Author Topic: My new garage and 200 amps  (Read 3037 times)
booradlly (OP)
Newbie
*
Offline Offline

Activity: 29
Merit: 0


View Profile
August 05, 2014, 05:18:37 AM
 #1

If I got a new 240v outlet, how would I use it to power my miners. What are my configuration options. Am I limited to power supplies that have 240v plugs (like IBM DPS-2000BB). If you were getting new circuit breakers put in what would you get? Eventually I won't be mining so I would use these outlets for tools (table saws, band saws), do they use 240v outlets?

^^^^  tl,dr   ^^^^

I have a new house and therefore a new garage. I would like to put all my miners in said garage. The circuit breaker panel is already in the garage. I have a meeting tomorrow morning with an electrician. At that time I would like to tell him what outlets I would like.

I've already talked to bge, and I can use 26000 watts. I'm planning to put all of this in the garage. Suggestions on outlets, configurations, my sanity, areas I might have issues. The goal here is safety first, looking normal second (like a heavily decked out tool room, not like Im trying to recreate a tesla experiment). If nothing else, because a year from now, I might not be mining, but I will need tools.

Is there a way to make a 240v outlet, a 120v outlet? I know you can't do the opposite as the wires in the wall would melt, but I would think you could do this? I think I saw a power strip that had 120v sockets, and it plugged into a 240v outlet hence making a 240v outlet a 120v outlet.

If I haven't made it clear, feel free to tell me I'm crazy and that I'm going to burn my house down, just be specific and detailed on the how.
1714645908
Hero Member
*
Offline Offline

Posts: 1714645908

View Profile Personal Message (Offline)

Ignore
1714645908
Reply with quote  #2

1714645908
Report to moderator
"Bitcoin: mining our own business since 2009" -- Pieter Wuille
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
1714645908
Hero Member
*
Offline Offline

Posts: 1714645908

View Profile Personal Message (Offline)

Ignore
1714645908
Reply with quote  #2

1714645908
Report to moderator
1714645908
Hero Member
*
Offline Offline

Posts: 1714645908

View Profile Personal Message (Offline)

Ignore
1714645908
Reply with quote  #2

1714645908
Report to moderator
DeathAndTaxes
Donator
Legendary
*
Offline Offline

Activity: 1218
Merit: 1079


Gerald Davis


View Profile
August 05, 2014, 05:21:06 AM
 #2

Why would you want to use 120V?  PC power supplies can run on either.  240V is more efficient, cheaper, and puts less stress/heat on the power supplies.
dropt
Legendary
*
Offline Offline

Activity: 1512
Merit: 1000



View Profile
August 05, 2014, 05:25:23 AM
 #3

Five 30A x 208/240V drops terminating with Nema L6-30r  receptacles.  Get Some PDUs to plug into those.  Save
the last 10A of headroom for some huge ass fans. You'll need them.
Pjones
Member
**
Offline Offline

Activity: 70
Merit: 10


View Profile
August 05, 2014, 05:40:25 AM
 #4

Ask your electrician.  He will know what the local codes are and stay within them. 
xstr8guy
Hero Member
*****
Offline Offline

Activity: 784
Merit: 1004


Glow Stick Dance!


View Profile
August 05, 2014, 05:40:48 AM
 #5

You don't need an electrician. Just buy a Tripplite PDU and appropriate cords for the PSUs for the 240v plug.

Btw, all current, good quality PSUs can take 240v.
booradlly (OP)
Newbie
*
Offline Offline

Activity: 29
Merit: 0


View Profile
August 05, 2014, 06:29:49 AM
 #6

Five 30A x 208/240V drops terminating with Nema L6-30r  receptacles.  Get Some PDUs to plug into those.  Save
the last 10A of headroom for some huge ass fans. You'll need them.

Why would you want to use 120V?  PC power supplies can run on either.  240V is more efficient, cheaper, and puts less stress/heat on the power supplies.

This is exactly what I was looking for, I think. When you say the pc power supply can be run on 240V, are you talking about using the PDUs that others have suggested or something else? I can't plug them directly in as the plug doesnt fit in the Nema L6-30r.
bcp19
Hero Member
*****
Offline Offline

Activity: 532
Merit: 500



View Profile
August 05, 2014, 10:10:07 AM
 #7

Five 30A x 208/240V drops terminating with Nema L6-30r  receptacles.  Get Some PDUs to plug into those.  Save
the last 10A of headroom for some huge ass fans. You'll need them.

