November 21, 2017, 05:11:24 PM |
|
I've seen some youtube videos of people using the "Hot Room" where all the hot air from the miners is being blown to. And the "Cold Room" where the miners are placed in racks and the temp is lower. Need advice on the following questions:
Lets say I have 20 S9's blowing 200CFM each = 4,000 CFM, and in the summer It gets hot 40C.
In the Hot Room, should I place a vent (intake fresh air from outside) of 5,000 CFM + $4,000 from the miners, and remove it with another vent of 9,000 - 10,000 CFM? or do I go only with the outtake fan equaling what the miners are blowing into?
In the Cool Room, I need to supply them with 4,000 CFM of air. I have an A/C of 5 Tons (2,000 cfm only), so do I need 2,000 of fan vent from outside? If so, what is the point of having a 5 ton A/C if the air from outside is warm-hot?
Thanks in advance for your help.
|