Author Topic: Antminer L3+ Electrical Setup Requirements, can someone help?  (Read 211 times)
frankbitcoin (OP)
Sr. Member
****
Offline Offline

Activity: 1302
Merit: 295


View Profile
November 14, 2017, 03:47:35 PM
 #1

so as far as I understand each antminer L3 runs at 800 watts, plus or minus 10%, with 11 - 13 volts.  I'd like to run TWO of them.  Is having a 240 volt installed enough to do it?  Could I run three or four on a 240 volt?  On the same one?   Huh
1715453211
Hero Member
*
Offline Offline

Posts: 1715453211

View Profile Personal Message (Offline)

Ignore
1715453211
Reply with quote  #2

1715453211
Report to moderator
1715453211
Hero Member
*
Offline Offline

Posts: 1715453211

View Profile Personal Message (Offline)

Ignore
1715453211
Reply with quote  #2

1715453211
Report to moderator
1715453211
Hero Member
*
Offline Offline

Posts: 1715453211

View Profile Personal Message (Offline)

Ignore
1715453211
Reply with quote  #2

1715453211
Report to moderator
Whoever mines the block which ends up containing your transaction will get its fee.
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
1715453211
Hero Member
*
Offline Offline

Posts: 1715453211

View Profile Personal Message (Offline)

Ignore
1715453211
Reply with quote  #2

1715453211
Report to moderator
1715453211
Hero Member
*
Offline Offline

Posts: 1715453211

View Profile Personal Message (Offline)

Ignore
1715453211
Reply with quote  #2

1715453211
Report to moderator
1715453211
Hero Member
*
Offline Offline

Posts: 1715453211

View Profile Personal Message (Offline)

Ignore
1715453211
Reply with quote  #2

1715453211
Report to moderator
MATHReX
Sr. Member
****
Offline Offline

Activity: 861
Merit: 281


View Profile
November 14, 2017, 04:05:40 PM
 #2

It comes down to available power from your electrical panel.
Let's say you have 30 Amps service with a 120 Volt connection, L3 will consume around 6.5-7 Amps. In that manner, you can run probably four with that panel.
If you have 30 Amps service with a 230 Volt connection, L3 will consume around 3.5-4 Amps. So, you can run around 8 or so.
Moreover, the above calculation is without your day to day electricity consumption, so consider it in your calculation before running.