Hey Gents, Appreciate the patience as I go through this. This could also be a noob question so please bear with me. I have access to an Industrial Site with a 600 AMP Single Phase Power in the US with very favourable power costs. I am trying to figure out how many 1KWh Miners I can put on this service without killing/burning anyone. I will need 10 KWh for support equipment such as switches, routers, monitors etc. Thanks once again, I have tried to look for answers online but getting a little confused with line voltage etc. Thanks
|
|
|
|
|
|
|
|
You get merit points when someone likes your post enough to give you some. And for every 2 merit points you receive, you can send 1 merit point to someone else!
|
|
|
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
|
|
|
|
fanatic26
|
|
August 07, 2017, 09:54:49 PM |
|
watts = amp x voltage
600 amp @ 208v is just a hair under 125kw. Id say you can safely run 100 1kw miners. Dont forget you will need ventilation and other things also on that same power to make it work. More than just a few switches and whatnot.
|
Stop buying industrial miners, running them at home, and then complaining about the noise.
|
|
|
NotFuzzyWarm
Legendary
Offline
Activity: 3626
Merit: 2544
Evil beware: We have waffles!
|
|
August 07, 2017, 09:59:48 PM |
|
Any simple google search regarding converting electric power will tell you that: Watts = Volts x Amps Plan on each miner taking 1,500w + another 15-20% reserve added because is a constant 24x7 load. Do math.
|
|
|
|
fusion0389
|
|
August 07, 2017, 10:32:27 PM |
|
Hey Gents, Appreciate the patience as I go through this. This could also be a noob question so please bear with me. I have access to an Industrial Site with a 600 AMP Single Phase Power in the US with very favourable power costs. I am trying to figure out how many 1KWh Miners I can put on this service without killing/burning anyone. I will need 10 KWh for support equipment such as switches, routers, monitors etc. Thanks once again, I have tried to look for answers online but getting a little confused with line voltage etc. Thanks
The electrician that i consulted stated that when calculating 24/7 loads one should not exceed 80% of their rated max capacity. So take 600amps x .80 = 480amps of absolute max 24/7 capacity. If you're running 3 phase 208v power, multiply 208v X 480 = 99,840 MAX 24/7 load. S9's realistically pull 1350-1400 watts so 99,840/1400 = 70 S9's safely. However, that does not account for cooling and\or ventilation, lighting, networking equipment, etc. so you probably need to shave a little out of there to account for those loads.
|
|
|
|
kritment (OP)
Member
Offline
Activity: 109
Merit: 13
|
|
August 07, 2017, 10:50:01 PM |
|
Thanks guys appreciate the replies. US is 120v power supply, not sure if I should calculate at 208v Thanks anyways
|
|
|
|
NotFuzzyWarm
Legendary
Offline
Activity: 3626
Merit: 2544
Evil beware: We have waffles!
|
|
August 07, 2017, 10:57:38 PM |
|
When talking non-office space commercial power in the US it will be 208 or higher at the main panel. Probably single phase and split into 2x 110v branches at the main panel just like in homes. Just as with the home panels, remove any 2 adjacent single-pole breakers (110v each) and replace with single 2-pole breaker. Instant 208v circuit now ready to be wired correctly to a 208 plug.
When talking that kind of miner loads using 208 should be a no-brainer as there are several excellent choices for using low(ish) cost server PSU's and they are are all >208V in.
|
|
|
|
kritment (OP)
Member
Offline
Activity: 109
Merit: 13
|
|
August 07, 2017, 11:27:48 PM |
|
Thanks NotFuzzyWarm No wonder you are legendary
|
|
|
|
NotFuzzyWarm
Legendary
Offline
Activity: 3626
Merit: 2544
Evil beware: We have waffles!
|
|
August 08, 2017, 12:11:38 AM Last edit: August 08, 2017, 01:30:13 AM by NotFuzzyWarm |
|
Thx As mentioned earlier, do keep in mind that all the power used ends up as heat and you must be sure to get rid of it. By and large, direct ventilation sucking the heat outside with large fans or blowers is most common and certainly the cheapest route.
|
|
|
|
fusion0389
|
|
August 08, 2017, 12:46:47 AM |
|
I second what notfuzzywarm said. I assumed you had 208 because that is what most commercial\industrial sites have. i have 240v at the panel that is split into (2) 120v phases. i'd suggest you get a commercial electrician out to your site for an eval. That'll tell you alot more about your current situation than anyone here can.
|
|
|
|
kritment (OP)
Member
Offline
Activity: 109
Merit: 13
|
|
August 08, 2017, 01:45:14 AM |
|
I second what notfuzzywarm said. I assumed you had 208 because that is what most commercial\industrial sites have. i have 240v at the panel that is split into (2) 120v phases. i'd suggest you get a commercial electrician out to your site for an eval. That'll tell you alot more about your current situation than anyone here can.
