Bitcoin Forum
May 10, 2024, 04:07:14 AM *
News: Latest Bitcoin Core release: 27.0 [Torrent]
 
   Home   Help Search Login Register More  
Pages: « 1 [2]  All
  Print  
Author Topic: My new garage and 200 amps  (Read 3038 times)
dropt
Legendary
*
Offline Offline

Activity: 1512
Merit: 1000



View Profile
August 05, 2014, 05:18:23 PM
 #21

You might be surprised what DIY mining pushes users into.
I'm quite certain DaT is well aware of what "DIY" miners get up to  Wink

Quote
5760W equals less than 4 x 1500w at the wall .. so you'll use only 3 outlets at max from the strip leaving about 1.2kW spare.. With all those C13 outlets available on the PDU one may think they're good to draw more, when in fact they should be taped out. With 20A circuits to have less spare (about 840W).
And if they're loading up their PSUs to that limit, they're likely to just use at 15% de-rated instead of 20% and load 4 outlets at 1,500W.  But they're likely not using 1500W at the wall draw, so this is really a non-issue.

Quote
Anyway, all setups are good as long as the end user monitors the currents and size their stuff so that they don't burn their house down. I like the 240V setups because they load the two 180 degree phases equally and you don't lose much having an unbalanced system.

Precisely.  Arguments can be made for any side; personally I prefer switched PDUs on 30A drops.
"You Asked For Change, We Gave You Coins" -- casascius
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
1715314034
Hero Member
*
Offline Offline

Posts: 1715314034

View Profile Personal Message (Offline)

Ignore
1715314034
Reply with quote  #2

1715314034
Report to moderator
1715314034
Hero Member
*
Offline Offline

Posts: 1715314034

View Profile Personal Message (Offline)

Ignore
1715314034
Reply with quote  #2

1715314034
Report to moderator
1715314034
Hero Member
*
Offline Offline

Posts: 1715314034

View Profile Personal Message (Offline)

Ignore
1715314034
Reply with quote  #2

1715314034
Report to moderator
jowaybea
Newbie
*
Offline Offline

Activity: 28
Merit: 0


View Profile
August 05, 2014, 05:48:15 PM
 #22

So, a tiny bit more research on PDU's taught me that the plug *tends* to be matched to the rating of the PDU.  So if you have 30A circuits and they install an L6-30R recepticle, and you buy a 30A rated PDU, you should be good to go.  Just make sure you do your own math so as to not overload the circuit, as a 30A PDU will have around a dozen outlets, and people going through this effort tend to run multiple miners per PSU, resulting in a whole lot more than 2.5A per PSU, even at 240V.
MrTeal
Legendary
*
Offline Offline

Activity: 1274
Merit: 1004


View Profile
August 06, 2014, 01:06:23 AM
 #23

I'd chime in with the others here, and say just go with a bunch of L6-30A outlets. PDUs are dirt cheap, even fancier ones.

I use these, and other than the control being RS-232 instead of Ethernet, I love them.
http://www.ebay.com/sch/i.html?_from=R40&_sacat=0&_nkw=pm10i-30a&_sop=15&_clu=2&_fcid=1&_localstpos=21203&_stpos=21203&gbr=1&_trksid=p2045573.m339&_trksid=p2045573.m339

If you're unsure on how long you want to run the gear, consider getting a PDU whip with conduit; StayOnline will sell you a prewired one that includes the receptacle and box prewired in flexible conduit. You can then run it on the surface instead of in the wall, and if you decide to remove your massive farm you can always move the whips around without touching the box, or remove them and sell them.
http://www.stayonline.com/nema-locking-blade-pdu-whips.aspx
volosator
Sr. Member
****
Offline Offline

Activity: 272
Merit: 250



View Profile
August 06, 2014, 04:22:10 PM
 #24

26kW sounds awesome for mining - assuming you know how to cool it all down.
I have hard times dealing with 3kW of heat in a large basement.
TyrTheAlpha
Member
**
Offline Offline

Activity: 63
Merit: 10


View Profile
August 06, 2014, 08:16:23 PM
 #25

Boordally, Could you clarify what you mean by “I can use 26000 watts”? I also get my home service from BGE. Are you saying you can use up to 26000 watts before they come knocking on your door?
jcoin
Member
**
Offline Offline

Activity: 78
Merit: 10



View Profile
August 07, 2014, 03:16:38 PM
 #26

Is there any feasible way to reuse the heat to save on oil/gas/water heaters?

