallet, so which one would be a good one to use?
I am going to consult also this forum and see what I can find as information.
Thank you

I assume you have a usa based home due to 120 volt power.

Transformers are hard on the wiring.

if you bump a 1 line 120volt  wire to 240 via a transformer then pull 5000 watts you will very likely melt it.

consult an electrician ask for a 220-240 volt line with a L6-30r receptacle

https://www.amazon.com/ELEGRP-Receptacle-Generator-Grounding-Industrial/dp/B08CXF9WDC/ref=asc_df_B08CXF9WDC?

it will need 10ga  wire and a 30 amp 2 pole circuit breaker.


like this https://www.amazon.com/Square-HomeLine-2-Pole-Circuit-Breaker/dp/B002YEJITO/ref=sr_1_4?


buy this cable
https://www.amazon.com/gp/product/B0C4YWYGS2/ref=ox_sc_act_title_1?


and this cable

https://www.amazon.com/IEC-C20-C13-Splitter-Cord/dp/B07J6S348C/ref=sr_1_5?


so

1) 30 amp 2 pole in your circuit box
2) l6-30r receptacle on the wall wire with 10 gauge wire
3) l6-30p to c19 10 gauge 10 foot cable
4) c20 to c13 that I listed.

Should be safe up to 4000 watts or easy peasy 1 s19

lastly do you have hard wired internet with eth cables?

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
mikeywith
Legendary
*
Offline Offline

Activity: 2226
Merit: 6375


be constructive or S.T.F.U


View Profile
October 11, 2023, 12:16:21 AM
 #3

I was told that I need a separate line of 220V, however I was thinking to get a step-up trafo from 110 to 220V having 5000W. Is this OK?

You could, but I would advice against it, there would some energy loss in this process, better to install 220v.

Quote
- I understood that the antminer comes w/o any power cables, so I have to get 2 power cables (similar like those for PCs) from what I could see on its picture, correct?

It's called C13, ya it's the same plug as the one you use on your PC, but sure thing is, it isn't the same rating, you are going to need each wire to be at least 1.5mm square thick.

Quote
- what software do I need in order to have it mine properly?

Nothing, just your Chrome browser or whatever you already use.

Quote
- in order to configure it, is it possible to connect it to a monitor and a keyboard?

No, you use your laptop / PC, write the miner IP address on the browser, and you will be inside the miner to do the pool configuration.
 
Quote
- I saw on a tutorial video that the miner needs 2 cables, so would I also need a UPS to plug those cables?

You mean PDU? you can, or you can just get the Y split cable that phill posted above, the only issue with that Y spilt is that your breaker/socket need to handle the entire amp draw whereby using 2 single cables the load is divided.

Quote
- as sometimes most of tutorial videos are pretty old regarding pools, and software used, is it possible to get a link towards a more recent video?

Nothing has changed ever since, all you need is pool URL and a worker name.

Quote
- do I need a cold wallet? I have right now 2 wallets on Crypto and Shakepay, however I understood that more securely would be a cold wallet, so which one would be a good one to use?

Your mining payouts will be sent to whatever address to enter in the pool website, they don't know/care what address is that, which wallet to use is off-topic and should be taken to Wallets sections



█▀▀▀











█▄▄▄
▀▀▀▀▀▀▀▀▀▀▀
e
▄▄▄▄▄▄▄▄▄▄▄
█████████████
████████████▄███
██▐███████▄█████▀
█████████▄████▀
███▐████▄███▀
████▐██████▀
█████▀█████
███████████▄
████████████▄
██▄█████▀█████▄
▄█████████▀█████▀
███████████▀██▀
████▀█████████
▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀
c.h.
▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄
▀▀▀█











▄▄▄█
▄██████▄▄▄
█████████████▄▄
███████████████
███████████████
███████████████
███████████████
███░░█████████
███▌▐█████████
█████████████
███████████▀
██████████▀
████████▀
▀██▀▀
flyboynyc
Newbie
*
Offline Offline

Activity: 19
Merit: 0


View Profile
October 11, 2023, 06:42:02 AM
 #4


Hey,

i am doing a similar setup as yours. Were you successful with the transformer?
philipma1957
Legendary
*
Online Online

Activity: 4116
Merit: 7864


'The right to privacy matters'


View Profile WWW
October 12, 2023, 12:46:48 AM
 #5


Hey,

i am doing a similar setup as yours. Were you successful with the transformer?

