yochdog (OP)
Legendary
Offline
Activity: 2044
Merit: 1000
|
|
December 29, 2014, 07:09:34 PM |
|
I am not that good when it comes to electrical matters. First person to tell me (correctly) how many watts this PDU can supply to mining equipment, wins the bounty: http://www.ebay.com/itm/PDI-PDU-100-KVA-480v-x-208v-3-Panel-Manuifactured-2009-/121527983792?pt=US_Uninterruptible_Power_Supplies&hash=item1c4ba1deb0
|
I am a trusted trader! Ask Inaba, Luo Demin, Vanderbleek, Sannyasi, Episking, Miner99er, Isepick, Amazingrando, Cablez, ColdHardMetal, Dextryn, MB300sd, Robocoder, gnar1ta$ and many others!
|
|
|
ASICSPACE
Full Member
Offline
Activity: 121
Merit: 100
Feel free to contact me via email, skype or phone!
|
|
December 29, 2014, 07:11:25 PM Last edit: January 01, 2015, 01:59:10 AM by ASICSPACE |
|
It's a 100 KVA which means 100KW. A little less actually because the transformer inside doesn't have a perfect power factor. KVA is "apparent power" while KW is real power. Apparent power is what you would get in a perfect world with no lagging reactive power due to the transformer. Check out this link: http://www.apcmedia.com/salestools/SADE-5TNQYF/SADE-5TNQYF_R1_EN.pdf?sdirect=trueWe're not using PDUs in our data center, just transformer + panels. We have some pics on our website: http://www.asicspace.com/
|
|
|
|
yochdog (OP)
Legendary
Offline
Activity: 2044
Merit: 1000
|
|
December 29, 2014, 07:13:30 PM |
|
KVA is equivelent to KW?
I thought there was a conversion involved.....
|
I am a trusted trader! Ask Inaba, Luo Demin, Vanderbleek, Sannyasi, Episking, Miner99er, Isepick, Amazingrando, Cablez, ColdHardMetal, Dextryn, MB300sd, Robocoder, gnar1ta$ and many others!
|
|
|
bonds
Member
Offline
Activity: 65
Merit: 10
|
|
December 29, 2014, 07:14:41 PM |
|
120 volts at 278 amps is 33360 watts
|
1Bonds3znU2tqc99b8cdDkBX9m6q9ftVG2
|
|
|
sbogovac
Legendary
Offline
Activity: 2744
Merit: 1193
I don't believe in denial.
|
|
December 29, 2014, 07:15:18 PM Last edit: December 29, 2014, 07:33:50 PM by sbogovac |
|
None,
It clearly states: SPECIFICATION OUTPUT 208/120 volts
I don't know which miners you had in mind, but generally ASIC miners run at 10-12 volts...
|
0x7442A5c37E513D335F53843cD20c00F77eAC7867
|
|
|
ASICSPACE
Full Member
Offline
Activity: 121
Merit: 100
Feel free to contact me via email, skype or phone!
|
|
December 29, 2014, 07:16:21 PM |
|
120 volts at 278 amps is 33360 watts
That's another way to look at it, but you forgot it's 3 phase so 120*278*3 = 100080 watts = 100 kw
|
|
|
|
bonds
Member
Offline
Activity: 65
Merit: 10
|
|
December 29, 2014, 07:16:58 PM |
|
120 volts at 278 amps is 33360 watts
That's another way to look at it, but you forgot it's 3 phase so 120*278*3 = 100080 watts = 100 kw Sheesh thats insane
|
1Bonds3znU2tqc99b8cdDkBX9m6q9ftVG2
|
|
|
ASICSPACE
Full Member
Offline
Activity: 121
Merit: 100
Feel free to contact me via email, skype or phone!
|
|
December 29, 2014, 07:17:55 PM |
|
KVA is equivelent to KW?
I thought there was a conversion involved.....
