I'm a bit confused, you say your solar does 1.5MW for 20 S19 but grid supplied transformer 320KVA (~320KW PF1.0) is 90 S19's. Something's not quite right here.
Ya i noticed that too, phill forgot to write the unit
instead of
our solar does 1.5 megawatts a day. that is about 20 s19s nonstop.
it should be
our solar does 1.5 Megawatt-day. that is about 20 s19s nonstop.
another more popular term to use would be megawatt-hours, so 1.5mw / 24 = 0.0625 or 62.5kw which is enough to run 20 S19s each does roughly 3kw.
However, the last representation of numbers would need to have the word "average" in it, since his solar arrays don't actually generate 62.5kw every hour, it's probably 4-5 hours that net him the 1500kw, so you can take a wild guess and assume his arrays do 300kw/h, if those are 200w panels, then you looking at 1500 of them, that's a whole lot of panels.
this just shows my ignorance but with that kind of airflow from the water curtain so close (a few feet looks like?) to the shelves the asics will live on that there is no water mist that could get sucked in.
No water as in liquid form would be coming out from the other end of the evap cooler, it will be cooler air with more humidity, as long as the miner's temp remains above dew point condensing won't happen, running evap coolers in humid places could be somewhat risky and would cause damage to the miners in the long run, but if the humidity levels are moderate or low, there should be no issue at all.
One thing you need to be careful about would be having a faulty internet connection while using custom firmware like Vnish, The devs of those custom firmware wanted to outsmart Bitmain by saving energy during internet outages, so they keep the fan spinning but the miner doesn't generate any heat (unlike the stock firmware), now if you got those evap coolers throwing in air with high humidity, and your miners' fans spinning, the surrounding of the miner fan will go below dew point and then kaboom.