Why would you want to use 120V?  PC power supplies can run on either.  240V is more efficient, cheaper, and puts less stress/heat on the power supplies.

This is exactly what I was looking for, I think. When you say the pc power supply can be run on 240V, are you talking about using the PDUs that others have suggested or something else? I can't plug them directly in as the plug doesnt fit in the Nema L6-30r.
You use something like this to power your PSU's:

http://www.buypdu.com/power-cords/iec-c13/iec-c14.html?gclid=CPLX_vTu-78CFWwQ7AodfRcA9w

Depending on the PSUs you are running will determine if you get the 10 or 15 amp version (though in truth, at 208/240v you will only need the 10amp).  The Triplite PDUs are set up to use these cords and will work with any EVGA/OCZ power supply.  A typical PDU can be found here:

http://www.tripplite.com/metered-pdu-30a-208v-240v-2u-c13-c19-outlets-l6-30p-single-phase~PDUMH30HV/

Remember, it's more efficient to use 208/240 versus 120 to power your equipment.

I do not suffer fools gladly... "Captain!  We're surrounded!"
I embrace my inner Kool-Aid.
zetaray
Hero Member
*****
Offline Offline

Activity: 658
Merit: 500


View Profile
August 05, 2014, 10:42:23 AM
 #8

For the same power rating, doesn't 240v takes less current from the mains than 120v? So what is the reason to use a 120v mains ?

.CryptoTotal.com.
                              l█████████▇▀
                              ████████▇▀
                              ███████▇▀
                              ██████▇▀
                              █████▇▀
                              ████▇▀
                              ███▇▀
                              ██▇▀
                              █▇▀
                              ▇▀
▇▇
▇▇

Express.Crypto.Checkout
Accepts Multiple Cryptos
Worldwide Shipping
jowaybea
Newbie
*
Offline Offline

Activity: 28
Merit: 0


View Profile
August 05, 2014, 01:44:09 PM
 #9

Five 30A x 208/240V drops terminating with Nema L6-30r  receptacles.  Get Some PDUs to plug into those.  Save
the last 10A of headroom for some huge ass fans. You'll need them.

Why would you want to use 120V?  PC power supplies can run on either.  240V is more efficient, cheaper, and puts less stress/heat on the power supplies.

This is exactly what I was looking for, I think. When you say the pc power supply can be run on 240V, are you talking about using the PDUs that others have suggested or something else? I can't plug them directly in as the plug doesnt fit in the Nema L6-30r.

Most PDU's have either L6-20p cords though you can find them with the C19/C20 or C14/C15 PSU style plugs.  You can get L6-30 to L6-20 adapters, but they start around $35-$40 each, so if you're going to have an electrician out, I'd have him install L6-20r recepticles right next to your L6-30r's.  Just watch how many amps you put on a circuit at any given time and you'll be fine.  That's usually not a big deal as a 30A circuit can safely handle 30x240 (x80% for continuous load safety factor) 5,760w.  That would easly handle 5xEVGA 1300G2 PSU's running 15xAntminer S3's.
jowaybea
Newbie
*
Offline Offline

Activity: 28
Merit: 0


View Profile
August 05, 2014, 01:46:12 PM
 #10

For the same power rating, doesn't 240v takes less current from the mains than 120v? So what is the reason to use a 120v mains ?

Only reason is because US households are wired primarily with 120v, and (even if you have a 240v circuit) it can be difficult to get 240v power cables for your PSU's.
jonnybravo0311
Legendary
*
Offline Offline

Activity: 1344
Merit: 1023


Mine at Jonny's Pool


View Profile WWW
August 05, 2014, 02:10:35 PM
 #11

For the same power rating, doesn't 240v takes less current from the mains than 120v? So what is the reason to use a 120v mains ?
This is the fate we suffer for being early adopters.  Back when electric service was new, the higher voltages tended to burn out the lightbulbs too quickly, so the 110/120V standard was adopted for residential power transmission.  By the time engineers figured out how to make stuff that wouldn't burn out with the higher voltages, the US didn't change because there was too much infrastructure already in place.