Nope, generally when you use KVA you're talking about the rating of equipment, while when you use KW you're talking about actual power usage. Make sure to load each phase evenly otherwise you'll cause harmonics. BTC address: 1KDDR9VrkjXugxrsnT4BjDWbNbyYDwSCC1
|
|
|
|
yochdog (OP)
Legendary
Offline
Activity: 2044
Merit: 1000
|
|
December 29, 2014, 07:24:43 PM |
|
KVA is equivelent to KW?
I thought there was a conversion involved.....
Nope, generally when you use KVA you're talking about the rating of equipment, while when you use KW you're talking about actual power usage. Make sure to load each phase evenly otherwise you'll cause harmonics. BTC address: 1KDDR9VrkjXugxrsnT4BjDWbNbyYDwSCC1 OK, you win. Coming your way.
|
I am a trusted trader! Ask Inaba, Luo Demin, Vanderbleek, Sannyasi, Episking, Miner99er, Isepick, Amazingrando, Cablez, ColdHardMetal, Dextryn, MB300sd, Robocoder, gnar1ta$ and many others!
|
|
|
ASICSPACE
Full Member
Offline
Activity: 121
Merit: 100
Feel free to contact me via email, skype or phone!
|
|
December 29, 2014, 07:29:31 PM |
|
KVA is equivelent to KW?
I thought there was a conversion involved.....
Nope, generally when you use KVA you're talking about the rating of equipment, while when you use KW you're talking about actual power usage. Make sure to load each phase evenly otherwise you'll cause harmonics. BTC address: 1KDDR9VrkjXugxrsnT4BjDWbNbyYDwSCC1 OK, you win. Coming your way. Got it, thanks! Feel free to PM me if you have any more questions. If you're trying to mine, I may be able to give you some pointers that can save you lots of money. Check out the mine we're building, link in my signature.
|
|
|
|
dogie
Legendary
Offline
Activity: 1666
Merit: 1185
dogiecoin.com
|
|
December 29, 2014, 10:24:41 PM |
|
Well there goes the hash rate!
|
|
|
|
klondike_bar
Legendary
Offline
Activity: 2128
Merit: 1005
ASIC Wannabe
|
|
December 30, 2014, 01:11:21 AM |
|
KVA is equivelent to KW?
I thought there was a conversion involved.....
not really. Watts = Volts x Amps --> W=VA -----> KVA=KW there is some discrepency depending on your voltage input/output and other factors, but 100KVA means about 208A of 480V input power. Safe practice dictates keeping full-time load at less than 80%
|
|
|
|
stan258
|
|
December 30, 2014, 02:13:13 AM |
|
KVA is equivelent to KW?
I thought there was a conversion involved.....
not really. Watts = Volts x Amps --> W=VA -----> KVA=KW there is some discrepency depending on your voltage input/output and other factors, but 100KVA means about 208A of 480V input power. Safe practice dictates keeping full-time load at less than 80% Manufactures generally advertise max potential in a perfect set up not constant supply, Klondike is correct. Edit - - - - TrippLite has had to re name several of their 220 - 240 PDUs because nobody in their right mind will ramp them up to full marketed AMPs
|
|
|
|
gdale
Newbie
Offline
Activity: 42
Merit: 0
|
|
December 30, 2014, 05:57:50 AM |
|
okay its out is this 225amp max at a 208volt's max this is because of 225 Amp Main Breaker this puts it at 46.8 kw's here is a calc for it http://www.rapidtables.com/calc/electric/power-calculator.htmput in the volts output of 208 and amps max is the main breaker of 225amps hope this helps edit its not 3 phase as no power factor is listed in spec
|
|
|
|
|
ASICSPACE
Full Member
Offline
Activity: 121
Merit: 100
Feel free to contact me via email, skype or phone!