If he uses a 5000 watt 120 to 240 boost transformer such as this one


https://www.amazon.com/Yinleader-Voltage-Converter-Transformer-VTUS-5000/dp/B09LQXP8R2/ref=sxin_16_pa_sp_search_thematic_sspa?

it will not work well

try and find a 50amp single pole circuit breaker.

and it needs more than  10 gauge wire it needs 8 gauge and there would be a proper plug to carry that much current.

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
boggym777 (OP)
Jr. Member
*
Offline Offline

Activity: 56
Merit: 14


View Profile
October 12, 2023, 07:28:40 PM
 #6

Hi,
I am new to mining, and am about to get towards the end of the month a new Antminer S19 95TH, so, as I have some time to prepare/plan, I was wondering if I could get some advice on how to set it up:
- I was told that I need a separate line of 220V, however I was thinking to get a step-up trafo from 110 to 220V having 5000W. Is this OK?
- I understood that the antminer comes w/o any power cables, so I have to get 2 power cables (similar like those for PCs) from what I could see on its picture, correct?
- what software do I need in order to have it mine properly?
- in order to configure it, is it possible to connect it to a monitor and a keyboard?
- I saw on a tutorial video that the miner needs 2 cables, so would I also need a UPS to plug those cables?
- as sometimes most of tutorial videos are pretty old regarding pools, and software used, is it possible to get a link towards a more recent video?
- do I need a cold wallet? I have right now 2 wallets on Crypto and Shakepay, however I understood that more securely would be a cold wallet, so which one would be a good one to use?
I am going to consult also this forum and see what I can find as information.
Thank you

I assume you have a usa based home due to 120 volt power.

Transformers are hard on the wiring.

if you bump a 1 line 120volt  wire to 240 via a transformer then pull 5000 watts you will very likely melt it.

consult an electrician ask for a 220-240 volt line with a L6-30r receptacle

https://www.amazon.com/ELEGRP-Receptacle-Generator-Grounding-Industrial/dp/B08CXF9WDC/ref=asc_df_B08CXF9WDC?

it will need 10ga  wire and a 30 amp 2 pole circuit breaker.


like this https://www.amazon.com/Square-HomeLine-2-Pole-Circuit-Breaker/dp/B002YEJITO/ref=sr_1_4?


buy this cable
https://www.amazon.com/gp/product/B0C4YWYGS2/ref=ox_sc_act_title_1?


and this cable

https://www.amazon.com/IEC-C20-C13-Splitter-Cord/dp/B07J6S348C/ref=sr_1_5?


so

1) 30 amp 2 pole in your circuit box
2) l6-30r receptacle on the wall wire with 10 gauge wire
3) l6-30p to c19 10 gauge 10 foot cable
4) c20 to c13 that I listed.

Should be safe up to 4000 watts or easy peasy 1 s19

lastly do you have hard wired internet with eth cables?

Hi philipma1957,

Thank you very much for the useful information.
I checked again my situation in the basement, and found an outlet for 240V that was intended for an electric dryer, however because my actual dryer is on gas, this outlet remained unused.
The circuit is already on the electric panel and has a breaker, like for a dryer. Would this be enough?
Also I was thinking to use a plug for that outlet with a cable of about 6m that I will pull to a double outlet that I would mount on a wall. What do you think?
I think I will do this with an electrician to do all that cabling.
I have internet 1000Mbps in the house, so I would need a cat7 cable from the router (2nd floor) to the basement, to plug it into the Antminer, right?