1jcoinJSbtKrukhGWtLqyXd9LSjsE9hHY
wh00per
Hero Member
*****
Offline Offline

Activity: 571
Merit: 500



View Profile
August 07, 2014, 03:22:32 PM
 #27

Only if you capture the heated (with a range hood / box and suction fans) air and feed it into your furnace inlet to be filtered and humidified .. else it's not that funny to run your rig in the living room because of the eventual noise.

CSA/cUL Certified Power Distribution Panels - Basic, Switched, Metered. 1-3 phases. Up to 600V. NMC:N4F9qvHz11BHcc4nh1LCJFsrZhA1EWgVwj
nanook7
Newbie
*
Offline Offline

Activity: 48
Merit: 0


View Profile
August 08, 2014, 04:31:28 AM
 #28

Well nobody runs a 1200W PSU @ 1200W of load.  30A is good for 5760W (after 20% derate).   30A PDU are dirt cheap if you are willing to buy used.   Datacenters go through tens of thousands of these so there is never ending supply.

http://i.ebayimg.com/00/s/NDIwWDc1MA==/z/cRYAAOSwxCxT4ECL/$_1.JPG

AP9571 is one example but there are plenty of other models which work equally well.  New ones are $150+ but used ones tend to go for $30 to $50 each.  A basic PDU is pretty much a high current power strip with a breaker.  It pretty much works or it doesn't so I have never had a problem buying used.

You will need to install* a 30A double pole breaker and NEMA L6-30R outlet for each one.  The AP9571 comes prewired with a matching NEMA L6-30P plug.  By the NEC, continual loads are derated 20% so you only get 24A usable from a 30A branch circuit.  One circuit (breaker, branch wiring, outlet, pdu) is good for 5.76KW (240V * 30A * 80%) which is probably more than most people can handle.  Remember electricity in = heat out.   So for those with dreams of building 100KW farms I would say start "small" you can build out in 5.76KW segments.  Even 5.76KW is a lot of heat.


* I can be done DIY, I put two in so I could power a 11KW GPU farm but this isn't a beginner project.  Remember electricity kills instantly and without warning.  Parts on the inside of the circuit breaker panel may remain energized with lethal voltage even if breakers are off.  It isn't a nuclear reactor but it does require some competence and good tools never hurt.

I know these datacenter PDUs are suppose to be feed 208V but if we feed them 240V will they still work and work without failure?
Ayers
Legendary
*
Offline Offline

Activity: 2618
Merit: 1023


Seabet.io | Crypto-Casino


View Profile
August 08, 2014, 06:57:47 AM
 #29

Why would you want to use 120V?  PC power supplies can run on either.  240V is more efficient, cheaper, and puts less stress/heat on the power supplies.

usa still using it if i'm not mistaken, and i don't know why they are so stubborn to use a non-efficient thing

dropt
Legendary
*
Offline Offline

Activity: 1512
Merit: 1000



View Profile
August 08, 2014, 02:39:34 PM
 #30

I know these datacenter PDUs are suppose to be feed 208V but if we feed them 240V will they still work and work without failure?

Check the ratings on whatever model you're looking at, but they should be fine.

I have some Dells that are rated to 240v but they're running at 252v.
wh00per
Hero Member
*****
Offline Offline

Activity: 571
Merit: 500



View Profile
August 09, 2014, 12:53:32 AM
 #31

usa still using it if i'm not mistaken, and i don't know why they are so stubborn to use a non-efficient thing

You don't change the infrastructure of a continent that easy. and .. the U.S. was way out front in putting electric power technology to practical use. In the early days, lower voltages were the most practical for electric lights — higher voltages burned out the bulbs. So the hundreds of power plants built in the U.S. prior to 1900 adopted 110 volts (or 115 or 120 volts) as their de facto standard. Starting in Germany around the turn of the century, people adopted the 220-volt (or 230- or 240-volt) standard, mostly because it's easier to transport this way and they had the technology to build better bulbs at the time.

CSA/cUL Certified Power Distribution Panels - Basic, Switched, Metered. 1-3 phases. Up to 600V. NMC:N4F9qvHz11BHcc4nh1LCJFsrZhA1EWgVwj
booradlly (OP)
Newbie
*
Offline Offline

Activity: 29
Merit: 0


View Profile
August 10, 2014, 06:32:49 AM
 #32

First off, wow, you guys are awesome. I expected a couple of answers, and you guys have just run with it, this is awesome.

Bad news, I had the meeting with the electrician and I overlooked something with the heavy-up (upgrade from 200A to 400A service), apparently the wire in the ground outside my house can handle 400A, but the wire from my meter to my breaker box is only rated for 180A. $1000 to run a new wire or replace that one. So yea no. Maybe later.