|
|
December 30, 2014, 04:26:05 PM |
|
okay its out is this 225amp max at a 208volt's max this is because of 225 Amp Main Breaker this puts it at 46.8 kw's here is a calc for it http://www.rapidtables.com/calc/electric/power-calculator.htmput in the volts output of 208 and amps max is the main breaker of 225amps hope this helps edit its not 3 phase as no power factor is listed in spec First of all you can tell there's a 480/277 to 208/120 transformer in here because those are the voltages listed in the listing, which clearly indicates three phase power because 208 is the line to line voltage between two of the phases and 120 is the line to neutral voltage between a phase and the neutral. Also you multiplied the output line to line voltage by the input current, incorrectly. After the current passes through the transformer it will will increase (as indicated in the listing) because a transformer will change the voltage, and the current, but the power remains the same. P = (V1 x I1) = (V2 x I2).
|
|
|
|
sbogovac
Legendary
Offline
Activity: 2744
Merit: 1193
I don't believe in denial.
|
|
December 30, 2014, 05:17:10 PM |
|
okay its out is this 225amp max at a 208volt's max this is because of 225 Amp Main Breaker this puts it at 46.8 kw's here is a calc for it http://www.rapidtables.com/calc/electric/power-calculator.htmput in the volts output of 208 and amps max is the main breaker of 225amps hope this helps edit its not 3 phase as no power factor is listed in spec First of all you can tell there's a 480/277 to 208/120 transformer in here because those are the voltages listed in the listing, which clearly indicates three phase power because 208 is the line to line voltage between two of the phases and 120 is the line to neutral voltage between a phase and the neutral. Also you multiplied the output line to line voltage by the input current, incorrectly. After the current passes through the transformer it will will increase (as indicated in the listing) because a transformer will change the voltage, and the current, but the power remains the same. P = (V1 x I1) = (V2 x I2). Still don't understand how this will "supply" any "watts to [12V] mining equipment [OP]" though...
|
0x7442A5c37E513D335F53843cD20c00F77eAC7867
|
|
|
ASICSPACE
Full Member
Offline
Activity: 121
Merit: 100
Feel free to contact me via email, skype or phone!
|
|
December 30, 2014, 05:20:17 PM |
|
okay its out is this 225amp max at a 208volt's max this is because of 225 Amp Main Breaker this puts it at 46.8 kw's here is a calc for it http://www.rapidtables.com/calc/electric/power-calculator.htmput in the volts output of 208 and amps max is the main breaker of 225amps hope this helps edit its not 3 phase as no power factor is listed in spec First of all you can tell there's a 480/277 to 208/120 transformer in here because those are the voltages listed in the listing, which clearly indicates three phase power because 208 is the line to line voltage between two of the phases and 120 is the line to neutral voltage between a phase and the neutral. Also you multiplied the output line to line voltage by the input current, incorrectly. After the current passes through the transformer it will will increase (as indicated in the listing) because a transformer will change the voltage, and the current, but the power remains the same. P = (V1 x I1) = (V2 x I2). Still don't understand how this will "supply" any "watts to [12V] mining equipment [OP]" though... That's the job of the power supplies.
|
|
|
|
Soros Shorts
Donator
Legendary
Offline
Activity: 1617
Merit: 1012
|
|
December 30, 2014, 06:20:23 PM |
|
KVA is equivelent to KW?
I thought there was a conversion involved.....
It is actually KW = KVA x (power factor) but the power factor of modern switching power supplies with active PFC that you find in mining equipment is usually very close to 1.0, so most people don't bother to account for it.
|
|
|
|
sbogovac
Legendary
Offline
Activity: 2744
Merit: 1193
I don't believe in denial.
|
|
December 30, 2014, 06:26:28 PM |
|
[...] Still don't understand how this will "supply" any "watts to [12V] mining equipment [OP]" though... That's the job of the power supplies. So - basically - you're saying "this PDU" will not be "supplying" any "Watts to mining equipment...? And even if you assume any role for PSU's than certainly those 100KW will not reach cet "mining equipment"...?
|