Thank you again
philipma1957
Legendary
*
Online Online

Activity: 4116
Merit: 7864


'The right to privacy matters'


View Profile WWW
October 12, 2023, 07:47:52 PM
 #7

Hi,
I am new to mining, and am about to get towards the end of the month a new Antminer S19 95TH, so, as I have some time to prepare/plan, I was wondering if I could get some advice on how to set it up:
- I was told that I need a separate line of 220V, however I was thinking to get a step-up trafo from 110 to 220V having 5000W. Is this OK?
- I understood that the antminer comes w/o any power cables, so I have to get 2 power cables (similar like those for PCs) from what I could see on its picture, correct?
- what software do I need in order to have it mine properly?
- in order to configure it, is it possible to connect it to a monitor and a keyboard?
- I saw on a tutorial video that the miner needs 2 cables, so would I also need a UPS to plug those cables?
- as sometimes most of tutorial videos are pretty old regarding pools, and software used, is it possible to get a link towards a more recent video?
- do I need a cold wallet? I have right now 2 wallets on Crypto and Shakepay, however I understood that more securely would be a cold wallet, so which one would be a good one to use?
I am going to consult also this forum and see what I can find as information.
Thank you

I assume you have a usa based home due to 120 volt power.

Transformers are hard on the wiring.

if you bump a 1 line 120volt  wire to 240 via a transformer then pull 5000 watts you will very likely melt it.

consult an electrician ask for a 220-240 volt line with a L6-30r receptacle

https://www.amazon.com/ELEGRP-Receptacle-Generator-Grounding-Industrial/dp/B08CXF9WDC/ref=asc_df_B08CXF9WDC?

it will need 10ga  wire and a 30 amp 2 pole circuit breaker.


like this https://www.amazon.com/Square-HomeLine-2-Pole-Circuit-Breaker/dp/B002YEJITO/ref=sr_1_4?


buy this cable
https://www.amazon.com/gp/product/B0C4YWYGS2/ref=ox_sc_act_title_1?


and this cable

https://www.amazon.com/IEC-C20-C13-Splitter-Cord/dp/B07J6S348C/ref=sr_1_5?


so

1) 30 amp 2 pole in your circuit box
2) l6-30r receptacle on the wall wire with 10 gauge wire
3) l6-30p to c19 10 gauge 10 foot cable
4) c20 to c13 that I listed.

Should be safe up to 4000 watts or easy peasy 1 s19

lastly do you have hard wired internet with eth cables?

Hi philipma1957,

Thank you very much for the useful information.
I checked again my situation in the basement, and found an outlet for 240V that was intended for an electric dryer, however because my actual dryer is on gas, this outlet remained unused.
The circuit is already on the electric panel and has a breaker, like for a dryer. Would this be enough?
Also I was thinking to use a plug for that outlet with a cable of about 6m that I will pull to a double outlet that I would mount on a wall. What do you think?
I think I will do this with an electrician to do all that cabling.
I have internet 1000Mbps in the house, so I would need a cat7 cable from the router (2nd floor) to the basement, to plug it into the Antminer, right?

Thank you again

most likely the plug will work as electric dryer 240volt lines draw a lot of power

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
NotFuzzyWarm
Legendary
*
Offline Offline

Activity: 3626
Merit: 2542


Evil beware: We have waffles!


View Profile
October 12, 2023, 07:53:24 PM
 #8

Quote
so I would need a cat7 cable from the router (2nd floor) to the basement, to plug it into the Antminer, right?
CAT-5 or 6 will be fine as miners actually use very little bandwidth and are happy even with a 10mbit connection. It is not until you start connecting to several miners that connection speed between the router & miners becomes a concern.