Jonny's Pool - Mine with us and help us grow!  Support a pool that supports Bitcoin, not a hardware manufacturer's pockets!  No SPV cheats.  No empty blocks.
DeathAndTaxes
Donator
Legendary
*
Offline Offline

Activity: 1218
Merit: 1079


Gerald Davis


View Profile
August 05, 2014, 02:15:22 PM
 #12

For the same power rating, doesn't 240v takes less current from the mains than 120v? So what is the reason to use a 120v mains ?
This is the fate we suffer for being early adopters.  Back when electric service was new, the higher voltages tended to burn out the lightbulbs too quickly, so the 110/120V standard was adopted for residential power transmission.  By the time engineers figured out how to make stuff that wouldn't burn out with the higher voltages, the US didn't change because there was too much infrastructure already in place.

Well US service is 240V.  It is 240V split phase producing 120V between either leg and the ground and 240V between both legs.  There are no 120V mains in the US (or it would be very non-standard and archaic).
jonnybravo0311
Legendary
*
Offline Offline

Activity: 1344
Merit: 1023


Mine at Jonny's Pool


View Profile WWW
August 05, 2014, 02:21:06 PM
 #13

For the same power rating, doesn't 240v takes less current from the mains than 120v? So what is the reason to use a 120v mains ?
This is the fate we suffer for being early adopters.  Back when electric service was new, the higher voltages tended to burn out the lightbulbs too quickly, so the 110/120V standard was adopted for residential power transmission.  By the time engineers figured out how to make stuff that wouldn't burn out with the higher voltages, the US didn't change because there was too much infrastructure already in place.

Well US service is 240V.  It is 240V split phase producing 120V between either leg and the ground and 240V between both legs.  There are no 120V mains in the US (or it would be very non-standard and archaic).
You're absolutely right... I just didn't want to get into it and confuse the OP by saying, "Well, we really are a 240V split at the center pole into 2 120V lines and a ground in your home".  That just seemed too much, so I stuck with the history lesson on why we've got 120V in our homes Smiley

Jonny's Pool - Mine with us and help us grow!  Support a pool that supports Bitcoin, not a hardware manufacturer's pockets!  No SPV cheats.  No empty blocks.
wh00per
Hero Member
*****
Offline Offline

Activity: 571
Merit: 500



View Profile
August 05, 2014, 03:03:26 PM
 #14

Five 30A x 208/240V drops terminating with Nema L6-30r  receptacles.  Get Some PDUs to plug into those.  Save
the last 10A of headroom for some huge ass fans. You'll need them.

You don't get 208V with a normal residential service. 208V is one leg of a 3-phase service .. usually data-center grade.
What you get with a residential service is 250V split phase. That should be good enough for mining, but the data-center PDUs are not rated for it.

https://bitcointalk.org/index.php?topic=521520.msg8182756#msg8182756

Have fun!

CSA/cUL Certified Power Distribution Panels - Basic, Switched, Metered. 1-3 phases. Up to 600V. NMC:N4F9qvHz11BHcc4nh1LCJFsrZhA1EWgVwj
DeathAndTaxes
Donator
Legendary
*
Offline Offline

Activity: 1218
Merit: 1079


Gerald Davis


View Profile
August 05, 2014, 03:06:14 PM
 #15

I think he was writing it as 208V/240V because it is the same exact connectors for 208V single phase and 240V.  Same wiring configuration, same plugs, same outlets, same PDUs, etc.  Never seen a PDU that didn't work on both 208V and 240V.  All the components have to be rated to 240V anyways or they would be a code violation.   
wh00per
Hero Member
*****
Offline Offline

Activity: 571
Merit: 500



View Profile
August 05, 2014, 03:15:25 PM
 #16

30A circuits limit your PSU at 3x 1200W (7..8A - 1500W each at the wall) power supplies per circuit in continuous load. I'd rather go with multiple receptacles of 20A (good enough for 2 power supplies each), and not using those expensive PDUs.

Overall is cheaper.

CSA/cUL Certified Power Distribution Panels - Basic, Switched, Metered. 1-3 phases. Up to 600V. NMC:N4F9qvHz11BHcc4nh1LCJFsrZhA1EWgVwj
cloverme
Legendary
*
Offline Offline

Activity: 1512
Merit: 1054


SpacePirate.io


View Profile WWW
August 05, 2014, 03:39:36 PM
 #17

I'm in the process of adding a 240v/30A line to my garage (but for an electric car), when I find out how much it costs, I'll post the info.

-You can't use the same outlets, the wiring has to be a higher gauge to handle the increased voltage.
-They'll need to install a 30A circuit into you panel. If you panel is ancient, it's possible they may need to replace your panel for fire safety.