Thanks fusion0389 agree will get an electrician. just doing some initial feasibility to see if its even worth putting 100 miners.
|
|
|
|
Unacceptable
Legendary
Offline
Activity: 2212
Merit: 1001
|
|
August 08, 2017, 07:14:48 AM |
|
Be sure to check the wires coming into your building from the pole,just because your panel has room for say 200 amps,if that drop from your pole is only rated at 100 amps (and I have seen MANY like this in homes) you will definitely not like the results
|
"If you run into an asshole in the morning, you ran into an asshole. If you run into assholes all day long, you are the asshole." -Raylan Givens Got GOXXED ?? https://www.youtube.com/watch?v=9KiqRpPiJAU&feature=youtu.be"An ASIC being late is perfectly normal, predictable, and legal..."Hashfast & BFL slogan
|
|
|
oawan
Member
Offline
Activity: 67
Merit: 10
|
|
August 08, 2017, 07:52:49 AM |
|
Hey Gents, Appreciate the patience as I go through this. This could also be a noob question so please bear with me. I have access to an Industrial Site with a 600 AMP Single Phase Power in the US with very favourable power costs. I am trying to figure out how many 1KWh Miners I can put on this service without killing/burning anyone. I will need 10 KWh for support equipment such as switches, routers, monitors etc. Thanks once again, I have tried to look for answers online but getting a little confused with line voltage etc. Thanks
The electrician that i consulted stated that when calculating 24/7 loads one should not exceed 80% of their rated max capacity. So take 600amps x .80 = 480amps of absolute max 24/7 capacity. If you're running 3 phase 208v power, multiply 208v X 480 = 99,840 MAX 24/7 load. S9's realistically pull 1350-1400 watts so 99,840/1400 = 70 S9's safely. However, that does not account for cooling and\or ventilation, lighting, networking equipment, etc. so you probably need to shave a little out of there to account for those loads. Slight correction, max load would be 208 * 480 * 1.73 (the 1.73 accounts for the fact that the power coming in is 3 phase).
|
|
|
|
fusion0389
|
|
August 08, 2017, 12:01:52 PM |
|
Hey Gents, Appreciate the patience as I go through this. This could also be a noob question so please bear with me. I have access to an Industrial Site with a 600 AMP Single Phase Power in the US with very favourable power costs. I am trying to figure out how many 1KWh Miners I can put on this service without killing/burning anyone. I will need 10 KWh for support equipment such as switches, routers, monitors etc. Thanks once again, I have tried to look for answers online but getting a little confused with line voltage etc. Thanks
The electrician that i consulted stated that when calculating 24/7 loads one should not exceed 80% of their rated max capacity. So take 600amps x .80 = 480amps of absolute max 24/7 capacity. If you're running 3 phase 208v power, multiply 208v X 480 = 99,840 MAX 24/7 load. S9's realistically pull 1350-1400 watts so 99,840/1400 = 70 S9's safely. However, that does not account for cooling and\or ventilation, lighting, networking equipment, etc. so you probably need to shave a little out of there to account for those loads. Slight correction, max load would be 208 * 480 * 1.73 (the 1.73 accounts for the fact that the power coming in is 3 phase). Thanks for catching that error
|
|
|
|
QuintLeo
Legendary
Offline
Activity: 1498
Merit: 1030
|
|
August 08, 2017, 06:34:23 PM |
|
Thanks guys appreciate the replies. US is 120v power supply, not sure if I should calculate at 208v Thanks anyways
Single phase power in the US and Canada (not sure on Mexico) is normally supplied at a nominal 220 volts, but center-tapped to allow easy installation of 110 volt circuits. 80% of 600 amps - 480 amps x 220 volts = 105.6 KW (appx), so that place should be able to handle 95 or so miners that soak 1KW from the wall comfortably, with some left over for fans lighting network gear and such (you stated 10kw, which should be a reasonably safe assumption if you don't use mechanical A/C to try to cool the miners). OP DID state "single phase power" - ignore the 3-phase calculations. 600 amp service standard "split phase" 220 is pretty common for buildings. DO check the wiring though - it's COMMON for a panel to be rated higher than the actual power feed can handle. The MAIN BREAKER should be properly sized for the feed, but I've seen rare cases where some moron swapped it out for a higher-capacity breaker because they were overloading the original without bothering to check that the actual WIRING was rated for that capacity.