- For bitcoin to succeed the community must police itself -    My info useful? Donations welcome! 1FuzzyWc2J8TMqeUQZ8yjE43Rwr7K3cxs9
 -Sole remaining active developer of cgminer, Kano's repo is here
-Support Sidehacks miner development. Donations to:   1BURGERAXHH6Yi6LRybRJK7ybEm5m5HwTr
boggym777 (OP)
Jr. Member
*
Offline Offline

Activity: 56
Merit: 14


View Profile
October 12, 2023, 08:06:47 PM
Merited by philipma1957 (2)
 #9

Hi,
I am new to mining, and am about to get towards the end of the month a new Antminer S19 95TH, so, as I have some time to prepare/plan, I was wondering if I could get some advice on how to set it up:
- I was told that I need a separate line of 220V, however I was thinking to get a step-up trafo from 110 to 220V having 5000W. Is this OK?
- I understood that the antminer comes w/o any power cables, so I have to get 2 power cables (similar like those for PCs) from what I could see on its picture, correct?
- what software do I need in order to have it mine properly?
- in order to configure it, is it possible to connect it to a monitor and a keyboard?
- I saw on a tutorial video that the miner needs 2 cables, so would I also need a UPS to plug those cables?
- as sometimes most of tutorial videos are pretty old regarding pools, and software used, is it possible to get a link towards a more recent video?
- do I need a cold wallet? I have right now 2 wallets on Crypto and Shakepay, however I understood that more securely would be a cold wallet, so which one would be a good one to use?
I am going to consult also this forum and see what I can find as information.
Thank you

I assume you have a usa based home due to 120 volt power.

Transformers are hard on the wiring.

if you bump a 1 line 120volt  wire to 240 via a transformer then pull 5000 watts you will very likely melt it.

consult an electrician ask for a 220-240 volt line with a L6-30r receptacle

https://www.amazon.com/ELEGRP-Receptacle-Generator-Grounding-Industrial/dp/B08CXF9WDC/ref=asc_df_B08CXF9WDC?

it will need 10ga  wire and a 30 amp 2 pole circuit breaker.


like this https://www.amazon.com/Square-HomeLine-2-Pole-Circuit-Breaker/dp/B002YEJITO/ref=sr_1_4?


buy this cable
https://www.amazon.com/gp/product/B0C4YWYGS2/ref=ox_sc_act_title_1?


and this cable

https://www.amazon.com/IEC-C20-C13-Splitter-Cord/dp/B07J6S348C/ref=sr_1_5?


so

1) 30 amp 2 pole in your circuit box
2) l6-30r receptacle on the wall wire with 10 gauge wire
3) l6-30p to c19 10 gauge 10 foot cable
4) c20 to c13 that I listed.

Should be safe up to 4000 watts or easy peasy 1 s19

lastly do you have hard wired internet with eth cables?

Hi philipma1957,

Thank you very much for the useful information.
I checked again my situation in the basement, and found an outlet for 240V that was intended for an electric dryer, however because my actual dryer is on gas, this outlet remained unused.
The circuit is already on the electric panel and has a breaker, like for a dryer. Would this be enough?
Also I was thinking to use a plug for that outlet with a cable of about 6m that I will pull to a double outlet that I would mount on a wall. What do you think?
I think I will do this with an electrician to do all that cabling.
I have internet 1000Mbps in the house, so I would need a cat7 cable from the router (2nd floor) to the basement, to plug it into the Antminer, right?

Thank you again

most likely the plug will work as electric dryer 240volt lines draw a lot of power
Yeah, I would think that that outlet should be OK because as you said the electric dryer would draw a lot of power.
So you think that line should be OK?
Also, I would instead of the plug you suggested https://www.amazon.com/ELEGRP-Receptacle-Generator-Grounding-Industrial/dp/B08CXF9WDC/ref=asc_df_B08CXF9WDC? to use a plug fitting that outlet, right? The outlet is already there, so I was thinking that I should as well use it, no?
Thank you
philipma1957
Legendary
*
Online Online

Activity: 4116
Merit: 7864


'The right to privacy matters'


View Profile WWW
October 12, 2023, 08:39:09 PM
 #10



you can keep the receptacle you will just need the plug that fits it.

https://www.amazon.com/gp/product/B09WQVGNNR/ref=ox_sc_act_title_1?

