A pump rotor that is stiff after a long shutdown and frees up after a few turns usually points to deposits or a film drying in the tight gap between rotor and can, not to the pump itself. Pre-mixed PC coolants like DP Ultra contain dyes, surfactants and corrosion inhibitors that can leave exactly that kind of residue when the loop sits still, especially if some water evaporated.
What has worked for hydro units:
- Flush the loop with distilled or deionized water, run it for a while, drain, and repeat until it comes out clear.
- Refill with deionized water plus a proper inhibitor/biocide, or with about 25-30% propylene glycol in DI water if there's any freeze risk. Avoid dyed or "UV" coolants and anything with particles.
- Keep conductivity low (DI water), use a mesh filter before the pump, and check for any biological growth.
- During long shutdowns, either run the pump for a few minutes every few days or drain the loop. Standing coolant in the pump gap is what causes the sticking.
- If the rotor is still stiff after a clean flush, pull the pump head and clean the can and impeller. Bearing wear also shows up this way.
As mentioned above, Bitmain doesn't publish a specific product for the S19 Hydro; antifreeze or DI water is what's used in practice.