|
I'm no longer legendary just in my own mind! Like something I said? Donations gratefully accepted. LYLnTKvLefz9izJFUvEGQEZzSkz34b3N6U (Litecoin) 1GYbjMTPdCuV7dci3iCUiaRrcNuaiQrVYY (Bitcoin)
|
|
|
kritment (OP)
Member
Offline
Activity: 109
Merit: 13
|
|
August 09, 2017, 04:04:32 AM |
|
Thanks guys appreciate the replies. US is 120v power supply, not sure if I should calculate at 208v Thanks anyways
Single phase power in the US and Canada (not sure on Mexico) is normally supplied at a nominal 220 volts, but center-tapped to allow easy installation of 110 volt circuits. 80% of 600 amps - 480 amps x 220 volts = 105.6 KW (appx), so that place should be able to handle 95 or so miners that soak 1KW from the wall comfortably, with some left over for fans lighting network gear and such (you stated 10kw, which should be a reasonably safe assumption if you don't use mechanical A/C to try to cool the miners). OP DID state "single phase power" - ignore the 3-phase calculations. 600 amp service standard "split phase" 220 is pretty common for buildings. DO check the wiring though - it's COMMON for a panel to be rated higher than the actual power feed can handle. The MAIN BREAKER should be properly sized for the feed, but I've seen rare cases where some moron swapped it out for a higher-capacity breaker because they were overloading the original without bothering to check that the actual WIRING was rated for that capacity. Thanks QuintLeo Yea not using AC, so 10 KW should be good. One last question promise On 3 Phase 600A how much would be the KWs? 316KW? thanks
|
|
|
|
QuintLeo
Legendary
Offline
Activity: 1498
Merit: 1030
|
|
August 09, 2017, 08:46:15 PM |
|
Depends on how the 3-phase feed is set up, between Delta Wye or that one wierd semi-Delta type setup nobody puts into new installations any more.
I've not worked directly with 3-phase in decades, so I don't remember exact details any more.
|
I'm no longer legendary just in my own mind! Like something I said? Donations gratefully accepted. LYLnTKvLefz9izJFUvEGQEZzSkz34b3N6U (Litecoin) 1GYbjMTPdCuV7dci3iCUiaRrcNuaiQrVYY (Bitcoin)
|
|
|
kritment (OP)
Member
Offline
Activity: 109
Merit: 13
|
|
August 09, 2017, 09:19:18 PM |
|
Depends on how the 3-phase feed is set up, between Delta Wye or that one wierd semi-Delta type setup nobody puts into new installations any more.
I've not worked directly with 3-phase in decades, so I don't remember exact details any more.
Thanks buddy appreciate the wisdom words
|
|
|
|
NotFuzzyWarm
Legendary
Offline
Activity: 3626
Merit: 2544
Evil beware: We have waffles!
|
|
August 10, 2017, 12:45:12 AM |
|
As mentioned earlier by folks talking 3-phase, it is V x A x1 .73 to give available 3-phase kw so 220v @ 600A is 228kW available. Not even going to get into the old but still common wild-leg 3-phase (no-no for miners) vs 'real' delta or wye...
|
|
|
|
FUKT
|
|
August 10, 2017, 01:35:37 PM |
|
agree will get an electrician. just doing some initial feasibility to see if its even worth putting 100 miners. Please do spend a few bucks asking for the professional electrician advise, who will do all the necessary measurements and provide you with the maximum viable constant load, as QuintLeo is right in that real numbers can be much different from the nominal, and in reality your net could support only 30 miners plus cooling equipment (if you need one).
|
|
|
|
kritment (OP)
Member
Offline
Activity: 109
Merit: 13
|
|
August 10, 2017, 09:57:05 PM |
|
Thanks you all for your input. QuintLeo and fuzzywarm do you have donation address? so i can drop something in there wont be big.... im a newbie
|
|
|
|
|