works with some dryer receptacles


and it would work with


 this cable
https://www.amazon.com/gp/product/B0C4YWYGS2/ref=ox_sc_act_title_1?


and this cable
https://www.amazon.com/IEC-C20-C13-Splitter-Cord/dp/B07J6S348C/ref=sr_1_5?

so wall outlet =1)

adatper I just linked =2)

l6 -30p to c19 cable =3)

c20 to spliter c13 = 4)

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
boggym777 (OP)
Jr. Member
*
Offline Offline

Activity: 56
Merit: 14


View Profile
October 13, 2023, 01:05:54 PM
 #11


Hey,

i am doing a similar setup as yours. Were you successful with the transformer?
Hi,
I actually quit the trafo solution as, from what I understood, it would get very hot, and become a fire hazard.
I got this information from several sources, so I opted in the end for the 220V line.
Have a great day
boggym777 (OP)
Jr. Member
*
Offline Offline

Activity: 56
Merit: 14


View Profile
October 13, 2023, 04:07:56 PM
 #12



you can keep the receptacle you will just need the plug that fits it.

https://www.amazon.com/gp/product/B09WQVGNNR/ref=ox_sc_act_title_1?

works with some dryer receptacles


and it would work with


 this cable
https://www.amazon.com/gp/product/B0C4YWYGS2/ref=ox_sc_act_title_1?


and this cable
https://www.amazon.com/IEC-C20-C13-Splitter-Cord/dp/B07J6S348C/ref=sr_1_5?

so wall outlet =1)

adatper I just linked =2)

l6 -30p to c19 cable =3)

c20 to spliter c13 = 4)

Thank you very much for your response philipma1957,
I already ordered the cables, and the outlet that you previously suggested, so I will see if I can find an electrician who would replace the existing outlet with the one you first suggested.
That adapter that you suggested  https://www.amazon.com/gp/product/B09WQVGNNR/ref=ox_sc_act_title_1? would be interesting because then I would not need any electrician to help me with the work.
I will think about those two solutions. I need only to send back the outlet and order the adapter.
Have a great day
philipma1957
Legendary
*
Online Online

Activity: 4116
Merit: 7864


'The right to privacy matters'


View Profile WWW
October 13, 2023, 05:13:24 PM
 #13



you can keep the receptacle you will just need the plug that fits it.

https://www.amazon.com/gp/product/B09WQVGNNR/ref=ox_sc_act_title_1?

works with some dryer receptacles


and it would work with


 this cable
https://www.amazon.com/gp/product/B0C4YWYGS2/ref=ox_sc_act_title_1?


and this cable
https://www.amazon.com/IEC-C20-C13-Splitter-Cord/dp/B07J6S348C/ref=sr_1_5?

so wall outlet =1)

adatper I just linked =2)

l6 -30p to c19 cable =3)

c20 to spliter c13 = 4)

Thank you very much for your response philipma1957,
I already ordered the cables, and the outlet that you previously suggested, so I will see if I can find an electrician who would replace the existing outlet with the one you first suggested.
That adapter that you suggested  https://www.amazon.com/gp/product/B09WQVGNNR/ref=ox_sc_act_title_1? would be interesting because then I would not need any electrician to help me with the work.
I will think about those two solutions. I need only to send back the outlet and order the adapter.
Have a great day

Either way should work.  let us know how it works out for you.

