Author Topic: Power setup for Antminer S9  (Read 187 times)
KEBKR (OP)
Jr. Member
*
Offline Offline

Activity: 30
Merit: 8


View Profile
July 07, 2018, 02:49:28 AM
Merited by OgNasty (1)
 #1

Hi.  First of all sorry if this has been covered but I couldn’t find an answer specific to my setup.  I have a fuse Panel, that’s old fashion glass fuses not breakers.  I have a 12-2 wire to a 220v (red wire to one side and black to the other ) with 2x20 amp fuses. This is then connected to a dual 20 amp outlet.  Does anyone know how many s9i units I can connect to this setup.  Could I do 2 per plug so 4 on this one line? 2 on the top outlet and 2 on the bottom?
1714671873
Hero Member
*
Offline Offline

Posts: 1714671873

View Profile Personal Message (Offline)

Ignore
1714671873
Reply with quote  #2

1714671873
Report to moderator
1714671873
Hero Member
*
Offline Offline

Posts: 1714671873

View Profile Personal Message (Offline)

Ignore
1714671873
Reply with quote  #2

1714671873
Report to moderator
Each block is stacked on top of the previous one. Adding another block to the top makes all lower blocks more difficult to remove: there is more "weight" above each block. A transaction in a block 6 blocks deep (6 confirmations) will be very difficult to remove.
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
1714671873
Hero Member
*
Offline Offline

Posts: 1714671873

View Profile Personal Message (Offline)

Ignore
1714671873
Reply with quote  #2

1714671873
Report to moderator
1714671873
Hero Member
*
Offline Offline

Posts: 1714671873

View Profile Personal Message (Offline)

Ignore
1714671873
Reply with quote  #2

1714671873
Report to moderator
Raymond_B
Member
**
Offline Offline

Activity: 504
Merit: 71

Just Getting Started...


View Profile WWW
July 07, 2018, 05:42:35 PM
 #2

You want to run no more than 80% continuous capacity on each circuit. So if the circuits are 20A then no more than 16A continuous each. So 2 Antminers per. Are you saying each outlet has a separate wire run? Or are you saying 2 outlets using one run of 12-2 wire? If it's the latter then you're limited to 2 miners period. If it's one run of 12-2 wire to each outlet then 2 per or 4 total if you have 2 circuits.

ccgllc
Copper Member
Full Member
***
Offline Offline

Activity: 658
Merit: 101

Math doesn't care what you believe.


View Profile
July 07, 2018, 06:07:34 PM
 #3

You want to run no more than 80% continuous capacity on each circuit. So if the circuits are 20A then no more than 16A continuous each. So 2 Antminers per. Are you saying each outlet has a separate wire run? Or are you saying 2 outlets using one run of 12-2 wire? If it's the latter then you're limited to 2 miners period. If it's one run of 12-2 wire to each outlet then 2 per or 4 total if you have 2 circuits.

Agreed.  My whole datacenter is wired based on (2) miners per 20amp 220V circuit.

Mined for a living since 2017.  Dabbled for years before that.
Linux admin since 0.96 kernel and Slackware distributions on (4) floppies...
KEBKR (OP)
Jr. Member
*
Offline Offline

Activity: 30
Merit: 8


View Profile
July 07, 2018, 11:30:29 PM
 #4

You want to run no more than 80% continuous capacity on each circuit. So if the circuits are 20A then no more than 16A continuous each. So 2 Antminers per. Are you saying each outlet has a separate wire run? Or are you saying 2 outlets using one run of 12-2 wire? If it's the latter then you're limited to 2 miners period. If it's one run of 12-2 wire to each outlet then 2 per or 4 total if you have 2 circuits.

Yes one 12-2 wire run from the panel to a dual outlet. So I’m limited to 2 miners per lead.  Thanks for the response, much appreciated!
Raymond_B
Member
**
Offline Offline

Activity: 504
Merit: 71

Just Getting Started...


View Profile WWW
July 07, 2018, 11:33:00 PM
Last edit: July 10, 2018, 01:07:17 AM by frodocooper
 #5

Yes one 12-2 wire run from the panel to a dual outlet. So I’m limited to 2 miners per lead.  Thanks for the response, much appreciated!

Hold up, you're using 220v so both wires carry current. If you physically only have one piece of wire that is 2 conductor 12 gauge then you need to change the outlet to a single as you have a SINGLE 220v 20A circuit. Previously you had 2 110v 20A outlets

KEBKR (OP)
Jr. Member
*
Offline Offline

Activity: 30
Merit: 8


View Profile
July 08, 2018, 02:24:41 AM
Last edit: July 10, 2018, 01:07:43 AM by frodocooper
 #6

Hold up, you're using 220v so both wires carry current. If you physically only have one piece of wire that is 2 conductor 12 gauge then you need to change the outlet to a single as you have a SINGLE 220v 20A circuit. Previously you had 2 110v 20A outlets

Yes I have one 12-2 wire with the black wire connected to one 110v leg and a 20 amp fuse and then the red wire connected to the other 110v leg and another 20 amp fuse.  This is connected to a dual 20 amp outlet.
tim-bc
Full Member
***
Offline Offline

Activity: 538
Merit: 175


View Profile
July 08, 2018, 02:32:21 AM
Last edit: July 10, 2018, 01:08:09 AM by frodocooper
 #7

Agreed.  My whole datacenter is wired based on (2) miners per 20amp 220V circuit.

I second this, the miners that I work with are also wired with 2 S9s per 20A breaker.

Ignore scammers on Skype, Telegram, etc. I will only ever contact you via forum PMs. See profile for fingerprint.
Raymond_B
Member
**
Offline Offline

Activity: 504
Merit: 71

Just Getting Started...


View Profile WWW
July 08, 2018, 02:45:57 AM
Last edit: July 10, 2018, 01:08:34 AM by frodocooper
 #8

Yes I have one 12-2 wire with the black wire connected to one 110v leg and a 20 amp fuse and then the red wire connected to the other 110v leg and another 20 amp fuse.  This is connected to a dual 20 amp outlet.

I just want to make sure you understand that you will need to replace that outlet with a single outlet, you do not have 2x 220v outlets. You've got 1 220v or 2 110v

KEBKR (OP)
Jr. Member
*
Offline Offline

Activity: 30
Merit: 8


View Profile
July 08, 2018, 02:53:59 AM
Last edit: July 10, 2018, 01:08:58 AM by frodocooper
 #9

I just want to make sure you understand that you will need to replace that outlet with a single outlet, you do not have 2x 220v outlets. You've got 1 220v or 2 110v

I’ve got this receptacle but what’s the difference in using this as opposed to a single outlet with a power bar with 2 miners attached?
https://www.homedepot.ca/en/home/p.20-amp-duplex-receptacle-ivory.1000135014.html
Raymond_B
Member
**
Offline Offline

Activity: 504
Merit: 71

Just Getting Started...


View Profile WWW
July 08, 2018, 03:15:38 AM
 #10

Nothing Smiley You're good, I thought you might have been thinking you actually had 4 circuits and were going to try to run 4 miners!

But you got it!

KEBKR (OP)
Jr. Member
*
Offline Offline

Activity: 30
Merit: 8


View Profile
July 08, 2018, 03:47:09 AM
 #11

Nothing Smiley You're good, I thought you might have been thinking you actually had 4 circuits and were going to try to run 4 miners!

But you got it!

Ok thanks.  Appreciate the help!