Author Topic: Harmonics in electrical system from mining off genset?  (Read 199 times)
VentMine (OP)
Full Member
***
Offline Offline

Activity: 236
Merit: 105


View Profile
March 06, 2018, 10:40:57 PM
 #1

Hey guys,

Curious I was talking to a genset vendor today and he mentioned running "server-like" equipment (Antminers) off of a genset may potentially have issues with harmonics and require harmonic conditioning to protect the alternator.

Should I be concerned about this?

1ESSdoVYKm8sNtYMfdkFBajhAe2e6G8keH
1715399645
Hero Member
*
Offline Offline

Posts: 1715399645

View Profile Personal Message (Offline)

Ignore
1715399645
Reply with quote  #2

1715399645
Report to moderator
1715399645
Hero Member
*
Offline Offline

Posts: 1715399645

View Profile Personal Message (Offline)

Ignore
1715399645
Reply with quote  #2

1715399645
Report to moderator
1715399645
Hero Member
*
Offline Offline

Posts: 1715399645

View Profile Personal Message (Offline)

Ignore
1715399645
Reply with quote  #2

1715399645
Report to moderator
"The nature of Bitcoin is such that once version 0.1 was released, the core design was set in stone for the rest of its lifetime." -- Satoshi
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
1715399645
Hero Member
*
Offline Offline

Posts: 1715399645

View Profile Personal Message (Offline)

Ignore
1715399645
Reply with quote  #2

1715399645
Report to moderator
1715399645
Hero Member
*
Offline Offline

Posts: 1715399645

View Profile Personal Message (Offline)

Ignore
1715399645
Reply with quote  #2

1715399645
Report to moderator
HagssFIN
Legendary
*
Offline Offline

Activity: 2436
Merit: 1706


Electrical engineer. Mining since 2014.


View Profile WWW
March 06, 2018, 10:46:41 PM
 #2

There are always harmonics present when using switched-mode power supplies.

If the harmonics start to be an issue, you can reduce the impact by adding a harmonics filter system in to your electrical system.

NotFuzzyWarm
Legendary
*
Offline Offline

Activity: 3626
Merit: 2542


Evil beware: We have waffles!


View Profile
March 07, 2018, 04:12:47 PM
Last edit: March 08, 2018, 11:29:26 PM by NotFuzzyWarm
 #3

Yes harmonics issues are possible if using cheap PSU's. However, most today have PFC - Power Factor Control - that mitigate the problem. Most will advertise if they have PFC and give a Power Factor rating.  A perfect resistive load gives a PF of 1.0 and most PSU's will be around 0.85 to 0.9 or better.

- For bitcoin to succeed the community must police itself -    My info useful? Donations welcome! 1FuzzyWc2J8TMqeUQZ8yjE43Rwr7K3cxs9
 -Sole remaining active developer of cgminer, Kano's repo is here
-Support Sidehacks miner development. Donations to:   1BURGERAXHH6Yi6LRybRJK7ybEm5m5HwTr
VentMine (OP)
Full Member
***
Offline Offline

Activity: 236
Merit: 105


View Profile
March 07, 2018, 05:26:04 PM
 #4

Yes harmonics issues are possible if using cheap PSU's. However, most today have PFC - Power Factor Control - that mitigate the problem. Most will advertise if they have PFC and give a Power Factor rating.  A perfect resistive load gives a PF of 1.0 and most PSU's will be around 0.85 to 0.9

Ahh k. Thanks gents. So I take it the Bitmain supplied PSU's have this as I recall their powerfactor is 0.95

1ESSdoVYKm8sNtYMfdkFBajhAe2e6G8keH
HagssFIN
Legendary
*
Offline Offline

Activity: 2436
Merit: 1706


Electrical engineer. Mining since 2014.


View Profile WWW
March 07, 2018, 05:39:07 PM
Last edit: March 08, 2018, 08:14:38 AM by HagssFIN
 #5

Yes harmonics issues are possible if using cheap PSU's. However, most today have PFC - Power Factor Control - that mitigate the problem. Most will advertise if they have PFC and give a Power Factor rating.  A perfect resistive load gives a PF of 1.0 and most PSU's will be around 0.85 to 0.9

^ This.

More usual case to end up in problems with harmonics is that if you have a lot of load consisting frequency converter controlled electrical motors for example.

So if you use good PSUs with PFC inside, harmonics shouldn't be an issue.

HoleShot
Member
**
Offline Offline

Activity: 70
Merit: 34


View Profile
March 08, 2018, 03:26:06 AM
 #6

I usually measure .97 PF on APW++ PSUs from Bitmain.

You can avoid almost all harmonics issues by avoiding non-resistive loads that use the neutral.

So, run all your power supplies, pumps and fans on 240V, but the coffee pot is fine on 120V.

VentMine (OP)
Full Member
***
Offline Offline

Activity: 236
Merit: 105


View Profile
March 08, 2018, 06:34:14 PM
 #7

I usually measure .97 PF on APW++ PSUs from Bitmain.

You can avoid almost all harmonics issues by avoiding non-resistive loads that use the neutral.

So, run all your power supplies, pumps and fans on 240V, but the coffee pot is fine on 120V.


The gen outputs 3-phase, so I have it configured to 230V L-L, 133 L-N. The 240/120 is single phase I believe?

Thanks for the responses guys, I didn't think I needed to worry about filtering but a recent conversation with a genset supplier spooked me.

1ESSdoVYKm8sNtYMfdkFBajhAe2e6G8keH
HoleShot
Member
**
Offline Offline

Activity: 70
Merit: 34


View Profile
March 09, 2018, 07:04:22 PM
 #8

Yes, the 230V/133V is your 3-phase output.

You should connect your miners like this.

A,B legs to miner 1
B,C legs to miner 2
C,A legs to miner 3

Then continue to rotate like this until maximum power is reached. I would not use the neutral. I would not use the single phase output.