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
boggym777 (OP)
Jr. Member
*
Offline Offline

Activity: 56
Merit: 14


View Profile
October 15, 2023, 01:42:05 PM
 #14



you can keep the receptacle you will just need the plug that fits it.

https://www.amazon.com/gp/product/B09WQVGNNR/ref=ox_sc_act_title_1?

works with some dryer receptacles


and it would work with


 this cable
https://www.amazon.com/gp/product/B0C4YWYGS2/ref=ox_sc_act_title_1?


and this cable
https://www.amazon.com/IEC-C20-C13-Splitter-Cord/dp/B07J6S348C/ref=sr_1_5?

so wall outlet =1)

adatper I just linked =2)

l6 -30p to c19 cable =3)

c20 to spliter c13 = 4)

Thank you very much for your response philipma1957,
I already ordered the cables, and the outlet that you previously suggested, so I will see if I can find an electrician who would replace the existing outlet with the one you first suggested.
That adapter that you suggested  https://www.amazon.com/gp/product/B09WQVGNNR/ref=ox_sc_act_title_1? would be interesting because then I would not need any electrician to help me with the work.
I will think about those two solutions. I need only to send back the outlet and order the adapter.
Have a great day

Either way should work.  let us know how it works out for you.
Hi,
I would have one other question.
The adapter you sent me the link of has 3 prongs, and my outlet has 4. Does it matter if I use all 4 prongs, or just 3?
For instance this one has 4 prongs:
https://www.amazon.ca/gp/product/B07P7YK39G?ref=ppx_pt2_dt_b_prod_image&th=1
Thank you
so98nn
Hero Member
*****
Offline Offline

Activity: 2086
Merit: 603


View Profile
October 16, 2023, 01:28:41 PM
 #15


Hey,

i am doing a similar setup as yours. Were you successful with the transformer?
[snip]
try and find a 50amp single pole circuit breaker.

and it needs more than  10 gauge wire it needs 8 gauge and there would be a proper plug to carry that much current.

If OP and others are going to be serious about their mining set on the scale of what @philipma1957 does then better follow their threads. I have been a secret follower of their threads and seen all the types of experiences that they have shared. Whether it is setting up a new miner, bringing in a new mining rack that can hold a big set up, or may be cooling down the entire mining farm, they have always seen putting their actual pictures and explaining what is happening at their facility.

I think that is the best way to go with it. You also share your experience and we can visualize the entire project with pictures. Please start checking out what they have done in the past. Moreover, there are detailed set up threads for dummies where one can get every bit of knowledge on how to proceed.
boggym777 (OP)
Jr. Member
*
Offline Offline

Activity: 56
Merit: 14


View Profile
October 16, 2023, 03:46:19 PM
 #16



you can keep the receptacle you will just need the plug that fits it.

https://www.amazon.com/gp/product/B09WQVGNNR/ref=ox_sc_act_title_1?

works with some dryer receptacles


and it would work with


 this cable
https://www.amazon.com/gp/product/B0C4YWYGS2/ref=ox_sc_act_title_1?


and this cable
https://www.amazon.com/IEC-C20-C13-Splitter-Cord/dp/B07J6S348C/ref=sr_1_5?

so wall outlet =1)

adatper I just linked =2)

l6 -30p to c19 cable =3)

c20 to spliter c13 = 4)

Thank you very much for your response philipma1957,
I already ordered the cables, and the outlet that you previously suggested, so I will see if I can find an electrician who would replace the existing outlet with the one you first suggested.
That adapter that you suggested  https://www.amazon.com/gp/product/B09WQVGNNR/ref=ox_sc_act_title_1? would be interesting because then I would not need any electrician to help me with the work.
I will think about those two solutions. I need only to send back the outlet and order the adapter.
Have a great day

Either way should work.  let us know how it works out for you.
Thank you very much philipma1957
boggym777 (OP)
Jr. Member
*
Offline Offline

Activity: 56
Merit: 14


View Profile
October 19, 2023, 01:05:29 PM
Last edit: October 19, 2023, 06:38:38 PM by boggym777
 #17

Hi,
I forgot to ask. How much bandwidth does my antminer S19 need? I found online that it would need 5Mbps, however I did not find something specifically related to my Antminer S19, OK?
I want to figure out if I should pull a network cable from the router (2nd floor) to the antminer (basement), or should I use 2 power outlet adapters?
Thank you
seek3r
Legendary
*
Offline Offline

Activity: 1260
Merit: 1954



View Profile
October 19, 2023, 08:05:06 PM
 #18

Hi,
I forgot to ask. How much bandwidth does my antminer S19 need? I found online that it would need 5Mbps, however I did not find something specifically related to my Antminer S19, OK?
There is a simple formula which is provided by Bitmain support:
Code:
Network bandwidth (Mbps) = number of servers (sets)/150.
Source: https://support.bitmain.com/hc/en-us/articles/5291909784601-Network-Bandwidth-and-Load#:~:text=The%20formula%20for%20calculating%20the,of%20servers%20(sets)%2F150.