I'm still putting more outlets in, it just wont be 26000watts. I'm assuming my max right now will be 30 s3s, or 12kw or 100A. I'll be confirming either way with BGE and will update.

Boordally, Could you clarify what you mean by “I can use 26000 watts”? I also get my home service from BGE. Are you saying you can use up to 26000 watts before they come knocking on your door?

BGE said if I went over that number there could be faults in the line in the ground outside my house. I never got around to asking them how bad a fault was? Like was "fault" code for melted wire (or rather you are now paying to repair the wire in the ground), or just a simple flipped ciruit breaker/slap on the wrist.

BGE told me 26000 watts when I gave them the following figures. "Servers" = Miners. They told me I could add 65 "Servers" onto my normal load. I reverse calculated the 26kw from that. None of this matters, now I just stay under 180A. They told me they had calculated the 65 "servers" by taking my base load, subtracting from some max number (they wouldnt tell me this number for some reason), and then dividing by 400w I had told them the servers run at.
                      old               new
Refrigerator      2000w            2000w                         
Microwave       1100w            1100w
Dishwasher    2400w              2400w
Washer          500w               500w
AC unit          4500w             4500w
lights             10w x12         10w x12

The above items are not continuous draw, but random and sporadic.
These items are continuous draw, so if you wanted the yearly usage simply multiple by hours in day and then days in year.
                      old              new               want
Computers      700w
Servers           400w x10      400w x30     400w x100
booradlly (OP)
Newbie
*
Offline Offline

Activity: 29
Merit: 0


View Profile
August 10, 2014, 06:42:16 AM
 #33

26kW sounds awesome for mining - assuming you know how to cool it all down.
I have hard times dealing with 3kW of heat in a large basement.
Is there any feasible way to reuse the heat to save on oil/gas/water heaters?

Only if you capture the heated (with a range hood / box and suction fans) air and feed it into your furnace inlet to be filtered and humidified .. else it's not that funny to run your rig in the living room because of the eventual noise.

Haha, this is awesome, you guys read my mind. This is a pre-con house so I was there when they installed the hvac system, and I asked a lot of questions. My plan is to funnel the heat from the miners into the main return. But I've got to power them first.
booradlly (OP)
Newbie
*
Offline Offline

Activity: 29
Merit: 0


View Profile
August 10, 2014, 06:59:26 AM
 #34

I'm in the process of adding a 240v/30A line to my garage (but for an electric car).
As a heads up most electricians that do residential work are more familiar with straight connectors but most PDUs use locking connectors.  Make sure they understand you will need an outlet with a locking connector if that is the plug your PDU uses.   For example a NEMA L6-30R not a NEMA 6-30R.  The L indicates locking connector.

Will a 6-30R male fit into a L6-30R or the reverse or are they mutually exclusive? If at all possible I would like to choose a connector that I can power a pdu, power a future electric car, power a table saw, power a welder, and (just for the heck of it) power a kiln (obviously not all at the same time Tongue ). Basically I would like to future proof as much as possible.
booradlly (OP)
Newbie
*
Offline Offline

Activity: 29
Merit: 0


View Profile
August 10, 2014, 07:09:20 AM
 #35

30A circuits limit your PSU at 3x 1200W (7..8A - 1500W each at the wall) power supplies per circuit in continuous load. I'd rather go with multiple receptacles of 20A (good enough for 2 power supplies each), and not using those expensive PDUs.

Overall is cheaper.

Just to be clear, when you refer to a cheaper 20A receptacle vs a more expensive 30A receptacle, you are referring to a 20A 120V receptacle vs a 30A 240V receptacle right? I just want to be sure, because there are 20A 240V receptacles also.
Flying Hellfish
Legendary
*
Offline Offline

Activity: 1764
Merit: 1754


Verified Bernie Bro - Feel The Bern!


View Profile
August 10, 2014, 12:18:32 PM
 #36



Will a 6-30R male fit into a L6-30R or the reverse or are they mutually exclusive? If at all possible I would like to choose a connector that I can power a pdu, power

As a point of clarity the 6-30R male you ask about is technically a 6-30P

A 6-30P will not plug directly into an L6-30R, but you can easily buy/make an adapter cable that is 6-30R to L6-30P which would allow you to plug a 6-30P plug into an L6-30R receptacle.  The cord cap can easily be swap on any device as can just the receptacle if you don't want to buy or make an adapter cable.
Pages: « 1 [2]  All
  Print  
 
Jump to:  

Powered by MySQL Powered by PHP Powered by SMF 1.1.19 | SMF © 2006-2009, Simple Machines Valid XHTML 1.0! Valid CSS!