Author Topic: Harmonics in electrical system from mining off genset?  (Read 196 times)
VentMine (OP)
Full Member
***
Offline Offline

Activity: 236
Merit: 105


View Profile
March 06, 2018, 10:40:57 PM
 #1

Hey guys,

Curious I was talking to a genset vendor today and he mentioned running "server-like" equipment (Antminers) off of a genset may potentially have issues with harmonics and require harmonic conditioning to protect the alternator.

Should I be concerned about this?

1ESSdoVYKm8sNtYMfdkFBajhAe2e6G8keH
1711720470
Hero Member
*
Offline Offline

Posts: 1711720470

View Profile Personal Message (Offline)

Ignore
1711720470
Reply with quote  #2

1711720470
Report to moderator
1711720470
Hero Member
*
Offline Offline

Posts: 1711720470

View Profile Personal Message (Offline)

Ignore
1711720470
Reply with quote  #2

1711720470
Report to moderator
1711720470
Hero Member
*
Offline Offline

Posts: 1711720470

View Profile Personal Message (Offline)

Ignore
1711720470
Reply with quote  #2

1711720470
Report to moderator
In order to achieve higher forum ranks, you need both activity points and merit points.
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
HagssFIN
Legendary
*
Offline Offline

Activity: 2422
Merit: 1704


Electrical engineer. Mining since 2014.


View Profile WWW
March 06, 2018, 10:46:41 PM
 #2

There are always harmonics present when using switched-mode power supplies.

If the harmonics start to be an issue, you can reduce the impact by adding a harmonics filter system in to your electrical system.

NotFuzzyWarm
Legendary
*
Offline Offline

Activity: 3584
Merit: 2482


Evil beware: We have waffles!


View Profile
March 07, 2018, 04:12:47 PM
Last edit: March 08, 2018, 11:29:26 PM by NotFuzzyWarm
 #3

Yes harmonics issues are possible if using cheap PSU's. However, most today have PFC - Power Factor Control - that mitigate the problem. Most will advertise if they have PFC and give a Power Factor rating.  A perfect resistive load gives a PF of 1.0 and most PSU's will be around 0.85 to 0.9 or better.

- For bitcoin to succeed the community must police itself -    My info useful? Donations welcome! 1FuzzyWc2J8TMqeUQZ8yjE43Rwr7K3cxs9
 -Sole remaining active developer of cgminer, Kano's repo is here
-Support Sidehacks miner development. Donations to:   1BURGERAXHH6Yi6LRybRJK7ybEm5m5HwTr
VentMine (OP)
Full Member
***
Offline Offline

Activity: 236
Merit: 105


View Profile
March 07, 2018, 05:26:04 PM
 #4

Yes harmonics issues are possible if using cheap PSU's. However, most today have PFC - Power Factor Control - that mitigate the problem. Most will advertise if they have PFC and give a Power Factor rating.  A perfect resistive load gives a PF of 1.0 and most PSU's will be around 0.85 to 0.9

Ahh k. Thanks gents. So I take it the Bitmain supplied PSU's have this as I recall their powerfactor is 0.95

1ESSdoVYKm8sNtYMfdkFBajhAe2e6G8keH
HagssFIN
Legendary
*
Offline Offline

Activity: 2422
Merit: 1704


Electrical engineer. Mining since 2014.


View Profile WWW
March 07, 2018, 05:39:07 PM
Last edit: March 08, 2018, 08:14:38 AM by HagssFIN
 #5

Yes harmonics issues are possible if using cheap PSU's. However, most today have PFC - Power Factor Control - that mitigate the problem. Most will advertise if they have PFC and give a Power Factor rating.  A perfect resistive load gives a PF of 1.0 and most PSU's will be around 0.85 to 0.9

^ This.

More usual case to end up in problems with harmonics is that if you have a lot of load consisting frequency converter controlled electrical motors for example.

So if you use good PSUs with PFC inside, harmonics shouldn't be an issue.

HoleShot
Member
**
Offline Offline

Activity: 70
Merit: 34


View Profile
March 08, 2018, 03:26:06 AM
 #6

I usually measure .97 PF on APW++ PSUs from Bitmain.

You can avoid almost all harmonics issues by avoiding non-resistive loads that use the neutral.

So, run all your power supplies, pumps and fans on 240V, but the coffee pot is fine on 120V.

VentMine (OP)
Full Member
***
Offline Offline

Activity: 236
Merit: 105


View Profile
March 08, 2018, 06:34:14 PM
 #7

I usually measure .97 PF on APW++ PSUs from Bitmain.

You can avoid almost all harmonics issues by avoiding non-resistive loads that use the neutral.

So, run all your power supplies, pumps and fans on 240V, but the coffee pot is fine on 120V.


The gen outputs 3-phase, so I have it configured to 230V L-L, 133 L-N. The 240/120 is single phase I believe?

Thanks for the responses guys, I didn't think I needed to worry about filtering but a recent conversation with a genset supplier spooked me.

1ESSdoVYKm8sNtYMfdkFBajhAe2e6G8keH
HoleShot
Member
**
Offline Offline

Activity: 70
Merit: 34


View Profile
March 09, 2018, 07:04:22 PM
 #8

Yes, the 230V/133V is your 3-phase output.

You should connect your miners like this.

A,B legs to miner 1
B,C legs to miner 2
C,A legs to miner 3

Then continue to rotate like this until maximum power is reached. I would not use the neutral. I would not use the single phase output.