Since you are using one unit the required bandwidth is less than 1Mbps. Smiley

I want to figure out if I should pull a network cable from the router (2nd floor) to the antminer (basement), or should I use 2 power outlet adapters?
Thank you
Regarding ur network setup, its always recommened to use a direct cable connection fore a more reliable and steady connection.
But I know myself that this is not always possible. Therefore, u can also choose the variant with the 2 power outlet adapters, if a direct wired connection is not possible.

.
.HUGE.
▄██████████▄▄
▄█████████████████▄
▄█████████████████████▄
▄███████████████████████▄
▄█████████████████████████▄
███████▌██▌▐██▐██▐████▄███
████▐██▐████▌██▌██▌██▌██
█████▀███▀███▀▐██▐██▐█████

▀█████████████████████████▀

▀███████████████████████▀

▀█████████████████████▀

▀█████████████████▀

▀██████████▀▀
█▀▀▀▀











█▄▄▄▄
▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀
.
CASINSPORTSBOOK
▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄▄
▀▀▀▀█











▄▄▄▄█
boggym777 (OP)
Jr. Member
*
Offline Offline

Activity: 56
Merit: 14


View Profile
October 20, 2023, 12:38:04 PM
 #19

Hi,
I forgot to ask. How much bandwidth does my antminer S19 need? I found online that it would need 5Mbps, however I did not find something specifically related to my Antminer S19, OK?
There is a simple formula which is provided by Bitmain support:
Code:
Network bandwidth (Mbps) = number of servers (sets)/150.
Source: https://support.bitmain.com/hc/en-us/articles/5291909784601-Network-Bandwidth-and-Load#:~:text=The%20formula%20for%20calculating%20the,of%20servers%20(sets)%2F150.

Since you are using one unit the required bandwidth is less than 1Mbps. Smiley

I want to figure out if I should pull a network cable from the router (2nd floor) to the antminer (basement), or should I use 2 power outlet adapters?
Thank you
Regarding ur network setup, its always recommened to use a direct cable connection fore a more reliable and steady connection.
But I know myself that this is not always possible. Therefore, u can also choose the variant with the 2 power outlet adapters, if a direct wired connection is not possible.
Thank you very much for the information.
I could pull a cable from the router (2nd level) to the miner (basement), however it will be through the house, and it would not be practical.
I could also pull it through the air ducts, however I need help, which I do not have right now.
I checked the speed and it is 10Mbps, and, from what I understood that the server would need some 5Mbps, it should be enough no?
Thank you
BitMaxz
Legendary
*
Online Online

Activity: 3248
Merit: 2970


Block halving is coming.


View Profile WWW
October 20, 2023, 04:58:49 PM
 #20

I checked the speed and it is 10Mbps, and, from what I understood that the server would need some 5Mbps, it should be enough no?
Thank you
If you are running one unit 10mbps should be beyond enough the important is the internet you provide to the unit is should stable and use a pool server that gives you low latency like if you are in the US then use the US pool server or if you are living in Asian country then use Asia pool server.

█▀▀▀











█▄▄▄
▀▀▀▀▀▀▀▀▀▀▀
e
▄▄▄▄▄▄▄▄▄▄▄
█████████████
████████████▄███
██▐███████▄█████▀
█████████▄████▀
███▐████▄███▀
████▐██████▀
█████▀█████
███████████▄
████████████▄
██▄█████▀█████▄
▄█████████▀█████▀
███████████▀██▀
████▀█████████
▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