In short, for miners, this is the same as adding miners to a datacenter. You'll need a PDU that has the C13 outlets to plug your miners into. I recommend tripplite, PDUMV30HV.
You also have to replace your power supply power cables with a C13/C14 cables, which cost $1.60 at monoprice (item 6329). 
Check to make sure your power supplies can handle the extra voltage, just look on the PS label, it usually says what in the input voltage limits are.
The nice thing is that on the higher voltage, you'll pull less amps, so you can put more miners on the circuit, but you need 15% reserved or you'll throw the 30A breaker.
DeathAndTaxes
Donator
Legendary
*
Offline Offline

Activity: 1218
Merit: 1079


Gerald Davis


View Profile
August 05, 2014, 03:44:53 PM
Last edit: August 05, 2014, 04:07:13 PM by DeathAndTaxes
 #18

Well nobody runs a 1200W PSU @ 1200W of load.  30A is good for 5760W (after 20% derate).   30A PDU are dirt cheap if you are willing to buy used.   Datacenters go through tens of thousands of these so there is never ending supply.



AP9571 is one example but there are plenty of other models which work equally well.  New ones are $150+ but used ones tend to go for $30 to $50 each.  A basic PDU is pretty much a high current power strip with a breaker.  It pretty much works or it doesn't so I have never had a problem buying used.

You will need to install* a 30A double pole breaker and NEMA L6-30R outlet for each one.  The AP9571 comes prewired with a matching NEMA L6-30P plug.  By the NEC, continual loads are derated 20% so you only get 24A usable from a 30A branch circuit.  One circuit (breaker, branch wiring, outlet, pdu) is good for 5.76KW (240V * 30A * 80%) which is probably more than most people can handle.  Remember electricity in = heat out.   So for those with dreams of building 100KW farms I would say start "small" you can build out in 5.76KW segments.  Even 5.76KW is a lot of heat.


* I can be done DIY, I put two in so I could power a 11KW GPU farm but this isn't a beginner project.  Remember electricity kills instantly and without warning.  Parts on the inside of the circuit breaker panel may remain energized with lethal voltage even if breakers are off.  It isn't a nuclear reactor but it does require some competence and good tools never hurt.
DeathAndTaxes
Donator
Legendary
*
Offline Offline

Activity: 1218
Merit: 1079


Gerald Davis


View Profile
August 05, 2014, 04:15:51 PM
 #19

-You can't use the same outlets, the wiring has to be a higher gauge to handle the increased voltage.

Correction.  120V and 240V circuits use the same wiring.  Wire gauge is based on current not voltage.

Quote
You'll need a PDU that has the C13 outlets to plug your miners into. I recommend tripplite, PDUMV30HV.

As a heads up most electricians that do residential work are more familiar with straight connectors but most PDUs use locking connectors.  Make sure they understand you will need an outlet with a locking connector if that is the plug your PDU uses.   For example a NEMA L6-30R not a NEMA 6-30R.  The L indicates locking connector.

Quote
The nice thing is that on the higher voltage, you'll pull less amps, so you can put more miners on the circuit, but you need 15% reserved or you'll throw the 30A breaker.

By code on continual loads, the current should be 20% lower when than the nameplate rating.  So 24A or 5,760W on a 30A PDU.
wh00per
Hero Member
*****
Offline Offline

Activity: 571
Merit: 500



View Profile
August 05, 2014, 04:56:25 PM
 #20

Well nobody runs a 1200W PSU @ 1200W of load.  30A is good for 5760W (after 20% derate).   30A PDU are dirt cheap if you are willing to buy used.   Datacenters go through tens of thousands of these so there is never ending supply.

You might be surprised what DIY mining pushes users into. 5760W equals less than 4 x 1500w at the wall .. so you'll use only 3 outlets at max from the strip leaving about 1.2kW spare.. With all those C13 outlets available on the PDU one may think they're good to draw more, when in fact they should be taped out. With 20A circuits to have less spare (about 840W).

Anyway, all setups are good as long as the end user monitors the currents and size their stuff so that they don't burn their house down. I like the 240V setups because they load the two 180 degree phases equally and you don't lose much having an unbalanced system.

CSA/cUL Certified Power Distribution Panels - Basic, Switched, Metered. 1-3 phases. Up to 600V. NMC:N4F9qvHz11BHcc4nh1LCJFsrZhA1EWgVwj