Hello all. I have recently acquired some new space, and it comes with a whole lot of these (wired and mounted, of course): There are actually 6 of them.....and I would like to use them to power my next build-out. I am seeking out the best advice on the most cost effective way to utilize these outlets to power many mining rigs. Points given for clarity, nice calculations in terms of capacity, and links to products that I may need to get my rigs plugged in a going. Thanks in advance!
|
I am a trusted trader! Ask Inaba, Luo Demin, Vanderbleek, Sannyasi, Episking, Miner99er, Isepick, Amazingrando, Cablez, ColdHardMetal, Dextryn, MB300sd, Robocoder, gnar1ta$ and many others!
|
|
|
Unacceptable
Legendary
Offline
Activity: 2212
Merit: 1001
|
|
January 04, 2014, 04:58:03 AM Last edit: January 04, 2014, 06:05:46 AM by Unacceptable |
|
Well,30 amps @ 220v=7200 watts max.So,6000 watts useable That is per 6000 watts breaker,not per outlet. Also,that's 4 prong=1-120v,1-120v,1-neutral & 1-ground,up to date for code The 30 amp twist lock ends can be had at Home Depot: http://www.homedepot.com/p/Cooper-Wiring-Devices-30-Amp-125-250-Volt-4-Wire-Twist-Lock-Plug-Black-L1430P/203492586#For a 30 amp circuit,use at least 10/4 AWG 4 wire cables,8/4 AWG if you can find it. Or this: http://www.homedepot.com/p/DEK-Universal-25-ft-10-4-Universal-Generator-Extension-Cord-ACC02/100675654#Couldn't find a 220 splitter,maybe a electrical supply house or have an electrician make one for you. BTW,check the breakers,how many oulets on each one Use a volt meter or a checker like this one,to find out if power is on or off on each outlet while turning the breaker on & off : http://www.homedepot.com/p/Commercial-Electric-120-240-VAC-Voltage-Tester-MS8901H/202520560#Good luck!!!
|
"If you run into an asshole in the morning, you ran into an asshole. If you run into assholes all day long, you are the asshole." -Raylan Givens Got GOXXED ?? https://www.youtube.com/watch?v=9KiqRpPiJAU&feature=youtu.be"An ASIC being late is perfectly normal, predictable, and legal..."Hashfast & BFL slogan
|
|
|
|
yochdog (OP)
Legendary
Offline
Activity: 2044
Merit: 1000
|
|
January 05, 2014, 11:09:16 PM |
|
Any specific reason why I could not use a PDU already utilizing an L14-30 cord end?
|
I am a trusted trader! Ask Inaba, Luo Demin, Vanderbleek, Sannyasi, Episking, Miner99er, Isepick, Amazingrando, Cablez, ColdHardMetal, Dextryn, MB300sd, Robocoder, gnar1ta$ and many others!
|
|
|
cp1
|
|
January 05, 2014, 11:15:36 PM |
|
I don't see any reason why you couldn't. Verify that they're 220, it's possible they're 120. Are they labeled under the receptacle?
|
|
|
|
yochdog (OP)
Legendary
Offline
Activity: 2044
Merit: 1000
|
|
January 05, 2014, 11:45:45 PM |
|
I don't see any reason why you couldn't. Verify that they're 220, it's possible they're 120. Are they labeled under the receptacle?
I am 98% certain it is 220v. I will find out for sure tomorrow when my electrician takes a look.
|
I am a trusted trader! Ask Inaba, Luo Demin, Vanderbleek, Sannyasi, Episking, Miner99er, Isepick, Amazingrando, Cablez, ColdHardMetal, Dextryn, MB300sd, Robocoder, gnar1ta$ and many others!
|
|
|
timk225
|
|
January 06, 2014, 05:44:39 AM |
|
Why are some outlets / wiring listed as 220 or 240 volts, and also why are some listed as 115 or 120 volts? Shouldn't they all be the same, 120 volts per line and get either 120 or 240 only? And how do you get 208 / 277 volts? That's from a 3 phase setup, isn't it?
|
|
|
|
repairguy
|
|
January 06, 2014, 06:06:45 AM |
|
Any specific reason why I could not use a PDU already utilizing an L14-30 cord end?
No, They are less common but would work. Can you give me an example of one that you had found? The only concern I would have is that they may run the equipment at 120v instead of 240v. It will work either way but most power supplies are more efficient when you operate them at 240v.
|
|
|
|
repairguy
|
|
January 06, 2014, 06:14:37 AM |
|
Why are some outlets / wiring listed as 220 or 240 volts, and also why are some listed as 115 or 120 volts? Shouldn't they all be the same, 120 volts per line and get either 120 or 240 only? And how do you get 208 / 277 volts? That's from a 3 phase setup, isn't it?
In America the common voltages are 120v (single phase) single leg of split phase 240 or 208 to neutral/ground 240v (single phase) both legs of split phase 240 240v (mix phase or dual phase or three phase) Can get complicated 208v three phase feed using two or three of the legs 277v single leg of 480v three phase to neutral/ground 480v three phase feed using two or three of the legs
|
|
|
|
repairguy
|
|
January 16, 2014, 09:54:01 AM |
|
To whom did you award the bounty??
|
|
|
|
yochdog (OP)
Legendary
Offline
Activity: 2044
Merit: 1000
|
|
January 16, 2014, 02:51:24 PM |
|
To whom did you award the bounty??
Geekman. He is actually in the same area as I am, and is assisting in person.
|
I am a trusted trader! Ask Inaba, Luo Demin, Vanderbleek, Sannyasi, Episking, Miner99er, Isepick, Amazingrando, Cablez, ColdHardMetal, Dextryn, MB300sd, Robocoder, gnar1ta$ and many others!
|
|
|
bitpop
Legendary
Offline
Activity: 2912
Merit: 1060
|
|
January 17, 2014, 01:20:20 PM |
|
To whom did you award the bounty??
Geekman. He is actually in the same area as I am, and is assisting in person. He didn't even post.
|
|
|
|
yochdog (OP)
Legendary
Offline
Activity: 2044
Merit: 1000
|
|
January 17, 2014, 02:23:07 PM |
|
To whom did you award the bounty??
Geekman. He is actually in the same area as I am, and is assisting in person. He didn't even post. he pm'd. Offered his expertise in person.
|